1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  <20182019  2020  2021  2022  2023  2024  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  <20182019  2020  2021  2022  2023  2024
Subject: RE: Latency between NI LabVIEW RT (cRIO) and EPICS on RT Linux
To: "'Mooney, Tim M.'" <[email protected]>, "'Johannes Spinneken (EGI)'" <[email protected]>, "'[email protected]'" <[email protected]>
Date: Fri, 9 Feb 2018 14:03:33 +0000
Curiosity continues …
This time I ran the 2 IOCS on the same machine.  So it removes the network latency, it is now inter-process communication on the same machine.
camonitor over 10 ms time period again (most values deleted to save space).  Calc1 incremented by 470, so there were 235 round trips.  The round trip time was thus 43 microseconds.  Comparing with the 92 microseconds when the IOCs are on different machines the round trip network overhead appears to be about 49 microseconds.  In this case each IOC was using 66% of a core, so it is not CPU bound.
Calc1                          2018-02-09 07:36:42.930026 723056
Calc2                          2018-02-09 07:36:42.930046 723057
Calc1                          2018-02-09 07:36:42.930074 723058
Calc2                          2018-02-09 07:36:42.930093 723059
Calc1                          2018-02-09 07:36:42.930109 723060
Calc2                          2018-02-09 07:36:42.930128 723061
Calc1                          2018-02-09 07:36:42.930146 723062
Calc1                          2018-02-09 07:36:42.939897 723518
Calc1                          2018-02-09 07:36:42.939933 723520
Calc2                          2018-02-09 07:36:42.939916 723519
Calc1                          2018-02-09 07:36:42.939971 723522
Calc2                          2018-02-09 07:36:42.939952 723521
Calc1                          2018-02-09 07:36:42.940010 723524
Calc2                          2018-02-09 07:36:42.939992 723523
Calc1                          2018-02-09 07:36:42.940051 723526
Finally I ran a test where both Calc1.db and Calc2.db are running in the same IOC.  This then eliminates both the network latency and the inter-process communication.  In this case Calc1 incremented by 748, so there were 374 round trips.  The round-trip time was thus 27 microseconds.  In this case I believe it is limited by CPU usage, the CPU use for the IOC is 130%, meaning it is using 1.3 cores.
Calc1                          2018-02-09 07:48:12.513015 406467
Calc2                          2018-02-09 07:48:12.513027 406468
Calc1                          2018-02-09 07:48:12.513038 406469
Calc1                          2018-02-09 07:48:12.522906 407209
Calc2                          2018-02-09 07:48:12.522922 407210
Calc1                          2018-02-09 07:48:12.522938 407211
Calc2                          2018-02-09 07:48:12.522954 407212
Calc1                          2018-02-09 07:48:12.522970 407213
Calc2                          2018-02-09 07:48:12.522985 407214
Calc1                          2018-02-09 07:48:12.523002 407215
Sent: Friday, February 09, 2018 7:14 AM
To: 'Mooney, Tim M.' <[email protected]>; 'Johannes Spinneken (EGI)' <[email protected]>; '[email protected]' <[email protected]>
Hi Johannes,
I was curious about what could be obtained in a test that is more similar to what you are asking, where there is an exchange of messages between an EPICS client and server.
I did another test, this time with IOCs running on 2 different Linux machines.  Each IOC is both a Channel Access client and a Channel Access server.
Machine 1 runs this database:
record(calc, "Calc1") {
  field(INPA, "Calc2 CP")
  field(CALC, "A+1")
Machine 2 runs this database
record(calc, "Calc2") {
  field(INPA, "Calc1 CP")
  field(CALC, "A+1")
Note that the INPA field has the CP property, meaning that calc record will process whenever it receives a Channel Access monitor on its input PV.  So the way it works is that Calc1 increments its value, Calc2 receives a monitor for that and increments its value, which in turn causes Calc1 to receive a monitor and increment its value, etc.  There is thus an exchange of messages as fast as possible.  It will be limited by the overhead in CA writes, CA monitor reception, processing the records, and network latency.
