1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  <2006>  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  <2006>  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Subject: Re: looking for OSI version of epid record
To: "LYNCH, Damien" <[email protected]>
Cc: "'Tim Mooney'" <[email protected]>, [email protected]
Date: Mon, 21 Aug 2006 08:58:03 -0500
LYNCH, Damien wrote:
I see the EPID record producing a value that should be added to
the ao record's VAL field, implying the ao record should have
OIF=Incremntal. But with the EPID record putting OVAL into what's
pointed to by OUTL (ie the ao record) I'd expect to have
OMSL=supervisory in the ao record.
Hang in there and see what happens as the controlled value responds to the new output value. With KP!=0 and KI==KD==0, you should see ERR=VAL-CVAL, and OVAL=KP*ERR. If not, do a "dbpr" on the record and send that. There might be some control field we're not thinking about with an unexpected value.
ERR is calculated correctly and OVAL contains the value == KP * ERR.
But this value now in OVAL is one that I would want to add to the VAL
field in the ao record pointed to by OUTL (which in my case writes to
a magnet power supply). Is it up then to the database designer to
perform an OVAL + ao.VAL calculation and get the result into ao.VAL?
Damien has a point -- do the EPID record authors realise that the AO record only looks at OIF and performs the required integration when OMSL=Supervisory and the delta is being fetched through DOL? The integration is implemented in fetch_value() which is only called if ((pao->dol.type != CONSTANT) && (pao->omsl == menuOmslclosed_loop)), thus if DOL is not set and a value is poked straight into the AO's VAL field using the EPID.OUTL link, no integration will take place.
This behaviour of the AO record was probably designed for the old PID record which expected you to use DOL with OIF, and is not something we can change now.
- Andrew
There is considerable overlap between the intelligence
of the smartest bears and the dumbest tourists.
  -- Yosemite National Park Ranger
Re: looking for OSI version of epid record Andrew Johnson
Re: looking for OSI version of epid record Tim Mooney
RE: looking for OSI version of epid record LYNCH, Damien
Prev: RE: looking for OSI version of epid record LYNCH, Damien
Next: Re: looking for OSI version of epid record Andrew Johnson
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  <2006>  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026