1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  <20122013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  <20122013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Subject: reading negative 16-bit numbers over Asyn modbus
To: <[email protected]>
Date: Thu, 5 Apr 2012 17:50:49 +0000
I have a Eurotherm 3217 controller that I'm talking to using modbus RTU over RS485 (via a Moxa terminal server). It seems to work fine, but I'm having trouble reading a negative number.
The Asyn support is configured to use modbus function code 3, like this: (from the eurotherm2k support module eurothermModbus.c):
mkname(str, strmaxlen, asynPortName, modbusAddress, loopNumber, 0, "PV");
asynRet = drvModbusAsynConfigure(str, asynPortName, modbusAddress,
		MODBUS_READW, loopStart+PV_OFFSET, 3,
		0, EUROTHERM_POLL_MS, "");
Where:
loop number is 1.
modbus addr is 1.
MODBUS_READW is 3 (this is the function code, so it's reading 16-bit words).
loopStart+PV_OFFSET is 1+0, so 1.
3 is the modbus length, which means 3*16-bit.
The 0 data type is Unsigned 16-bit binary integers.
This works fine for positive numbers, but negative fails. I tried changing the modbus data type to 4, which should mean INT16 2's complement, but it seems to fail at some point and just return zero in the record.
If I turn on asyn trace, the negative word I am reading back is "fd 1c". The actual reading I expect is about -750. So this looks to be correct if assuming 2's complement encoding.
Anybody successfully read negative integers over modbus?
I'm using modbus 2-2, and asyn 4-14.
Update... looking at drvModbusAsyn.c, I see that convertFromBinary() only implements 3 types of type conversion (modbus data types 1, 2 and 3 in the list in the documentation?)
Cheers,
Matthew
Dr Matthew Pearson
Senior Software Systems Engineer
Diamond Light Source
Chilton, Didcot
OX11 0DE
UK
MX Controls Team Leader
Beamline Controls - I19, I24, B24
RE: reading negative 16-bit numbers over Asyn modbus Mark Rivers
Prev: Re: Question about 85XX dual core CPU board for VxWorks/EPICS Andrew Johnson
Next: RE: reading negative 16-bit numbers over Asyn modbus Mark Rivers
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  <20122013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Prev: Re: Question about 85XX dual core CPU board for VxWorks/EPICS 王林