Here is the result of running camonitor in both records over a 10 ms time interval.  The Calc1 record incremented from 910732 to 910948 in this time, or a difference of 216.  It increments by 2 for each round-trip exchange, so there were 108 round trips.  Since this was over a period of 10 ms that means that the round-trip time was about 92 microseconds.
So the 10 ms time you are seeing is definitely not limited by EPICS Channel Access, record processing, or network overhead, it is something specific to your system!
corvette> camonitor Calc1 Calc2
Calc1                          2018-02-09 06:51:09.779757 910732
Calc2                          2018-02-09 06:51:09.780078 910733
Calc1                          2018-02-09 06:51:09.779837 910734
Calc2                          2018-02-09 06:51:09.780161 910735
Calc1                          2018-02-09 06:51:09.779919 910736
Calc2                          2018-02-09 06:51:09.780242 910737
Calc1                          2018-02-09 06:51:09.780001 910738
Calc2                          2018-02-09 06:51:09.780325 910739
Calc1                          2018-02-09 06:51:09.780082 910740
Calc2                          2018-02-09 06:51:09.780409 910741
Calc1                          2018-02-09 06:51:09.780175 910742
Calc2                          2018-02-09 06:51:09.780494 910743
Calc1                          2018-02-09 06:51:09.780250 910744
Calc2                          2018-02-09 06:51:09.780576 910745
Calc1                          2018-02-09 06:51:09.780331 910746
Calc1                          2018-02-09 06:51:09.780411 910748
Calc2                          2018-02-09 06:51:09.780655 910747
Calc1                          2018-02-09 06:51:09.780495 910750
Calc2                          2018-02-09 06:51:09.780739 910749
Calc2                          2018-02-09 06:51:09.780818 910751
Calc1                          2018-02-09 06:51:09.780578 910752
Calc2                          2018-02-09 06:51:09.780903 910753
Calc1                          2018-02-09 06:51:09.780661 910754
Calc2                          2018-02-09 06:51:09.780983 910755
Calc1                          2018-02-09 06:51:09.780744 910756
Calc2                          2018-02-09 06:51:09.781065 910757
Calc1                          2018-02-09 06:51:09.780824 910758
Calc2                          2018-02-09 06:51:09.781148 910759
Calc1                          2018-02-09 06:51:09.780902 910760
Calc2                          2018-02-09 06:51:09.781229 910761
Calc1                          2018-02-09 06:51:09.780984 910762
Calc2                          2018-02-09 06:51:09.781307 910763
Calc1                          2018-02-09 06:51:09.781066 910764
Calc2                          2018-02-09 06:51:09.781388 910765
Calc1                          2018-02-09 06:51:09.781148 910766
Calc2                          2018-02-09 06:51:09.781473 910767
Calc1                          2018-02-09 06:51:09.781232 910768
Calc2                          2018-02-09 06:51:09.781556 910769
Calc1                          2018-02-09 06:51:09.781315 910770
Calc2                          2018-02-09 06:51:09.781634 910771
Calc1                          2018-02-09 06:51:09.781394 910772
Calc2                          2018-02-09 06:51:09.781719 910773
Calc1                          2018-02-09 06:51:09.781479 910774
Calc2                          2018-02-09 06:51:09.781802 910775
Calc1                          2018-02-09 06:51:09.781559 910776
Calc2                          2018-02-09 06:51:09.781883 910777
Calc1                          2018-02-09 06:51:09.781642 910778
Calc2                          2018-02-09 06:51:09.781965 910779
Calc1                          2018-02-09 06:51:09.781726 910780
Calc2                          2018-02-09 06:51:09.782060 910781
Calc1                          2018-02-09 06:51:09.781825 910782
