1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  <2021>  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  <2021>  2022  2023  2024  2025  2026
Subject: Re: Rate of change calculation
To: Donny Domagoj Cosic <[email protected]>
Date: Mon, 29 Mar 2021 11:52:46 +0000
Hi Donny,
> It seems like the PP and NPP are both returning the same value even though the actual charge is changing.
> Any ideas on why this would be happening or suggestions would be greatly appreciated.
I suspect that what is happening is that it first evaluates INPA, processing Charge record.  It then evaluates INPB which reads the Charge record, obtaining the same value that was just read when INPA was evaluated.
I think this will fix the problem.  It just assigns the value of A to B after doing the subtraction.
record(calc, "$(KEIT):CalcCurrent")
     field(SCAN, "1 second")
     field(INPA, "$(KEIT):Charge PP")
      field(CALC, "B-A;B:=A")
From: Tech-talk <[email protected]> on behalf of Donny Domagoj Cosic via Tech-talk <[email protected]>
Sent: Monday, March 29, 2021 6:35 AM
To: Tech-talk
Subject: Rate of change calculation
Hello,
I am trying to calculate the rate of change of a record using a calc
record as follows:
record(ai, "$(KEIT):Charge")
     field(DESC, "Measure Charge")
     field(DTYP, "steam")
     field("@devKeithley6514.proto measureCharge() $(PORT)")
     field(SCAN, "Passive")
     field(INPB, "$(KEIT):Charge NPP")
     field(CALC, "B-A")
The calc record always returns 0. If I change the calc to B+A, to check
what is going on, I always get double the charge. It seems like the PP
is changing. Any ideas on why this would be happening or suggestions
Thank you in advance,
Donny
Donny Domagoj Cosic
  Institut Ruđer Bošković, Bijenička cesta 54, 10000 Zagreb, Croatia
Rate of change calculation Donny Domagoj Cosic via Tech-talk
Prev: Re: Rate of change calculation Smith, Martin via Tech-talk
Next: Re: Rate of change calculation Donny Domagoj Cosic via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  <2021>  2022  2023  2024  2025  2026
Prev: Re: Rate of change calculation Donny Domagoj Cosic via Tech-talk
Next: modbus read error Дмитрий Прощенко via Tech-talk
