The value was being converted from a double to a float for one of the debugging statements, which explains the small difference in the value printed.
Sent: Tuesday, May 06, 2014 12:20 AM
To: Mark Rivers; Tonia Batten; [email protected]
Subject: Re: Newport XPS-Q8 and Motor Record - armv5teb architecture
>2014/05/02 10:10:56.266 devMotorAsyn::send_msg: SMTR1608-9-B20-05:brag command=7, pact=1, value=45000.000000
>devAsynMotor::build_trans, calling queueRequest, pmsg=0x60b3cc, command=7, interface=1, dvalue=45000.000046
>This is fine, the value 45000. has been copied to pmsg->dvalue
Is it?
The first trace says:
45000.000000
The second says:
45000.000046
Could you make a printout showing the address of the double (not only the address of the struct),
and the sizeof(double) ?
Could we make a hexdump of the double value ?
On 5/4/14 12:32 AM, Mark Rivers wrote:
> Folks,
> Tonia Batten is having a very strange problem that I cannot understand, perhaps someone on tech-talk has an idea.
> She is using the Newport XPS motor driver. It works fine when it is run on an Intel machine. However, when it is run on an armv5teb she is seeing a behavior I cannot understand. This happens both with the older model 2 XPS driver (C code), as well as the newer model 3 driver (C++).
> The asyn device support defines the following message structure:
> typedef struct {
> motorCommand command;
> interfaceType interface;
> int ivalue;
> double dvalue;
> } motorAsynMessage;
> In the code that is called from the motor record it does the following:
> /* Make a copy of asynUser. This is needed because we can have multiple
> * requests queued. It will be freed in the callback */
> pasynUser = pasynManager->duplicateAsynUser(pasynUser, asynCallback, 0);
> pmsg = pasynManager->memMalloc(sizeof *pmsg);
> pmsg->ivalue=0;
> pmsg->dvalue=0.;
> pmsg->interface = float64Type;
> pasynUser->userData = pmsg;
> switch (command) {
> case SET_VELOCITY:
> pmsg->command = motorVelocity;
> pmsg->dvalue = *param;
> break;
> /* Queue asyn request, so we get a callback when driver is ready */
> pasynUser->reason = pPvt->driverReasons[pmsg->command];
> status = pasynManager->queueRequest(pasynUser, 0, 0);
> So in the case of the SET_VELOCITY it copies the desired velocity to pmsg->dvalue. It calls pasynManager->queueRequest to call back device support when the driver is ready.
> This is the start of the code in the device support callback function:
> static void asynCallback(asynUser *pasynUser)
> motorAsynPvt *pPvt = (motorAsynPvt *)pasynUser->userPvt;
> motorRecord *pmr = pPvt->pmr;
> motorAsynMessage *pmsg = pasynUser->userData;
> int status;
> int commandIsMove = 0;
> Tonia has added some debugging to the device support code. When the velocity is being set, for example the code called by the motor record prints the following:
> However, when pasynManager does the callback to device support from the queueRequest she sees the following:
> devAsynMotor::asynCallback, entry, pmsg=0x60b3cc, command=7, interface=1, dvalue=0.000000
> 2014/05/02 10:10:56.308 devMotorAsyn::asynCallback: SMTR1608-9-B20-05:brag command=7, ivalue=0, dvalue=0.000000, pasynUser->reason=7
> 2014/05/02 10:10:56.310 asynMotorController:writeFloat64:: axis=0, function=7, value=0.000000
> Note that pmsg has the same address (=0x60b3cc,), so it is getting a pointer to the same address as before the queueRequest.
> However, pmsg->dvalue is now 0, rather than 45000.
> Any idea how this could happen?
> Thanks,
> Mark
> From: Tonia Batten [[email protected]]
> Sent: Friday, May 02, 2014 12:18 PM
> To: Mark Rivers
> Subject: RE: Newport XPS-Q8 and Motor Record - armv5teb architecture
> Hi Mark,
> I am experiencing the same problem using the model 3 XPS driver. I have included details from my testing below. I can’t see anything in asyn-4-22/asyn/asynDriver/asynManager.c queueRequest function that would cause this. Any insight you can provide is appreciated.
> Regards, Tonia
> Here is my st.cmd file.