Calc2                          2018-02-09 06:51:09.782160 910783
Calc1                          2018-02-09 06:51:09.781917 910784
Calc2                          2018-02-09 06:51:09.782239 910785
Calc1                          2018-02-09 06:51:09.781997 910786
Calc2                          2018-02-09 06:51:09.782321 910787
Calc1                          2018-02-09 06:51:09.782078 910788
Calc2                          2018-02-09 06:51:09.782401 910789
Calc1                          2018-02-09 06:51:09.782158 910790
Calc2                          2018-02-09 06:51:09.782479 910791
Calc1                          2018-02-09 06:51:09.782235 910792
Calc2                          2018-02-09 06:51:09.782580 910793
Calc1                          2018-02-09 06:51:09.782338 910794
Calc2                          2018-02-09 06:51:09.782705 910795
Calc1                          2018-02-09 06:51:09.782461 910796
Calc2                          2018-02-09 06:51:09.782827 910797
Calc1                          2018-02-09 06:51:09.782591 910798
Calc2                          2018-02-09 06:51:09.782953 910799
Calc1                          2018-02-09 06:51:09.782712 910800
Calc2                          2018-02-09 06:51:09.783078 910801
Calc1                          2018-02-09 06:51:09.782836 910802
Calc2                          2018-02-09 06:51:09.783204 910803
Calc1                          2018-02-09 06:51:09.782962 910804
Calc2                          2018-02-09 06:51:09.783328 910805
Calc1                          2018-02-09 06:51:09.783086 910806
Calc2                          2018-02-09 06:51:09.783451 910807
Calc1                          2018-02-09 06:51:09.783209 910808
Calc2                          2018-02-09 06:51:09.783576 910809
Calc1                          2018-02-09 06:51:09.783333 910810
Calc2                          2018-02-09 06:51:09.783699 910811
Calc1                          2018-02-09 06:51:09.783456 910812
Calc2                          2018-02-09 06:51:09.783826 910813
Calc1                          2018-02-09 06:51:09.783590 910814
Calc2                          2018-02-09 06:51:09.783951 910815
Calc1                          2018-02-09 06:51:09.783713 910816
Calc2                          2018-02-09 06:51:09.784081 910817
Calc1                          2018-02-09 06:51:09.783859 910818
Calc2                          2018-02-09 06:51:09.784212 910819
Calc1                          2018-02-09 06:51:09.783990 910820
Calc2                          2018-02-09 06:51:09.784325 910821
Calc1                          2018-02-09 06:51:09.784084 910822
Calc2                          2018-02-09 06:51:09.784448 910823
Calc1                          2018-02-09 06:51:09.784206 910824
Calc2                          2018-02-09 06:51:09.784570 910825
Calc1                          2018-02-09 06:51:09.784333 910826
Calc2                          2018-02-09 06:51:09.784695 910827
Calc1                          2018-02-09 06:51:09.784453 910828
Calc2                          2018-02-09 06:51:09.784819 910829
Calc1                          2018-02-09 06:51:09.784583 910830
Calc2                          2018-02-09 06:51:09.784944 910831
Calc1                          2018-02-09 06:51:09.784701 910832
Calc2                          2018-02-09 06:51:09.785074 910833
Calc1                          2018-02-09 06:51:09.784831 910834
Calc2                          2018-02-09 06:51:09.785222 910835
Calc1                          2018-02-09 06:51:09.785000 910836
Calc2                          2018-02-09 06:51:09.785338 910837
Calc1                          2018-02-09 06:51:09.785100 910838
Calc2                          2018-02-09 06:51:09.785456 910839
Calc1                          2018-02-09 06:51:09.785213 910840
Calc2                          2018-02-09 06:51:09.785565 910841
Calc1                          2018-02-09 06:51:09.785320 910842
