My concern is that comms errors, where a glitch causes a character to be
mutated into a CR, will pass through without being detected. Granted the
probability is very low on this happening, but we have had very 'noisy'
serial links in the past.
Also be aware that a waveform record can be configured for multiple
lines of data (ie. a specified number of command terminators are
expected). You should test that your modification does not adversely
affect this behavior.
Perhaps a more elaborate scheme for specifying the command terminator,
such that a given site/device can be configured for specific anomolies,
is needed. Maybe a specification something like:
"\%2rn" (ie. upto 2 CR followed by a aingle LF)
"\%*r\n" (ie. any number of CR followed by a single LF)
"\%*r\%2n" (ie. any number of CR followed by upto 2 LF)
could be implemented. Note in this case getFrame() having to prescan the
command terminator to keep local information. hmmm I guess setWriteCmt()
would not have to be changed but formatCmt() would then we let the getFrame()
routine dynamically interpret the command terminator.
Of course the bizarre case where "\%" is a valid CMT would have to be
handled (eg. "\\%" could mean to not interpret).
AH
> From [email protected] Thu Apr 18 09:15:05 2002
> Date: Thu, 18 Apr 2002 09:14:50 -1000
.php>
> Hi,
> we are having problems with the strategy used by drvAscii to find line
> terminators. We are considering changing it locally to solve our particular
> problem and wonder if this would impact anybody else if the change were
> propagated.
> Our particular problem involves a compumotor 6000 controller. Most of the time
> it terminates strings with CR LF as requested but for some reason it sometimes
> issues CR CR LF. This completely bamboozles drvAscii which has been told to
> expect CR LF.
> The termination detection of drvAscii resets the string pointer of the prototype
> termination string back to zero if it encounters 2nd or 3rd characters that are
> not of the expected sequence. I.e. (the spaces aren't real, just for clarity):
> prototype string terminator: CR LF
> received string: * T P E 5
> CR CR LF /0
> prototype string terminator pointer: 0 0 0 0 0 0 1
> 0 1
> next expected terminator character CR CR CR CR CR CR LF CR LF
> drvAscii then times out and the string is lost.
> The solution seems to be to not reset the terminator string pointer:
> CR CR LF /0
> 1
> next expected terminator character CR CR CR CR CR CR LF LF
> Assuming the extra CR still in the string doesn't cause the subsequent scanf in
> drvAscii problems, then the received string should be returned to epics (we
> haven't tried it yet).
> Hope the examples are clearer than mud!
> So, can anyone see any problems with this proposed change, or, a better solution
> cheers
> Ian A Smith Telephone: (808) 961 3756
> Joint Astronomy Centre Fax: (808) 961 6516
> 660 N. A'ohoku Place (808) 969 6591
> University Park Web: http://www.jach.hawaii.edu
> Hilo
> Hawaii
> 96720
Re: drvAscii - termintor strategy Peregrine M. McGehee
Re: strange behaviour of dbLoadtemplate Luedeke Andreas WSLA/209
<2002>
2025
2026
Re: strange behaviour of dbLoadtemplate Marty Kraimer
Re: drvAscii - termintor strategy Allan Honey
<2002>
2025
2026