Thank you for replying. Happy New Year.
>a) The read back position of "DCM:ThetaM.RBV" is flickering. > You see this already when the IOC is running. > Why is that ?
flickering?
The motor is pretty stable once moving is done.
For example:
DCM:ThetaM.VAL 2025-01-03 08:54:05.156115 7.51376 <-- different -0.02; set a new VAL DCM:ThetaM.RBV 2025-01-03 08:54:05.156115 7.52741 <-- motor starts to move DCM:ThetaM.RBV 2025-01-03 08:54:05.335235 7.52131 <-- moving... DCM:ThetaM.RBV 2025-01-03 08:54:05.505113 7.51621 DCM:ThetaM.RBV 2025-01-03 08:54:05.675255 7.51376 DCM:ThetaM.RBV 2025-01-03 08:54:05.845205 7.51361 DCM:ThetaM.VAL 2025-01-03 08:54:05.845205 7.51376 <-- motor record is down moving. RBV syncs back to VAL. DCM:ThetaM.RBV 2025-01-03 08:54:05.995251 7.51356 <-- Well, the motor(axis) still moves a little bit due to inertia or other factors. DCM:ThetaM.RBV 2025-01-03 08:54:06.495140 7.51371 DCM:ThetaM.RBV 2025-01-03 08:54:06.795186 7.51376 DCM:ThetaM.RBV 2025-01-03 08:54:06.965241 7.51381 <-- However, the movement is very small.
> Mechanical load, high-precision encoder ? motor resolution is 2.7778e-05 degree / pulse encoder resolution is 5e-5 degree / count
> Is the controller running in closed loop ?
No. But its RTRY field of motor record is 10.
> b1) Increase the sleep() even more, 5.0 seconds ??
I tried 3 and 8 seconds. No success.
I will try again after holidays.
> b2) Use the patched version of the motor from ESS, I'll take a look at it. But it may not be feasible to change the underlying motor module.
Hej again,
happy new year !
Thanks for reporting back and sharing your experiences.
I think that there are 2 problems/phenomenon :
Why is that ?
Mechanics are suspected to be a contributer.
b) The initialisation is still flaky - sometimes RBV has a value of 0.0
I can see 3 ways to improve it:
which has been improved to handle this.
And comes with log-prints, which allow a better remote-debug
using this log-prints
https://github.com/EuropeanSpallationSource/motor
b3) I have seen the use of an EPICS (?) hook somewhere in one
of the motor-drivers. But after searching for hooks I still
can not find an example here on my disk or in old emails.
Another question:
How much is the motor moving ?
/Torsten
On 2025-01-03 02:54, LiangChih Chiang wrote:
> I added epicsThreadSleep(1.0) after creating motor controller and axes.
> I use camonitor to trace the VAL/RBV of motor records of three axes.
> I rebooted ioc nine times.
> Please see the following log.
> I noticed that axes Z1 and Z2 successfully restored the VAL/RBV from the
> controller every time.
> But the behavior of axis ThetaM is strange.
> Two out of nine reboots, the VAL field of ThetaM record is successfully
> restored.
> One out of nine reboots, the VAL field of ThetaM record is set to zero.
> Six out of nine reboots, the VAL field of ThetaM record is set to
> (previous value - 0.02).
> Why -0.02?
> DCM:Z1.VAL 2025-01-02 16:28:46.483683 -0.04
> DCM:Z1.RBV 2025-01-02 16:28:46.483683 -0.0401
> DCM:Z2.VAL 2025-01-02 20:41:47.713687 0.0657
> DCM:Z2.RBV 2025-01-02 20:41:47.713687 0.0653
> DCM:ThetaM.VAL 2025-01-02 16:28:50.353358 7.53376 <--
> DCM:ThetaM.RBV 2025-01-02 16:28:50.353358 7.53376
> ioc reboot
> DCM:Z1.VAL 2025-01-03 08:46:20.410653 -0.0401
> DCM:Z1.RBV 2025-01-03 08:46:20.410653 -0.04