> #!./bin/linux-armv5teb/ideasMonoMtr
> ## You may have to change ideasMonoMtr to something else
> ## everywhere it appears in this file
> #< envPaths
> ## Register all support components
> dbLoadDatabase("./dbd/ideasMonoMtr.dbd",0,0)
> ideasMonoMtr_registerRecordDeviceDriver(pdbbase)
> ## Load record instances
> dbLoadRecords("./db/IDEAS_MonoMtr.db")
> dbLoadRecords("./db/IDEAS_MonoPseudoMtr.db")
> dbLoadRecords("$(MOTOR)/db/motorUtil.db", "P=SMTR1608-9-B20-05:")
> # asyn port, IP address, IP port, number of axes,
> # active poll period (ms), idle poll period (ms),
> # enable set position, set position settling time (ms)
> XPSCreateController("XPS1", "192.168.0.254", 5001, 1, 10, 5000, 0, 5000)
> # asynPort, IP address, IP port, poll period (ms)
> XPSAuxConfig("XPS_AUX1", "192.168.0.254", 5001, 500)
> # XPS asyn port, axis, groupName.positionerName, stepSize
> XPSCreateAxis("XPS1",0,"S.Pos","10000")
> asynSetTraceMask("XPS1",0,0xFF)
> asynSetTraceIOMask("XPS1",0,0x2)
> # XPS asyn port, max points, FTP username, FTP password
> # Note: this must be done after configuring axes
> XPSCreateProfile("XPS1", 2000, "Administrator", "Administrator")
> iocInit
> Here is the asyn Trace information when I try and move the motor.
> 2014/05/02 10:10:56.253 SMTR1608-9-B20-05:brag devMotorAsyn::update_values, needUpdate=0
> 2014/05/02 10:10:56.257 devMotorAsyn::send_msg: SMTR1608-9-B20-05:brag command=5, pact=1, value=1000.000000
> devAsynMotor::build_trans, calling queueRequest, pmsg=0x597bd4, command=6, interface=1, dvalue=1000.000001
> 2014/05/02 10:10:56.260 XPS1 addr 0 queueRequest priority 0 not lockHolder
> 2014/05/02 10:10:56.262 devMotorAsyn::send_msg: SMTR1608-9-B20-05:brag command=6, pact=1, value=10000.000000
> devAsynMotor::build_trans, calling queueRequest, pmsg=0x60b224, command=5, interface=1, dvalue=10000.000012
> 2014/05/02 10:10:56.266 XPS1 addr 0 queueRequest priority 0 not lockHolder
> 2014/05/02 10:10:56.267 XPS1 addr 0 queueRequest priority 0 not lockHolder
> 2014/05/02 10:10:56.268 devMotorAsyn::send_msg: SMTR1608-9-B20-05:brag command=0, pact=1, value=246415.275059
> 2014/05/02 10:10:56.268 devMotorAsyn::send_msg: SMTR1608-9-B20-05:brag command=8, pact=1, value=0.000000
> devAsynMotor::build_trans, calling queueRequest, pmsg=0x60b574, command=0, interface=1, dvalue=0.000000
> 2014/05/02 10:10:56.269 XPS1 addr 0 queueRequest priority 0 not lockHolder
> 2014/05/02 10:10:56.272 asynManager::portThread port=XPS1 callback
> devAsynMotor::asynCallback, entry, pmsg=0x597bd4, command=6, interface=1, dvalue=0.000000
> 2014/05/02 10:10:56.273 devMotorAsyn::asynCallback: SMTR1608-9-B20-05:brag command=6, ivalue=0, dvalue=0.000000, pasynUser->reason=6
> 2014/05/02 10:10:56.274 asynMotorController:writeFloat64:: axis=0, function=6, value=0.000000
> 2014/05/02 10:10:56.274 asynManager::portThread port=XPS1 callback
> devAsynMotor::asynCallback, entry, pmsg=0x60b224, command=5, interface=1, dvalue=0.000000