Calc2                          2018-02-09 06:51:09.785690 910843
Calc1                          2018-02-09 06:51:09.785444 910844
Calc2                          2018-02-09 06:51:09.785816 910845
Calc1                          2018-02-09 06:51:09.785572 910846
Calc2                          2018-02-09 06:51:09.785941 910847
Calc1                          2018-02-09 06:51:09.785697 910848
Calc2                          2018-02-09 06:51:09.786072 910849
Calc1                          2018-02-09 06:51:09.785862 910850
Calc2                          2018-02-09 06:51:09.786195 910851
Calc1                          2018-02-09 06:51:09.785971 910852
Calc2                          2018-02-09 06:51:09.786303 910853
Calc1                          2018-02-09 06:51:09.786063 910854
Calc2                          2018-02-09 06:51:09.786385 910855
Calc1                          2018-02-09 06:51:09.786142 910856
Calc2                          2018-02-09 06:51:09.786463 910857
Calc1                          2018-02-09 06:51:09.786218 910858
Calc2                          2018-02-09 06:51:09.786544 910859
Calc1                          2018-02-09 06:51:09.786303 910860
Calc2                          2018-02-09 06:51:09.786627 910861
Calc1                          2018-02-09 06:51:09.786392 910862
Calc2                          2018-02-09 06:51:09.786714 910863
Calc1                          2018-02-09 06:51:09.786473 910864
Calc2                          2018-02-09 06:51:09.786796 910865
Calc1                          2018-02-09 06:51:09.786554 910866
Calc2                          2018-02-09 06:51:09.786875 910867
Calc1                          2018-02-09 06:51:09.786635 910868
Calc2                          2018-02-09 06:51:09.786956 910869
Calc1                          2018-02-09 06:51:09.786716 910870
Calc2                          2018-02-09 06:51:09.787037 910871
Calc1                          2018-02-09 06:51:09.786801 910872
Calc2                          2018-02-09 06:51:09.787122 910873
Calc1                          2018-02-09 06:51:09.786883 910874
Calc2                          2018-02-09 06:51:09.787204 910875
Calc1                          2018-02-09 06:51:09.786965 910876
Calc2                          2018-02-09 06:51:09.787285 910877
Calc1                          2018-02-09 06:51:09.787047 910878
Calc2                          2018-02-09 06:51:09.787373 910879
Calc1                          2018-02-09 06:51:09.787133 910880
Calc2                          2018-02-09 06:51:09.787455 910881
Calc1                          2018-02-09 06:51:09.787214 910882
Calc2                          2018-02-09 06:51:09.787538 910883
Calc1                          2018-02-09 06:51:09.787299 910884
Calc2                          2018-02-09 06:51:09.787623 910885
Calc1                          2018-02-09 06:51:09.787379 910886
Calc2                          2018-02-09 06:51:09.787701 910887
Calc1                          2018-02-09 06:51:09.787458 910888
Calc2                          2018-02-09 06:51:09.787782 910889
Calc1                          2018-02-09 06:51:09.787538 910890
Calc2                          2018-02-09 06:51:09.787863 910891
Calc1                          2018-02-09 06:51:09.787624 910892
Calc2                          2018-02-09 06:51:09.787948 910893
Calc1                          2018-02-09 06:51:09.787705 910894
Calc2                          2018-02-09 06:51:09.788025 910895
Calc1                          2018-02-09 06:51:09.787786 910896
Calc2                          2018-02-09 06:51:09.788112 910897
Calc1                          2018-02-09 06:51:09.787869 910898
Calc2                          2018-02-09 06:51:09.788192 910899
Calc1                          2018-02-09 06:51:09.787949 910900
Calc2                          2018-02-09 06:51:09.788273 910901
Calc1                          2018-02-09 06:51:09.788030 910902