> DCM:Z2.VAL 2025-01-03 08:46:20.350513 0.0653
> DCM:Z2.RBV 2025-01-03 08:46:20.350513 0.0657
> DCM:ThetaM.VAL 2025-01-03 08:46:20.500699 7.53376 <-- same
> as previous
> DCM:ThetaM.RBV 2025-01-03 08:46:20.500699 7.53376
> ioc reboot
> DCM:Z1.VAL 2025-01-03 08:54:04.045355 -0.04
> DCM:Z1.RBV 2025-01-03 08:54:04.045355 -0.0401
> DCM:Z2.VAL 2025-01-03 08:54:03.985246 0.0657
> DCM:Z2.RBV 2025-01-03 08:54:03.985246 0.0653
> different -0.02
> motor move
> ioc reboot
> DCM:Z1.VAL 2025-01-03 09:00:47.829590 -0.0401
> DCM:Z1.RBV 2025-01-03 09:00:47.829590 -0.04
> DCM:Z2.VAL 2025-01-03 09:00:47.769508 0.0653
> DCM:Z2.RBV 2025-01-03 09:00:47.769508 0.0657
> DCM:ThetaM.VAL 2025-01-03 09:00:49.279478 7.49377 <--
> different -0.01999
> DCM:ThetaM.RBV 2025-01-03 09:00:49.279478 7.49611 <--
> motor move
> DCM:ThetaM.RBV 2025-01-03 09:00:49.449660 7.49371
> DCM:ThetaM.RBV 2025-01-03 09:00:49.619596 7.49351
> DCM:ThetaM.VAL 2025-01-03 09:00:49.619596 7.49377
> DCM:ThetaM.RBV 2025-01-03 09:00:49.939543 7.49356
> DCM:ThetaM.RBV 2025-01-03 09:00:50.269661 7.49376
> Manually move ThetaM to 7.553761
> DCM:ThetaM.VAL 2025-01-03 09:04:05.044900 7.55378
> DCM:ThetaM.VAL 2025-01-03 09:04:05.045646 7.55376
> DCM:ThetaM.RBV 2025-01-03 09:04:05.371519 7.49566
> DCM:ThetaM.RBV 2025-01-03 09:04:05.541574 7.50071
> DCM:ThetaM.RBV 2025-01-03 09:04:05.711567 7.50711
> DCM:ThetaM.RBV 2025-01-03 09:04:05.881592 7.51536
> DCM:ThetaM.RBV 2025-01-03 09:04:06.061484 7.52551
> DCM:ThetaM.RBV 2025-01-03 09:04:06.231575 7.53506
> DCM:ThetaM.RBV 2025-01-03 09:04:06.402009 7.54296
> DCM:ThetaM.RBV 2025-01-03 09:04:06.571571 7.54866
> DCM:ThetaM.RBV 2025-01-03 09:04:06.741529 7.55221
> DCM:ThetaM.RBV 2025-01-03 09:04:06.911574 7.55296
> DCM:ThetaM.VAL 2025-01-03 09:04:06.911574 7.55376
> DCM:ThetaM.RBV 2025-01-03 09:04:07.071671 7.55301
> DCM:ThetaM.RBV 2025-01-03 09:04:07.241982 7.55326
> DCM:ThetaM.RBV 2025-01-03 09:04:07.561637 7.55381
> DCM:ThetaM.RBV 2025-01-03 09:04:07.881647 7.55346
> DCM:ThetaM.RBV 2025-01-03 09:04:08.211724 7.55356
> DCM:ThetaM.RBV 2025-01-03 09:04:08.531501 7.55376
> ioc reboot
> DCM:Z1.VAL 2025-01-03 09:05:56.102804 -0.04
> DCM:Z1.RBV 2025-01-03 09:05:56.102804 -0.0401
> DCM:Z2.VAL 2025-01-03 09:05:56.042681 0.0657
> DCM:Z2.RBV 2025-01-03 09:05:56.042681 0.0653
> DCM:ThetaM.VAL 2025-01-03 09:05:56.174482 7.55376 <-- same
> as previous
> DCM:ThetaM.RBV 2025-01-03 09:05:56.174482 7.55376 <-- but
> motor move
> DCM:ThetaM.RBV 2025-01-03 09:05:57.012778 7.55206
> DCM:ThetaM.RBV 2025-01-03 09:05:57.502889 7.54196
> DCM:ThetaM.RBV 2025-01-03 09:05:57.822823 7.54366
> DCM:ThetaM.RBV 2025-01-03 09:05:57.992678 7.54791
> DCM:ThetaM.RBV 2025-01-03 09:05:58.162720 7.55171
> DCM:ThetaM.RBV 2025-01-03 09:05:58.342759 7.55266
> DCM:ThetaM.RBV 2025-01-03 09:05:58.492806 7.55271
> DCM:ThetaM.RBV 2025-01-03 09:05:58.662711 7.55371
> DCM:ThetaM.RBV 2025-01-03 09:05:58.962828 7.55376
> DCM:ThetaM.RBV 2025-01-03 09:05:59.132771 7.55381
> DCM:ThetaM.RBV 2025-01-03 09:06:02.762853 7.55386
> ioc reboot
> DCM:Z1.VAL 2025-01-03 09:09:37.385148 -0.0401
> DCM:Z1.RBV 2025-01-03 09:09:37.385148 -0.04
> DCM:Z2.VAL 2025-01-03 09:09:37.325204 0.0653
> DCM:Z2.RBV 2025-01-03 09:09:37.325204 0.0657
> DCM:ThetaM.VAL 2025-01-03 09:09:38.354986 0 <--
> different, zero!