> 2014/05/02 10:10:56.285 devMotorAsyn::asynCallback: SMTR1608-9-B20-05:brag command=5, ivalue=0, dvalue=0.000000, pasynUser->reason=5
> 2014/05/02 10:10:56.291 asynMotorController:writeFloat64:: axis=0, function=5, value=0.000000
> 2014/05/02 10:10:56.299 SMTR1608-9-B20-05:brag devMotorAsyn::update_values, needUpdate=0
> 2014/05/02 10:10:56.303 asynManager::portThread port=XPS1 callback
> 2014/05/02 10:10:56.311 asynManager::portThread port=XPS1 callback
> devAsynMotor::asynCallback, entry, pmsg=0x60b574, command=0, interface=1, dvalue=0.000000
> 2014/05/02 10:10:56.314 devMotorAsyn::asynCallback: SMTR1608-9-B20-05:brag command=0, ivalue=0, dvalue=0.000000, pasynUser->reason=1
> 2014/05/02 10:10:56.316 XPSAxis:move: Set XPS XPS1, axis 0 move to 0.000000, min vel=0.000000, max_vel=0.000000, accel=0.000000, minJerk=0.005000, maxJerk=0.050000
> 2014/05/02 10:10:56.325 SendAndReceive unexpected response =-17,GroupMoveAbsolute (S.Pos,5.66625162537e-311),EndOfAPI
> 2014/05/02 10:10:56.329 XPSAxis:move: Error performing GroupMoveAbsolute[XPS1,0] -17
> 2014/05/02 10:10:56.330 SMTR1608-9-B20-05:brag devMotorAsyn::statusCallback new value=[p:60000.000000,e:60007.000000,s:4980] P
> 2014/05/02 10:10:56.332 asynMotorController:writeFloat64: Set driver XPS1, axis 0 move absolute to 0.000000, base velocity=0.000000, velocity=0.000000, acceleration=0.000000
> 2014/05/02 10:10:56.334 asynMotorController:writeFloat64 error, status=3 axis=0, function=1, value=0.000000
> 2014/05/02 10:10:56.336 devMotorAsyn::asynCallback: SMTR1608-9-B20-05:brag pasyn{Float64,Int32}->write returned
> 2014/05/02 10:10:56.337 SMTR1608-9-B20-05:brag devMotorAsyn::update_values, needUpdate=1
> 2014/05/02 10:10:56.344 XPSAxis:poll: [XPS1,0]: S.Pos axisStatus=11
> 2014/05/02 10:10:56.353 SMTR1608-9-B20-05:brag devMotorAsyn::statusCallback new value=[p:60000.000000,e:60007.000000,s:4982]
> 2014/05/02 10:10:56.354 SMTR1608-9-B20-05:brag devMotorAsyn::update_values, needUpdate=1
> epics> dbpr SMTR1608-9-B20-05:brag 10
> ACCL: 0.2 ACKS: NO_ALARM ACKT: YES ADEL: 0
> ALST: 0 ASG: ASP: (nil) ATHM: 0
> BACC: 0.2 BDST: 0 BKPT: 00 BVEL: 1
> CARD: 0 CBAK: 0x597710 CDIR: 1 CNEN: Disable
> DCOF: 0 DESC: Mono Brag DHLM: 59
> DIFF: 18.6415275058764 DINP:CONSTANT DIR: Pos
> DISA: 0 DISP: 0 DISS: NO_ALARM DISV: 1
> DLLM: 1 DLY: 0 DMOV: 1 DOL:CONSTANT
> DPVT: 0x597728 DRBV: 6 DSET: 0x47f3d0 DTYP: asynMotor
> DVAL: 24.6415275058764 EGU: degrees ERES: 1.0e-04
> EVNT: 0 FLNK:CONSTANT 0 FOF: 0 FOFF: Variable
> FRAC: 1 HHSV: NO_ALARM HIGH: 0 HIHI: 0
> HLM: 59 HLS: 0 HLSV: NO_ALARM HOMF: 0
> HOMR: 0 HOPR: 0 HSV: NO_ALARM HVEL: 0.1
> ICOF: 0 INIT: JAR: 5 JOGF: 0
> JOGR: 0 JVEL: 1 LCNT: 0
> LDVL: 24.6415275058764 LLM: 1 LLS: 0
> LLSV: NO_ALARM LOCK: NO LOLO: 0 LOPR: 0
> LOW: 0 LRLV: 0 LRVL: 246415 LSET: 0x597ff0
> LSPG: Go LSV: NO_ALARM LVAL: 24.6415275058764
> LVIO: 0 MDEL: 0 MIP: 0 MISS: 0
> MLIS: 00 5c ee 80 00 5f b9 40 00 00 00 46 MLOK: 00 59 50 c8
> MLST: 0 MMAP: 0 MOVN: 0 MRES: 1.0e-04