Calc2                          2018-02-09 06:51:09.788352 910903
Calc1                          2018-02-09 06:51:09.788108 910904
Calc2                          2018-02-09 06:51:09.788432 910905
Calc1                          2018-02-09 06:51:09.788189 910906
Calc2                          2018-02-09 06:51:09.788513 910907
Calc1                          2018-02-09 06:51:09.788270 910908
Calc2                          2018-02-09 06:51:09.788594 910909
Calc1                          2018-02-09 06:51:09.788352 910910
Calc2                          2018-02-09 06:51:09.788673 910911
Calc1                          2018-02-09 06:51:09.788429 910912
Calc2                          2018-02-09 06:51:09.788754 910913
Calc1                          2018-02-09 06:51:09.788510 910914
Calc2                          2018-02-09 06:51:09.788841 910915
Calc1                          2018-02-09 06:51:09.788599 910916
Calc2                          2018-02-09 06:51:09.788921 910917
Calc1                          2018-02-09 06:51:09.788682 910918
Calc2                          2018-02-09 06:51:09.789001 910919
Calc1                          2018-02-09 06:51:09.788757 910920
Calc2                          2018-02-09 06:51:09.789081 910921
Calc1                          2018-02-09 06:51:09.788837 910922
Calc2                          2018-02-09 06:51:09.789162 910923
Calc1                          2018-02-09 06:51:09.788919 910924
Calc2                          2018-02-09 06:51:09.789245 910925
Calc1                          2018-02-09 06:51:09.789000 910926
Calc2                          2018-02-09 06:51:09.789324 910927
Calc1                          2018-02-09 06:51:09.789080 910928
Calc2                          2018-02-09 06:51:09.789404 910929
Calc1                          2018-02-09 06:51:09.789162 910930
Calc2                          2018-02-09 06:51:09.789485 910931
Calc1                          2018-02-09 06:51:09.789241 910932
Calc2                          2018-02-09 06:51:09.789566 910933
Calc1                          2018-02-09 06:51:09.789328 910934
Calc2                          2018-02-09 06:51:09.789645 910935
Calc1                          2018-02-09 06:51:09.789401 910936
Calc2                          2018-02-09 06:51:09.789725 910937
Calc1                          2018-02-09 06:51:09.789483 910938
Calc2                          2018-02-09 06:51:09.789806 910939
Calc1                          2018-02-09 06:51:09.789562 910940
Calc2                          2018-02-09 06:51:09.789886 910941
Calc1                          2018-02-09 06:51:09.789646 910942
Calc2                          2018-02-09 06:51:09.789965 910943
Calc1                          2018-02-09 06:51:09.789722 910944
Calc2                          2018-02-09 06:51:09.790046 910945
Calc1                          2018-02-09 06:51:09.789803 910946
Calc2                          2018-02-09 06:51:09.790127 910947
Calc1                          2018-02-09 06:51:09.789882 910948
Calc2                          2018-02-09 06:51:09.790208 910949
Sent: Tuesday, February 06, 2018 2:40 PM
To: 'Mooney, Tim M.' <[email protected]>; Johannes Spinneken (EGI) <[email protected]>; [email protected]
Hi Johannes,
Here is one quick measurement.
-          I have an areaDetector simDetector running on a Linux machine.  It has a small image size (50x50) so it can run very fast.  It is doing about 5,500 frames/s.
-          There is an image counter PV that updates each time there is a new image, i.e. at 5,500 Hz.
-          I ran “camonitor” on a different Linux machine to see how fast it received the monitor updates on that PV.  I used –tcs so we see both the CA client timestamps and the CA server timestamps. I sent the camonitor output to a file so the terminal I/O would not slow it down.
-          Both of these machines have 10GB Ethernet connections.
This is the result, covering a time period of about 10 ms.