> DCM:ThetaM.RBV 2025-01-03 09:09:38.354986 7.55181 <--
> motor move
> DCM:ThetaM.RBV 2025-01-03 09:09:38.535008 7.54706
> DCM:ThetaM.RBV 2025-01-03 09:09:38.704917 7.54026
> DCM:ThetaM.RBV 2025-01-03 09:09:38.875048 7.53131
> DCM:ThetaM.RBV 2025-01-03 09:09:39.045385 7.52046
> DCM:ThetaM.RBV 2025-01-03 09:09:39.215134 7.50731
> DCM:ThetaM.RBV 2025-01-03 09:09:39.385166 7.49361
> DCM:ThetaM.RBV 2025-01-03 09:09:39.555112 7.48036
> DCM:ThetaM.RBV 2025-01-03 09:09:39.725153 7.46636
> DCM:ThetaM.RBV 2025-01-03 09:09:39.894942 7.45281
> DCM:ThetaM.RBV 2025-01-03 09:09:40.064989 7.43961
> DCM:ThetaM.RBV 2025-01-03 09:09:40.234971 7.42526
> DCM:ThetaM.RBV 2025-01-03 09:09:40.405113 7.41221
> DCM:ThetaM.RBV 2025-01-03 09:09:40.585072 7.39761
> DCM:ThetaM.RBV 2025-01-03 09:09:40.755044 7.38401
> DCM:ThetaM.RBV 2025-01-03 09:09:40.925113 7.37066
> DCM:ThetaM.RBV 2025-01-03 09:09:42.095077 7.31426
> DCM:ThetaM.VAL 2025-01-03 09:09:42.095077 7.31426 <-- I
> stop the motor.
> DCM:ThetaM.RBV 2025-01-03 09:09:46.705116 7.31421
> ioc reboot
> DCM:Z1.VAL 2025-01-03 09:12:18.906995 -0.04
> DCM:Z1.RBV 2025-01-03 09:12:18.906995 -0.0401
> DCM:Z2.VAL 2025-01-03 09:12:18.846984 0.0657
> DCM:Z2.RBV 2025-01-03 09:12:18.846984 0.0653
> DCM:ThetaM.VAL 2025-01-03 09:12:21.346979 7.29431 <--
> different −0.01995
> DCM:ThetaM.RBV 2025-01-03 09:12:21.346979 7.29431 <--
> motor move
> ioc reboot
> DCM:Z1.VAL 2025-01-03 09:18:20.230656 -0.0401
> DCM:Z1.RBV 2025-01-03 09:18:20.230656 -0.04
> DCM:Z2.VAL 2025-01-03 09:18:20.170608 0.0653
> DCM:Z2.RBV 2025-01-03 09:18:20.170608 0.0657
> DCM:ThetaM.VAL 2025-01-03 09:18:20.311337 7.27437 <--
> different −0.01994
> DCM:ThetaM.RBV 2025-01-03 09:18:20.311337 7.29431 <--
> motor move
> DCM:ThetaM.RBV 2025-01-03 09:18:21.150538 7.29231
> DCM:ThetaM.RBV 2025-01-03 09:18:21.320404 7.28771
> DCM:ThetaM.RBV 2025-01-03 09:18:21.500407 7.28171
> DCM:ThetaM.RBV 2025-01-03 09:18:21.670389 7.27681
> DCM:ThetaM.RBV 2025-01-03 09:18:21.840686 7.27421
> DCM:ThetaM.RBV 2025-01-03 09:18:22.010457 7.27406
> DCM:ThetaM.VAL 2025-01-03 09:18:22.010457 7.27437
> DCM:ThetaM.RBV 2025-01-03 09:18:22.330451 7.27421
> DCM:ThetaM.RBV 2025-01-03 09:18:22.660350 7.27431
> DCM:ThetaM.RBV 2025-01-03 09:18:22.960309 7.27436
> DCM:ThetaM.RBV 2025-01-03 09:18:23.130896 7.27441
> ioc reboot
> DCM:Z1.VAL 2025-01-03 09:22:00.722740 -0.04
> DCM:Z1.RBV 2025-01-03 09:22:00.722740 -0.0401
> DCM:Z2.VAL 2025-01-03 09:22:00.662695 0.0657
> DCM:Z2.RBV 2025-01-03 09:22:00.662695 0.0653
> DCM:ThetaM.VAL 2025-01-03 09:22:02.912859 7.25442 <--
> different −0.01995
> DCM:ThetaM.RBV 2025-01-03 09:22:02.912859 7.25441 <--
> motor move
> ioc reboot
> DCM:Z1.VAL 2025-01-03 09:33:58.400417 -0.0401
> DCM:Z1.RBV 2025-01-03 09:33:58.400417 -0.04
> DCM:Z2.VAL 2025-01-03 09:33:58.340350 0.0653
> DCM:Z2.RBV 2025-01-03 09:33:58.340350 0.0657
> DCM:ThetaM.VAL 2025-01-03 09:33:59.330344 7.23447 <--
> different −0.01995
> DCM:ThetaM.RBV 2025-01-03 09:33:59.330344 7.25241 <--
> motor move
> DCM:ThetaM.RBV 2025-01-03 09:33:59.500272 7.24781
> DCM:ThetaM.RBV 2025-01-03 09:33:59.680584 7.24186
> DCM:ThetaM.RBV 2025-01-03 09:33:59.850291 7.23701
> DCM:ThetaM.RBV 2025-01-03 09:34:00.020355 7.23431
> DCM:ThetaM.RBV 2025-01-03 09:34:00.190267 7.23416
> DCM:ThetaM.VAL 2025-01-03 09:34:00.190267 7.23447
> DCM:ThetaM.RBV 2025-01-03 09:34:00.510337 7.23431
> DCM:ThetaM.RBV 2025-01-03 09:34:00.840415 7.23441
> DCM:ThetaM.RBV 2025-01-03 09:34:01.140389 7.23446
