1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  <2021>  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  <2021>  2022  2023  2024  2025  2026
Subject: Re: Re: Re: A problem with modbus reading floating point numbers
To: "mark l rivers" <[email protected]>
Date: Fri, 19 Nov 2021 16:43:54 +0800 (GMT+08:00)
Thank you very much,mark.
But I have some questions about modbus datatypes and ASyn interface types:
1. Does the modbus enumeration type start at 0 or 1?  Rval is also incorrect when we try to set modbus data type to 0x8.
drvModbusAsynConfigure("MOXA_E1242_In_Word",   "moxa",    255, 4,  0x208,  0x8,    0x8,  2000,    "moxa E1242")
2. AsynFloat32 type not found,  Only asynFloat32Array was found,Can I use it to read 4-byte float values?
Rval is also incorrect when trying to set DTYP to asynFloat32Array.
record(ai, "$(P)$(R)_AI") {
    field(DTYP,"asynFloat32Array")
    field(INP,"@asynMask($(PORT) $(OFFSET) $(BITS))MODBUS_DATA")
    field(LINR,"LINEAR")
    field(EGUL,"$(EGUL)")
    field(EGUF,"$(EGUF)")
    field(HOPR,"$(EGUF)")
    field(LOPR,"$(EGUL)")
    field(PREC,"$(PREC)")
    field(SCAN,"$(SCAN)")
Gao Zhenhua
-----原始邮件-----
发件人:"Mark L Rivers" <[email protected]>
发送时间:2021-11-18 21:32:55 (星期四)
收件人: "高振华" <[email protected]>
抄送: "[email protected]" <[email protected]>
主题: Re: Re: A problem with modbus reading floating point numbers
> note: I used the AI_scaledValue command to read moxa E1242 instead of the raw AI_rawValue command.
> Instead of reading the original 2-byte integer, the 4-byte float value converted to the scaled value is read .
So the Moxa is returning a 4-byte float, or is it returning an integer?
The drvModbusAsynConfigure command is this:
drvModbusAsynConfigure("MOXA_E1242_In_Word",   "moxa",    255, 4,  0x208,  0x8,    0x7,  2000,    "moxa E1242")
So you are using Modbus data type 0x7 which is INT32_BE.  So the driver is reading a 32-bit integer, not a 32-bit float.
Your ai record is configured for asynInt32 device support:
    field(DTYP,"asynInt32")
If the Moxa is returning a float you need to change both the Modbus data type and the asyn interface in the ai record.
Sent: Thursday, November 18, 2021 2:29 AM
To: Mark L Rivers <[email protected]>
Cc: [email protected] <[email protected]>
Subject: Re: Re: A problem with modbus reading floating point numbers
Hi Mark,
Now rval=7 instead of 49169 for 7.5V.
note:I used the AI_scaledValue command to read moxa E1242 instead of the raw AI_rawValue command.
dbpr as follows:
epics> dbpr MOXA:ADC1_AI 2
ACKS: NO_ALARM      ACKT: YES           ADEL: 0             AFTC: 0
AOFF: 0             ASG :               ASLO: 1             BKPT: 00
DESC:               DISA: 0             DISP: 0             DISS: NO_ALARM
DISV: 1             DTYP: asynInt32     EGU :               EGUF: 65535
EGUL: 0             EOFF: 0             ESLO: 1             EVNT:
FLNK: CONSTANT      HHSV: NO_ALARM      HIGH: 0             HIHI: 0
HOPR: 65535         HSV : NO_ALARM      HYST: 0
INP : INST_IO @asynMask(MOXA_E1242_In_Word 0 16)MODBUS_DATA LCNT: 0
LINR: LINEAR        LLSV: NO_ALARM      LOLO: 0             LOPR: 0
LOW : 0             LSV : NO_ALARM      MDEL: 0             NAME: MOXA:ADC1_AI
NSEV: NO_ALARM      NSTA: NO_ALARM      PACT: 0             PHAS: 0
PINI: NO            PREC: 3             PRIO: LOW           PUTF: 0
ROFF: 0             RPRO: 0             RVAL: 7             SCAN: I/O Intr
SDIS: CONSTANT      SDLY: -1            SEVR: NO_ALARM      SIML: CONSTANT
SIMM: NO            SIMS: NO_ALARM      SIOL: CONSTANT      SMOO: 0
SSCN: <nil>         STAT: NO_ALARM      SVAL: 0
TIME: 2021-11-18 15:14:56.279766515     TPRO: 0             TSE : 0
