1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  <2013>  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  <2013>  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Subject: RE: motor record: continuously update limit switches
To: "'Konrad, Martin'" <[email protected]>, "[email protected]" <[email protected]>, "[email protected]" <[email protected]>, "[email protected]" <[email protected]>
Date: Fri, 26 Jul 2013 20:40:24 +0000
Hi Martin,
> Unfortunately this seems not to be the case with the PC6K device
> support. MSTA seems not to be updated while the motor is stopped. Can
> this be considered a bug?
Yes, I think so.
I tested the OMS-58 and MSTA does update if the limit is disconnected and STUP is set to 1.  It only shows 1 limit, not both, but I believe that is a limitation of the OMS-58 hardware, it only reports the limit switch in the direction of last travel.
I also tested the ACS MCB-4B.  When no limits were pressed MSTA was 0x2.  When I disconnected the cable and pressed STUP then MSTA changed of 0x2006. So bits 3 and 14 (numbering from 1) were changed from 0 to 1 as expected.  It is thus showing both of the limits.
There are 2 drivers for the ACS MCB-4B, a old Model 1 driver and a new Model 3 driver.  The test I did was on an IOC running the old Model 1 driver.  The PC6K is also a Model 1 driver, so it should be able to update MSTA in response to STUP just like the MCB-4B does.
An important difference I see in the device support for the MCB-4B and PC6K is the following:
devMCB4B.cc
    case GET_INFO:
        /* These commands are not actually done by sending a message, but
           rather they will indirectly cause the driver to read the status
           of all motors */
        break;
devPC6K.cc
        case GET_INFO:
               of all motors */
            sendMsg = false;
            break;
So the PC6K is setting sendMsg=false for the GET_INFO command, but the MCB4B is not.  The GET_INFO command is what STUP does.  I would suggest commenting out that line and seeing if then the STUP works.
-----Original Message-----
Sent: Friday, July 26, 2013 3:07 PM
To: Mark Rivers; [email protected]; [email protected]; [email protected]
Cc: [email protected]
Subject: Re: motor record: continuously update limit switches
Hi!
Thanks for you reply, Mark.
> HLS, RHLS, LLS and RLLS only update when you try to move the motor in
> the direction of the offending switch.
> However, the MSTA field will update if you write 1 to the STUP
> field.
> Is your goal to make the user aware of the limit status by changing
> something in the GUI?
Yes, exactly. Maybe also for a state-machine that implements some sort
of a calibration procedure.
> It would be nice if HLS, RHLS, LLS and RLLS reflected the actual
> limit status.  In fact the motor record documentation is wrong.  For
> HLS and RHLS it says:
> " If either of these fields is nonzero, then the motor is at the
> positive-limit switch, where the positive sense is that of the
> user-coordinate system for HLS, and that of the raw (step-number)
> coordinate system for RHLS."
> That is not true, it does not reflect the state of the switch.  It
> only reflects the error status if the switch is hit and the user
> tries to move in the direction of that switch.
@Ron/Tim/Joe: Can you fix the documentation with the next release,
please? And while we're at it: The Documentation website says "Last
modified: June 25, 2003" which is most likely wrong as well.
Thank you very much,
Martin
motor record: continuously update limit switches Konrad, Martin
Re: motor record: continuously update limit switches Konrad, Martin
Prev: Re: motor record: continuously update limit switches Konrad, Martin
Next: RE: CA question with two identical servers Emmanuel Mayssat
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  <2013>  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Next: Re: motor record: continuously update limit switches Konrad, Martin