> DCM:ThetaM.RBV 2025-01-03 09:34:01.310255 7.23451
> On Thu, Jan 2, 2025 at 11:26 AM LiangChih Chiang <[email protected]
> <mailto:[email protected]>> wrote:
> Hi,
> >To explain a little more, it is important that the driver has
> completed the first poll cycle for the position and status of each
> axis before iocInit.
> >This is because the motor record looks at those positions during
> iocInit, and if there are non-zero it uses those values as the
> current position.
> >You can add the following to your startup script after you create
> the controller and axes to sleep for 1 second.
> I did add epicsThreadSleep(1.0).
> There are 5 motors(axis 1 to 5) connected to the motor controller.
> After epicsThreadSleep(1.0) added, it seems that the VAL/RBV of
> motor records of axis 2 to 5 can be successfully loaded back from
> the controller after IOC reboot.
> But the behavior of axis 0 (this axis is the most important) is strange.
> After IOC reboot, the motor record of axis 0 will move.
> It seems that the VAL field is set to a new value
> and I can't figure out the relationship between the new and old values.
> The axis 0 is the main axis(Bragg angle) of a double crystal
> monochromator,
> and it has corresponding pseudo motor to represent the Energy of x-
> ray beam.
> On Wed, Nov 20, 2024 at 11:04 PM Mark Rivers
> each axis before iocInit. This is because the motor record
> looks at those positions during iocInit, and if there are non-
> zero it uses those values as the current position. You can add
> the following to your startup script after you create the
> Let us know if this does not fix the problem.
> Mark
> *From:* Tech-talk <[email protected] <mailto:tech-
> [email protected]>> on behalf of Torsten Bögershausen via
> Tech-talk <[email protected] <mailto:[email protected]>>
> *Sent:* Wednesday, November 20, 2024 5:15 AM
> *To:* LiangChih Chiang <[email protected]
> <mailto:[email protected]>>; [email protected]
> <mailto:[email protected]> <[email protected]
> *Subject:* Re: I implemented the Model 3 of EPICS motor driver
> support, but the VAL and RBV of motor record are zero after IOC
> reboot.
> Hej,
> without having seen ypur code, I would speculate that you run
> into a not-unknown issue using Model 3 motors, connected via
> a serial cable, USB or Ethernet?
> The value that the motorRecord needs is read from the driver,
> wich must have been able to read it from your hardware.
> Here are ESS we have a patched motor, which can handle this.
> If you use the upstream version, the easist workaround may be
> to add a sleep() after the createController() line in your st.cmd
> HTH
> /Torsten
> On 2024-11-20 09:47, LiangChih Chiang via Tech-talk wrote:
> > Hello, EPICS mates.
> > I implemented the Model 3 of EPICS motor driver support for
> some motor
> > controller,
> > but the VAL and RBV of the motor record are zero after IOC
> reboot.
> > I think the motor record doesn't restore the values of motor
> pulse and
> > encoder count from the motor controller after IOC reboot.
> > What member functions of asynMotorController and
> asynMotorAxis classes
> > should I implement?
> > Best regards.
- Re: I implemented the Model 3 of EPICS motor driver support, but the VAL and RBV of motor record are zero after IOC reboot. Torsten Bögershausen via Tech-talk
- Re: I implemented the Model 3 of EPICS motor driver support, but the VAL and RBV of motor record are zero after IOC reboot. LiangChih Chiang via Tech-talk
<2025>
2026
<2025>
2026