> MSTA: 18818 NAME: SMTR1608-9-B20-05:brag NMAP: 0
> NSEV: NO_ALARM NSTA: NO_ALARM NTM: YES NTMF: 2
> OFF: 0 OMSL: supervisory OUT:INST_IO @asyn(XPS1,0)
> PACT: 0 PCOF: 0 PHAS: 0 PINI: NO
> POST: PP: 0 PPN: (nil) PPNR: (nil)
> PREC: 5 PREM: PRIO: LOW PROC: 0
> PUTF: 0 RBV: 6 RCNT: 0 RDBD: 1.0e-04
> RDBL:CONSTANT RDES: 0x548f38 RDIF: 186415 REP: 60007
> RHLS: 0 RINP:CONSTANT RLLS: 0 RLNK:CONSTANT
> RLV: 0 RMOD: Default RMP: 60000 RPRO: 0
> RRBV: 60000 RRES: 0 RSET: 0x47f1d0 RTRY: 0
> RVAL: 246415 RVEL: 0 S: 50 SBAK: 50
> SBAS: 5 SCAN: Passive SDIS:CONSTANT SET: Use
> SEVR: NO_ALARM SMAX: 0 SPMG: Go SPVT: (nil)
> SREV: 200 SSET: 0 STAT: NO_ALARM STOO:CONSTANT
> STOP: 0 STUP: OFF SUSE: 0 SYNC: 0
> TDIR: 0 TIME: 2014-05-02 10:12:37.121731000 TPRO: 0
> TSE: 0 TSEL:CONSTANT TWF: 0 TWR: 0
> TWV: 1 UDF: 0 UEIP: No UREV: 0.02
> URIP: No VAL: 24.6415275058764 VBAS: 0.1
> VELO: 1 VERS: 6.8 VMAX: 0 VOF: 0
> epics> asynReport 10 XPS1
> XPS1 multiDevice:Yes canBlock:Yes autoConnect:Yes
> enabled:Yes connected:Yes numberConnects 1
> nDevices 1 nQueued 0 blocked:No
> asynManagerLock:No synchronousLock:No
> exceptionActive:No exceptionUsers 0 exceptionNotifys 0
> traceMask:0x1 traceIOMask:0x0 traceInfoMask:0x1
> interposeInterfaceList
> asynOctet pinterface 0x47f984 drvPvt 0x574470
> interfaceList
> asynCommon pinterface 0x47fb40 drvPvt 0x572760
> asynDrvUser pinterface 0x47fc28 drvPvt 0x572760
> asynOctet pinterface 0x47fb8c drvPvt 0x572760
> asynInt32 pinterface 0x47fb4c drvPvt 0x572760
> asynFloat64 pinterface 0x47fb7c drvPvt 0x572760
> asynFloat64Array pinterface 0x47fbf0 drvPvt 0x572760
> asynGenericPointer pinterface 0x47fc00 drvPvt 0x572760
> addr 0 autoConnect Yes enabled Yes connected Yes exceptionActive No
> exceptionActive No exceptionUsers 0 exceptionNotifys 0
> blocked No
> traceMask:0xff traceIOMask:0x2 traceInfoMask:0x1
> XPS motor driver: XPS1
> numAxes: 1
> firmware version: XPS-Q8 Firmware Standard V1.2.1
> moving poll period: 0.010000
> idle poll period: 5.000000
> enableSetPosition: 0
> setPositionSettlingTime: 5.000000
> IPAddress: 192.168.0.254
> IPPort: 5001
> ftpUserName: Administrator
> ftpUserPassword: Administrator
> movesDeferred: 0
> autoEnable: 1
> noDisableError: 0
> axis 0
> name = S.Pos
> step size = 0.0001
> poll socket = 0, moveSocket = 3
> status = 11
> Port: XPS1
> Timestamp: <undefined>
> Input EOS[0]:
> Output EOS[0]:
> Parameter list 0
> Number of parameters is: 78
> Parameter 0 type=asynFloat64, name=MOTOR_MOVE_REL, value is undefined
> Parameter 1 type=asynFloat64, name=MOTOR_MOVE_ABS, value=0.000000, status=0
> Parameter 2 type=asynFloat64, name=MOTOR_MOVE_VEL, value is undefined
> Parameter 3 type=asynFloat64, name=MOTOR_HOME, value is undefined
> Parameter 4 type=asynInt32, name=MOTOR_STOP_AXIS, value is undefined
> Parameter 5 type=asynFloat64, name=MOTOR_VELOCITY, value=0.000000, status=0
> Parameter 6 type=asynFloat64, name=MOTOR_VEL_BASE, value=0.000000, status=0
