1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  <2021>  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  <2021>  2022  2023  2024  2025  2026 
<== Date ==> <== Thread ==>

Subject: ODP: Failed connection using e3-s7plc to Siemens S7-1500
From: Mateusz Nabywaniec via Tech-talk <[email protected]>
To: Miklós Boros <[email protected]>, Dominik Domagała <[email protected]>, "[email protected]" <[email protected]>, Timo Korhonen <[email protected]>, Mateusz Nabywaniec via Tech-talk <[email protected]>
Date: Wed, 24 Nov 2021 12:28:56 +0000
Dear all,

Many thanks for your help, especially for Miklós Boros. We succeded with connection to PLC using E3-S7PLC without using Modbus registers. 
We made integration inthe easiest way  by using TSEND and TRCV. We discovered that TCON and TDISCON were wrongly synchronised.  Before we use parameters sent by E3, TCON overwrite register with 0's.
In TIA Portal we got status 0000 (received) so we thought that there was problem with offset. After we slow down the loop we saw that value was overwritten. 


Thank you once again,
Dominik Domagała, Mateusz Nabywaniec
S2Innovation

Od: Miklós Boros <[email protected]>
Wysłane: środa, 17 listopada 2021 10:40
Do: Mateusz Nabywaniec <[email protected]>; Dominik Domagała <[email protected]>; [email protected] <[email protected]>; Timo Korhonen <[email protected]>
Temat: RE: Failed connection using e3-s7plc to Siemens S7-1500
 

Hi,

 

I made an example project including:

  • An e3 IOC with several variables sent and received.
  • Run script to run the IOC
  • Also attached the PLC code for TIA15.1 that talks with this IOC.

 

So this IOC talks with the PLC code I have attached.

 

I have some extra features in my IOC-PLC communication such as Hash checking and heartbeat check, communication diagnostics and several other, that won’t make it easy to you to understand the db file, but I hope it helps.

 

For the PLC part, import the scl files attached with External source option.

First the PLCFactory_external_source_standard_TIAv15.1.scl and than the PLCFactory_external_source_TIAv15.1.scl.

 

Call these blocks from OB1.

 

 

Before you call Utilities  make sure to have the clock memory and system memory byte enabled.

Also be aware that the _UtilitiesFB instance already exists in the External source input, so when you call the Utilities FB as above, don’t generate a new instance, but select the _UtilitiesFB.

 

I hope it helps.

 

Feladó: Mateusz Nabywaniec <[email protected]>
Küldve: Wednesday, November 17, 2021 10:15 AM
Címzett: Miklós Boros <[email protected]>; Dominik Domagała <[email protected]>; [email protected]; Timo Korhonen <[email protected]>; [email protected]
Tárgy: ODP: Failed connection using e3-s7plc to Siemens S7-1500

 

Hi, 

 

thanks for answer.

Could you show how your modbus configuration exactly looks like?

 

Cheers,

Mateusz


Od: Miklós Boros <[email protected]>
Wysłane: wtorek, 16 listopada 2021 20:58
Do: Mateusz Nabywaniec <[email protected]>; Dominik Domagała <[email protected]>; [email protected] <[email protected]>; Timo Korhonen <[email protected]>; [email protected] <[email protected]>
Temat: RE: Failed connection using e3-s7plc to Siemens S7-1500

 

Hi,

 

It’s hard to tell.

Here is what I usually have .iocsh for sending data from the PLC to the IOC.

 

#- S7 port           : 2000

#- Input block size  : 21482 bytes

#- Output block size : 0 bytes

#- Endianness        : BigEndian

s7plcConfigure("PLCName", $(IPADDR=192.168.0.1), $(S7_PORT=2000), 21482, 0, 1, $(RECVTIMEOUT=300), 0)

 

Beside this I have the modbus registers configured here to send data from the IOC to the PLC and of course the dbLoadRecords

 

In the DB I have records like this:

record(ai, "CrS-CMS:Cryo-PLC-01:GIntlockMax")

{

                field(SCAN, "I/O Intr")

                field(DTYP, "S7plc")

                field(INP,  "@$(PLCNAME)/20 T=INT16")

                field(DISS, "INVALID")

                field(DISV, "0")

                field(SDIS, "CrS-CMS:Cryo-PLC-01:PLCHashCorrectR")

                field(DESC, "Total number of Global Interlocks")

                info("plc_datablock", "DEV_CrS-CMS:Cryo-PLC-01_iDB")

                info("plc_variable", "GIntlockMax")

}

 

record(bi, "CrS-CMS:Cryo-PLC-01:SpareBOOL6")

{

                field(SCAN, "I/O Intr")

                field(DTYP, "S7plc")

                field(INP,  "@$(PLCNAME)/62 T=UINT16 B=5")

                field(DISS, "INVALID")

                field(DISV, "0")

                field(SDIS, "CrS-CMS:Cryo-PLC-01:PLCHashCorrectR")

                field(DESC, "SpareBOOL6")

                info("plc_datablock", "DEV_CrS-CMS:Cryo-PLC-01_iDB")

                info("plc_variable", "SpareBOOL6")

}

 

In the INP we calculate the offsets in the WORD array with a script, so we can insert variables easily.