TSEL: CONSTANT      UDF : 0             UDFS: INVALID       VAL : 7
epics>
#traceIO
2021/11/18 15:50:06.322 192.168.127.254:502 write 12
00 99 00 00 00 06 ff 04 02 00 00 04
2021/11/18 15:50:06.339 192.168.127.254:502 read 17
00 99 00 00 00 0b ff 04 08 c0 11 00 00 00 0f 00 26
2021/11/18 15:50:06.340 192.168.127.254:502 write 12
00 9a 00 00 00 06 ff 04 02 08 00 08
2021/11/18 15:50:06.355 192.168.127.254:502 read 25
00 9a 00 00 00 13 ff 04 10 16 30 40 f0 00 00 00 00 00 96 3b
16 00 be 3b be
Best Regards, Gao Zhenhua
-----原始邮件-----
发送时间:2021-11-17 22:22:52 (星期三)
主题: Re: A problem with modbus reading floating point numbers
Hi Gao,
I think I see the problem:
file "../../db/ai.template" { pattern
{P,         R,      PORT,               OFFSET, BITS,  EGUL,  EGUF,   PREC,   SCAN}
{MOXA:,    ADC1,   MOXA_E1242_In_Word,   0,      16,   0.,    65535.,    3,      "I/O Intr"}
{MOXA:,    ADC2,   MOXA_E1242_In_Word,   1,      16,   0.,    65535.,    3,      "I/O Intr"}
You have set EGUF to 65535.  If you do that then the ai record will do a linear conversion, but the output values in EGU units will be the same as the input values in RAW units.  You should set the EGUF to be the maximum value of the ADC in the engineering units you want to use.  For example, if it is a 0 to 10V ADC then you can set EGUF=10 and then the ai record will be in the units of volts.  If it is -10V to 10V ADC you should set EGUL=-10.
Sent: Wednesday, November 17, 2021 2:36 AM
Subject: A problem with modbus reading floating point numbers
Hi Mark,
I am reading the ai value of moxa E1242 multifunctional IO module and I have a problem,
Cannot display floating point numbers, only integer numbers,
cannot display decimal places.
What's the reason? thanks.
#moxa1242.cmd
#!./../../bin/linux-x86_64/modbusApp
< envPaths
dbLoadDatabase("../../dbd/modbus.dbd")
modbus_registerRecordDeviceDriver(pdbbase)
drvAsynIPPortConfigure("moxa","192.168.127.254:502",0,0,1)
asynSetOption("moxa",0, "disconnectOnReadTimeout", "Y")
modbusInterposeConfig("moxa",0,5000,0)
#read moxa E1242 AI_scaledValue,7 is little endian,8 is big endian
# Enable ASYN_TRACEIO_HEX on octet server
asynSetTraceIOMask("moxa",0,4)
# Enable ASYN_TRACE_ERROR and ASYN_TRACEIO_DRIVER on octet server
asynSetTraceMask("moxa",0,9)
dbLoadTemplate("moxa1242.substitutions")
iocInit
asynReport 1
dbl
#moxa1242.substitutions
#asyn record for the underlying asyn octet port
file "$(ASYN)/db/asynRecord.db" { pattern
{P,           R,       PORT,      ADDR,   IMAX,    OMAX}
{MOXA:    OctetAsyn,    moxa,     0,      80,      80}
#ai.template
#    field(LINR,"NO CONVERSION")
#traceIO
2021/11/17 15:41:17.075 192.168.127.254:502 write 12
01 17 00 00 00 06 ff 04 02 08 00 08
2021/11/17 15:41:17.083 192.168.127.254:502 read 25
01 17 00 00 00 13 ff 04 10 13 b0 40 f0 00 00 00 00 00 dc 3b
5c 00 a0 3b a0
#caget display
[gaozh@localhost db]$ caget MOXA:ADC1_AI
MOXA:ADC1_AI                   7
note:The actual input is 7.5V.
application environment:
EPICS 7.0.3
Asyn R4-33
Modbus R2-11
Gao Zhenhua
BSRF(Beijing Synchrotron Radiation Facility)
Email:[email protected]
祝好!
高振华
电话:010-88235426
祝好!
高振华
电话:010-88235426
Re: Re: Re: A problem with modbus reading floating point numbers Mark L Rivers via Tech-talk
A problem with modbus reading floating point numbers 高振华 via Tech-talk
Re: Re: A problem with modbus reading floating point numbers 高振华 via Tech-talk
Prev: ADEiger R3-1 released Mark L Rivers via Tech-talk
Next: Re: Re: Re: A problem with modbus reading floating point numbers Mark L Rivers via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  <2021>  2022  2023  2024  2025  2026
Prev: Re: Re: A problem with modbus reading floating point numbers Mark L Rivers via Tech-talk