Viper:~>camonitor -tcs 13SIM1:cam1:ArrayCounter_RBV > test.out
^C
Viper:~>more test.out
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.602116(2018-02-06 14:34:30.602287) 4182302
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.602320(2018-02-06 14:34:30.602489) 4182303
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.602505(2018-02-06 14:34:30.602611) 4182304
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.602696(2018-02-06 14:34:30.602888) 4182305
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.602899(2018-02-06 14:34:30.603005) 4182306
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.603127(2018-02-06 14:34:30.603238) 4182307
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.603344(2018-02-06 14:34:30.603470) 4182308
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.603536(2018-02-06 14:34:30.603642) 4182309
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.603727(2018-02-06 14:34:30.603838) 4182310
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.603899(2018-02-06 14:34:30.604019) 4182311
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.604109(2018-02-06 14:34:30.604228) 4182312
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.604318(2018-02-06 14:34:30.604440) 4182313
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.604506(2018-02-06 14:34:30.604606) 4182314
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.604692(2018-02-06 14:34:30.604842) 4182315
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.604884(2018-02-06 14:34:30.605005) 4182316
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.605076(2018-02-06 14:34:30.605206) 4182317
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.605260(2018-02-06 14:34:30.605363) 4182318
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.605427(2018-02-06 14:34:30.605539) 4182319
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.605613(2018-02-06 14:34:30.605725) 4182320
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.605795(2018-02-06 14:34:30.605919) 4182321
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.605966(2018-02-06 14:34:30.606132) 4182322
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.606149(2018-02-06 14:34:30.606265) 4182323
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.606319(2018-02-06 14:34:30.606431) 4182324
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.606479(2018-02-06 14:34:30.606594) 4182325
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.606611(2018-02-06 14:34:30.606727) 4182326
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.606820(2018-02-06 14:34:30.606917) 4182327
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.607015(2018-02-06 14:34:30.607116) 4182328
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.607186(2018-02-06 14:34:30.607287) 4182329
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.607363(2018-02-06 14:34:30.607459) 4182330
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.607542(2018-02-06 14:34:30.607643) 4182331
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.607732(2018-02-06 14:34:30.607841) 4182332
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.607914(2018-02-06 14:34:30.608016) 4182333
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.608100(2018-02-06 14:34:30.608202) 4182334
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.608252(2018-02-06 14:34:30.608355) 4182335
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.608432(2018-02-06 14:34:30.608532) 4182336
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.608620(2018-02-06 14:34:30.608731) 4182337
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.608801(2018-02-06 14:34:30.608909) 4182338
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.608983(2018-02-06 14:34:30.609098) 4182339
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.609164(2018-02-06 14:34:30.609279) 4182340
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.609341(2018-02-06 14:34:30.609449) 4182341
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.609526(2018-02-06 14:34:30.609625) 4182342
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.609701(2018-02-06 14:34:30.609817) 4182343
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.609877(2018-02-06 14:34:30.609990) 4182344
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.610057(2018-02-06 14:34:30.610185) 4182345
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.610268(2018-02-06 14:34:30.610392) 4182346
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.610454(2018-02-06 14:34:30.610568) 4182347
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.610620(2018-02-06 14:34:30.610739) 4182348
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.610800(2018-02-06 14:34:30.610908) 4182349
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.610988(2018-02-06 14:34:30.611097) 4182350
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.611168(2018-02-06 14:34:30.611289) 4182351
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.611355(2018-02-06 14:34:30.611454) 4182352
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.611536(2018-02-06 14:34:30.611644) 4182353
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.611728(2018-02-06 14:34:30.611834) 4182354
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.611915(2018-02-06 14:34:30.612013) 4182355
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.612084(2018-02-06 14:34:30.612204) 4182356
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.612265(2018-02-06 14:34:30.612388) 4182357
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.612447(2018-02-06 14:34:30.612543) 4182358
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.612619(2018-02-06 14:34:30.612721) 4182359
13SIM1:cam1:ArrayCounter_RBV   2018-02-06 14:34:30.612806(2018-02-06 14:34:30.612915) 4182360
You can see that it does not appear to lose any monitors, and the time between monitors is just under 200 microseconds.  So at least in this setup we have not yet hit the EPICS protocol or network speed limits.
From: [email protected] [mailto:[email protected]] On Behalf Of Mooney, Tim M.