 

Cheers,

Miklos

 

Feladó: Mateusz Nabywaniec <[email protected]>
Küldve: Tuesday, November 16, 2021 3:42 PM
Címzett: Miklós Boros <[email protected]>; Dominik Domagała <[email protected]>; [email protected]; Timo Korhonen <[email protected]>; [email protected]
Tárgy: ODP: Failed connection using e3-s7plc to Siemens S7-1500

 

Hi, 

 

thanks for your help. 

Sorry for not answering soon. Here is update from our side.

 

We are able to connect to PLC using E3. We used TSEND_C and TRCV_C. Unfortunetely, we are not able to set the value of data block in PLC. 

Here is our record, the name of our station is cpu1.

The variable is configured as a byte. 

 

record (bi, "testrcv")
{
field (DESC, "test description")
field (DTYP, "S7plc")
field (INP, "@cpu1/0")
field (SCAN, "I/O Intr")
field (PINI, "YES")
field (ZNAM, "off")
field (ONAM, "on")
}

 

 When we run caput command on 'testrcv' the change of the PV is only seen locally. 

The firewall is disabled and we can see communication between PLC and our VM (we are using CentOS 7) in Wireshark. 

Do you have any ideas what can be problem ?

 

Cheers, 

Mateusz Nabywaniec

 


Od: Miklós Boros <[email protected]>
Wysłane: piątek, 29 października 2021 21:06
Do: Mateusz Nabywaniec <[email protected]>; Dominik Domagała <[email protected]>; [email protected] <[email protected]>; Timo Korhonen <[email protected]>; [email protected] <[email protected]>
Temat: RE: Failed connection using e3-s7plc to Siemens S7-1500

 

Hi,

 

The timeout is most likely because the PLC does not send anything.

The s7plc module needs to get some data before the timeout.

If the telnet connects, you should see some binary data in the terminal.

 

We are using the T_SEND_C block to cyclically send a word array to the IOC. (and modbus to get data MB_SERVER)

 

TSEND_C is a nice way to handle the connection (open/close) and send in one block.

 

#TSEND_C_DB(REQ := #SendTrigger,

            CONT := TRUE,

            LEN := INT_TO_UINT(IN := #BytesToSend),

            DONE => #SendDone,

            BUSY => #SendBusy,

            ERROR => #SendError,

            STATUS => #SendStatus,

            CONNECT := #SendConnData,

            DATA := #PLCToEPICSData);

 

#SendConnData.LocalPort := INT_TO_UINT(IN := #S7Port); (we use port 2000)

#SendConnData.ConnectionType := 11;

#SendConnData.InterfaceId := #InterfaceID; (64 for X1)

#SendConnData.ID := INT_TO_WORD(IN := #S7ConnectionID); (we have 256)

I have a 100ms SendTrigger for most application.

 

Cheers,

Miklos

 

Feladó: Mateusz Nabywaniec <[email protected]>
Küldve: Friday, October 29, 2021 4:29 PM
Címzett: Miklós Boros <[email protected]>; [email protected]; Dominik Domagała <[email protected]>; [email protected]; Timo Korhonen <[email protected]>
Tárgy: ODP: Failed connection using e3-s7plc to Siemens S7-1500

 

Hi, 

 

thanks for messages. Update from our side:

 

Loading... Please enable _javascript_ or update your browser.

support.industry.siemens.com

We can connect to 102 using telnet. Here is output after running st.cmd: 

 

10/29/21 10:17:30.277 s7plcCloseConnection cpu1
10/29/21 10:17:30.469 s7plcConnect cpu1: connected to 192.168.0.10:102
10/29/21 10:17:41.546 s7plcWaitForInput cpu1: timeout after 10 seconds.
10/29/21 10:17:41.546 s7plcReceiveThread cpu1: waiting for input failed: Connection timed out
10/29/21 10:17:41.546 s7plcCloseConnection cpu1
10/29/21 10:17:41.779 s7plcConnect cpu1: connected to 192.168.0.10:102
10/29/21 10:17:52.806 s7plcWaitForInput cpu1: timeout after 10 seconds.
10/29/21 10:17:52.806 s7plcReceiveThread cpu1: waiting for input failed: Connection timed out
10/29/21 10:17:52.806 s7plcCloseConnection cpu1
10/29/21 10:17:53.068 s7plcConnect cpu1: connected to 192.168.0.10:102
10/29/21 10:18:04.070 s7plcWaitForInput cpu1: timeout after 10 seconds.
10/29/21 10:18:04.070 s7plcReceiveThread cpu1: waiting for input failed: Connection timed out
10/29/21 10:18:04.070 s7plcCloseConnection cpu1
10/29/21 10:18:04.085 s7plcConnect cpu1: connected to 192.168.0.10:102
10/29/21 10:18:15.332 s7plcWaitForInput cpu1: timeout after 10 seconds.
10/29/21 10:18:15.332 s7plcReceiveThread cpu1: waiting for input failed: Connection timed out
10/29/21 10:18:15.332 s7plcCloseConnection cpu1

 

Do you have any suggestions about that?

