1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  <20102011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  <20102011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Subject: Re: writing to aao crashes ioc
To: Benjamin Franksen <[email protected]>
Cc: [email protected]
Date: Tue, 20 Apr 2010 14:21:47 +0200
Hi Ben,
You are right. The link gets initialized too early. I allocate the memory in the device support but that's already too late.
I suspect that the idea was to allow bptr to be a pointer to hardware registers or third party buffers and thus save the time for copying the data from hardware to bptr. The code even says:
/* init records sets the bptr to point to the data */
if((status=(*pdset->init_record)(paao))) return(status);
But that can never have worked properly with local links.
aai does the same late allocation. Writing to or reading from aai through a db link crashes the ioc too.
Modifying the records to do the allocation is tricky. There might be device supports out there that do allocation for bptr without checking for not NULL. My version of the Soft Channel support does the check but there may be others. In that case the device support and links from other records would use different buffers.
It may be safer to move pdset->init_record to pass 0. I have not found any other record type that does this. Can there be any problem with this approach?
Who uses aai/aao and which device supports exist?
Dirk
Benjamin Franksen wrote:
On Tuesday 20 April 2010, Dirk Zimoch wrote:
Tim Mooney wrote:
Dirk,  I was seeing something similar (though in 3.14.11),
and "dbpr <recordname>,5" showed "DTYP: <nil>",
until I added the line
device(aao,CONSTANT,devAaoSoft,"Soft Channel")
to the .dbd file.
Hi Tim.
That is not the problem:
DTYP: Soft Channel
The ioc also crashes when the aao record is not processed! Thus DTYP
cannot be the problem.
I believe the aao record support is at fault.
The problem is that it does not allocate bptr itself but leaves this to device support. However, when device support's init_record method is called, it is too late. Because by then links have already been initialized, thus cvt_db_addr has been called, which sets the field address to bptr, i.e. NULL.
This explains why regular puts work but puts via db links lead to a crash. If you dbpf from the ioc shell or do caput, the cvt_db_addr gets called and since this is after device support init, bptr will contain a valid pointer to the array.
You could verify my theory by issuing a 'caput aao1.OUT aao2'. After this, the IOC should not crash when processing aao1. It shoudl still crash when processing ao1, until you re-initialize thits OUT link, too.
Solution: Fix aao (and probably aai) record support to either allocate bptr itself or else call device support's init_record during the first pass of record support initialization.
Cheers
Ben
Re: writing to aao crashes ioc Andrew Johnson
writing to aao crashes ioc Dirk Zimoch
Re: writing to aao crashes ioc Tim Mooney
Re: writing to aao crashes ioc Dirk Zimoch
Re: writing to aao crashes ioc Benjamin Franksen
Prev: Re: writing to aao crashes ioc Benjamin Franksen
Next: Re: writing to aao crashes ioc Andrew Johnson
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  <20102011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Prev: Re: writing to aao crashes ioc Eric Bjorklund