Sent: Tuesday, February 06, 2018 2:12 PM
To: Johannes Spinneken (EGI) <[email protected]>; [email protected]
Subject: Re: Latency between NI LabVIEW RT (cRIO) and EPICS on RT Linux
Hi Johannes,
With an interrupt service routine, vxWorks can read from or write to an IndustryPack FPGA at around 10 kHz, but I would not try to process an EPICS record at that rate - at least not a record that isn't prepared to throttle the rate at which it posts monitors.  I don't usually process general purpose EPICS records faster than around 100 Hz.  I think it's pretty common practice to keep stuff faster than around 100 Hz restricted to driver code, which doesn't really have to know about EPICS.
Tim Mooney ([email protected]) (630)252-5417
Beamline Controls Group (www.aps.anl.gov)
Advanced Photon Source, Argonne National Lab
From: [email protected] <[email protected]> on behalf of Johannes Spinneken (EGI) <[email protected]>
Sent: Tuesday, February 6, 2018 1:33:13 PM
To: [email protected]
Subject: Latency between NI LabVIEW RT (cRIO) and EPICS on RT Linux
Hi
I am fairly new to EPICS and have been testing an application with the following setup:
  • National Instruments cRIO running an EPICS server
  • EPICS client on RT Linux (fully preemptible Kernel 4.9.76) using EPICS base libs (C application)
  • PV write on cRIO in LabVIEW RT, with new data at 1ms intervals (using 1ms timed loop)
  • Read of EPICS PV in RT Linux with loop times <1ms
  • Posting data back to another EPICS PV to then be read as “round trip” timing on cRIO
The setup works in principle, but I am seeing higher latencies than I was expecting. I was hoping to achieve latencies in the low ms order (say 1 – 2ms data round trip from cRIO to RT Linux back to cRIO). In practice, I observe round-trip timings of order 10ms. Two questions:
(i)                   What is the best timing (latency) that can generally be achieved using EPICS? Is there something fundamental in the protocol that prohibits data exchange in the low ms order? I understand that this will of course depend on target hardware / software, but a ballpark figure would be good as “expectation management”. A typical ping between cRIO and Linux RT takes approx. 0.2ms, so the hardware seems clearly capable of <1ms timings.
(ii)                 Does anyone have experience with running EPICS on LabVIEW RT / cRIO? I suspect some (most) of the latency is due to the way in which NI handles TCP traffic. I already discovered that data is normally buffered for 10ms (or 8 kB). This can be avoided by using the Shared Variable Data Flush VI:
http://zone.ni.com/reference/en-XX/help/371361H-01/lvcomm/flushsharedvar/
which indeed reduced round-trip timings by around 8-10ms. However, I seem to be unable to push timings down further below the 10ms round-trip mark. Any guidance would be much appreciated.
Many thanks!
Best wishes
Johannes
Johannes Spinneken PhD FRSA
Principal Systems Engineer
Evergreen Innovations UK & USA
+1 916 266 3709 (US cell)
+44 7868 923583 (UK mobile)
www.evergreeninnovations.co
Re: Latency between NI LabVIEW RT (cRIO) and EPICS on RT Linux Johannes Spinneken (EGI)
Re: Latency between NI LabVIEW RT (cRIO) and EPICS on RT Linux Mooney, Tim M.
RE: Latency between NI LabVIEW RT (cRIO) and EPICS on RT Linux Mark Rivers
Prev: 回复: Question about values of historic PVs dislpayed in CSS XY Graph widget lzf neu
Next: Re: 回复: Question about values of historic PVs dislpayed in CSS XY Graph widget Shen, Guobao
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  <20182019  2020  2021  2022  2023  2024
Prev: RE: Latency between NI LabVIEW RT (cRIO) and EPICS on RT Linux Mark Rivers
Next: Re: Latency between NI LabVIEW RT (cRIO) and EPICS on RT Linux Johannes Spinneken (EGI)
ANJ, 09 Feb 2018 Valid HTML 4.01! · Home · News · About · Base · Modules · Extensions · Distributions · Download ·