1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  <20132014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  <20132014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Subject: RE: BiRa Ethernet Power Supply Controllers
To: Rod Nussbaumer <[email protected]>, epics Techtalk <[email protected]>
Date: Thu, 12 Sep 2013 10:28:29 -0700
We use BiRa power supplies with all our magnets.
We don't use the ethernet interface (and I don't think they are using it at SLAC either) for the following reason:
*** Don't trust the internal regulation of your power supplies ***
In practice, the PS are regulated at 10^-3 (= delta I / I), so 10A has 10mA noise.
If you want regulation at 10^-4 level, you need external feedback electronics.
(transducer --(error on I)--> controller board --(convoluted with input signal)---> input of the PS)
That feedback loop cannot use ethernet because it is too slow!!!
In practice, the current setting we trust is the one read on our calibrated transducer.
Another key advantage of this setting is that you can change the BiRa PS with a new one and the system will behave exactly the same (even so the PS may be slightly different in terms of output offset/noise/etc).
Obviously if you use the PS for something other than magnets, where the internal regulation is sufficient, then the Ethernet/EPICS interface may be useful.
I went to their website and read they support EPICS
 http://www.bira.com/products/bigen/
now I am curious too.
Emmanuel
> Date: Wed, 11 Sep 2013 16:39:24 -0700
> From: [email protected]
> To: [email protected]
> Subject: BiRa Ethernet Power Supply Controllers
> Hi all.
> Has anyone had any exeprience with BiRa Ethernet Power Supply
> Controllers? BiRa is advertising that SLAC has used them, so I would be
> happy to hear from anyone there with some firsthand knowledge.
> What is the nature of the EPICS support? Being ethernet, I was hoping
> for something SCPI-like, but the datasheet doesn't suggest that.
> Our power supply group would also like to contact anyone that may have
> knowledge of the hardware, installation, and those aspects of these devices.
> Thanks.
> Rod Nussbaumer
> ISAC Controls, TRIUMF
> Vancouver, Canada.
BiRa Ethernet Power Supply Controllers Rod Nussbaumer
Prev: RE: EtherCAT and NI slave chassis [SEC=UNCLASSIFIED] ronaldo.mercado
Next: RE: BiRa Ethernet Power Supply Controllers Allison, Stephanie
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  <20132014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Prev: BiRa Ethernet Power Supply Controllers Rod Nussbaumer