 

Regards, 

Mateusz Nabywaniec, 

S2Innovation, Cracow, Poland 


Od: Miklós Boros <[email protected]>
Wysłane: czwartek, 28 października 2021 17:31
Do: Mateusz Nabywaniec <[email protected]>; [email protected] <[email protected]>; Dominik Domagała <[email protected]>; [email protected] <[email protected]>; Timo Korhonen <[email protected]>
Temat: Re: Failed connection using e3-s7plc to Siemens S7-1500

 

Dear Mateusz,

 

Usually the issue is in the PLC.

You can doublecheck it by telnet into the PLC IP on port 2000. 

for example: telnet 192.168.0.100 2000

You should get an active connection and if you send something you should see it too in a binary form.

 

If you can't telnet it means the PLC does not open the port 2000 properly.

 

Check if you use the proper HW_ID for T_CON. X1 is usually 64 and X2 is 72.

 

The send block also needs a constant trigger.

 

Tell me if you need an example.

 

Cheers,

Miklós Boros

 


Feladó: Tech-talk <[email protected]>, Mateusz Nabywaniec via Tech-talk <[email protected]> nevében
Elküldve: 2021. október 28., csütörtök 15:42
Címzett: [email protected]; Dominik  Domagała; [email protected]; [email protected]
Tárgy: Failed connection using e3-s7plc to Siemens S7-1500

 

Hello,

 

Together with @Dominik  Domagała we are trying to connect with Siemens S7-1500 using e3-s7plc module (https://gitlab.esss.lu.se/e3/wrappers/communication/e3-s7plc) created by ESS.

 

We have EPICS 7.0.5 installed on CentOS 7 VM as well as E3 modules.

Here is our start cmd based on : http://epics.web.psi.ch/software/s7plc/YHLhtcPLCa.pdf

 

‘’’

require s7plc

epicsEnvSet("TOP","$(E3_CMD_TOP)/..")

s7plcConfigure cpu1,192.168.0.1,2000,240,240,1,2000,500

dbLoadRecords ("$(TOP)/db/records.db")

iocInit

‘’’

 

Unfortunetely we have the error:

`s7plcConnect cpu1: background connect to 192.168.0.1:2000 failed: Connection refused.`

 

The firewall on VM and host side are disabled.

 

PLC Program configuration:

 

-Full Access.

-Enabled PUT/GET connections.

-Data blocks ale with full access , not optimized

-TCON in stand by with status BUSY

 

TCON configuration:

-Active Est. ON

-Unspecified partner with IP address (E3 address)

-TCP connection type by port 2000.

 

When we are starting E3 server we are getting information as below

10/28/21 08:44:00.763 s7plcConnect cpu1: background connect to 192.168.0.1:2000 failed: Connection refused

We can’t get why E3-s7plc does not work on our machine. Does anybody had similar issue or successfully connected using e3-s7plc with Siemens S7-1513-1?

 

Thanks in advance,

Mateusz Nabywaniec 

 

S2Innovation, Cracow, Poland

 

 


References:
Failed connection using e3-s7plc to Siemens S7-1500 Mateusz Nabywaniec via Tech-talk
Re: Failed connection using e3-s7plc to Siemens S7-1500 Miklós Boros via Tech-talk
ODP: Failed connection using e3-s7plc to Siemens S7-1500 Mateusz Nabywaniec via Tech-talk
RE: Failed connection using e3-s7plc to Siemens S7-1500 Miklós Boros via Tech-talk
ODP: Failed connection using e3-s7plc to Siemens S7-1500 Mateusz Nabywaniec via Tech-talk
RE: Failed connection using e3-s7plc to Siemens S7-1500 Miklós Boros via Tech-talk
ODP: Failed connection using e3-s7plc to Siemens S7-1500 Mateusz Nabywaniec via Tech-talk

Navigate by Date:
Prev: Re: Alternative to EPICS Gateway Gerrit Kühn via Tech-talk <[email protected]
Next: Re: Finding the server where a PV's IOC is located Sobhani, Bayan via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  <2021>  2022  2023  2024  2025  2026 
Navigate by Thread:
Prev: ODP: Failed connection using e3-s7plc to Siemens S7-1500 Mateusz Nabywaniec via Tech-talk
Next: Plotting images in Phoebus Smith, William via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  <2021>  2022  2023  2024  2025  2026 
ANJ, 19 Mar 2026 · Home · News · About · Talk · Base · Modules · Extensions ·
· Distributions · Download · Documents · Links · Licensing ·