> Parameter 7 type=asynFloat64, name=MOTOR_ACCEL, value=0.000000, status=0
> Parameter 8 type=asynFloat64, name=MOTOR_POSITION, value=60000.000000, status=0
> Parameter 9 type=asynFloat64, name=MOTOR_ENCODER_POSITION, value=60006.000000, status=0
> Parameter 10 type=asynInt32, name=MOTOR_DEFER_MOVES, value is undefined
> Parameter 11 type=asynInt32, name=MOTOR_MOVE_HOME, value is undefined
> Parameter 12 type=asynFloat64, name=MOTOR_RESOLUTION, value is undefined
> Parameter 13 type=asynFloat64, name=MOTOR_ENCODER_RATIO, value is undefined
> Parameter 14 type=asynFloat64, name=MOTOR_PGAIN, value=0.000000, status=0
> Parameter 15 type=asynFloat64, name=MOTOR_IGAIN, value=0.000000, status=0
> Parameter 16 type=asynFloat64, name=MOTOR_DGAIN, value=0.000000, status=0
> Parameter 17 type=asynFloat64, name=MOTOR_HIGH_LIMIT, value=590000.000000, status=0
> Parameter 18 type=asynFloat64, name=MOTOR_LOW_LIMIT, value=10000.000000, status=0
> Parameter 19 type=asynInt32, name=MOTOR_CLOSED_LOOP, value is undefined
> Parameter 20 type=asynInt32, name=MOTOR_STATUS, value=18818, status=0
> Parameter 21 type=asynInt32, name=MOTOR_UPDATE_STATUS, value is undefined
> Parameter 22 type=asynInt32, name=MOTOR_STATUS_DIRECTION, value=0, status=0
> Parameter 23 type=asynInt32, name=MOTOR_STATUS_DONE, value=1, status=0
> Parameter 24 type=asynInt32, name=MOTOR_STATUS_HIGH_LIMIT, value=0, status=0
> Parameter 25 type=asynInt32, name=MOTOR_STATUS_AT_HOME, value is undefined
> Parameter 26 type=asynInt32, name=MOTOR_STATUS_SLIP, value is undefined
> Parameter 27 type=asynInt32, name=MOTOR_STATUS_POWERED, value is undefined
> Parameter 28 type=asynInt32, name=MOTOR_STATUS_FOLLOWING_ERROR, value=0, status=0
> Parameter 29 type=asynInt32, name=MOTOR_STATUS_HOME, value=1, status=0
> Parameter 30 type=asynInt32, name=MOTOR_STATUS_HAS_ENCODER, value=1, status=0
> Parameter 31 type=asynInt32, name=MOTOR_STATUS_PROBLEM, value=0, status=0
> Parameter 32 type=asynInt32, name=MOTOR_STATUS_MOVING, value=0, status=0
> Parameter 33 type=asynInt32, name=MOTOR_STATUS_GAIN_SUPPORT, value=1, status=0
> Parameter 34 type=asynInt32, name=MOTOR_STATUS_COMMS_ERROR, value=0, status=0
> Parameter 35 type=asynInt32, name=MOTOR_STATUS_LOW_LIMIT, value=0, status=0
> Parameter 36 type=asynInt32, name=MOTOR_STATUS_HOMED, value=1, status=0
> Parameter 37 type=asynInt32, name=PROFILE_NUM_AXES, value is undefined
> Parameter 38 type=asynInt32, name=PROFILE_NUM_POINTS, value is undefined
> Parameter 39 type=asynInt32, name=PROFILE_CURRENT_POINT, value is undefined
> Parameter 40 type=asynInt32, name=PROFILE_NUM_PULSES, value is undefined
> Parameter 41 type=asynInt32, name=PROFILE_START_PULSES, value is undefined
> Parameter 42 type=asynInt32, name=PROFILE_END_PULSES, value is undefined
> Parameter 43 type=asynInt32, name=PROFILE_ACTUAL_PULSES, value is undefined
> Parameter 44 type=asynInt32, name=PROFILE_NUM_READBACKS, value is undefined
> Parameter 45 type=asynInt32, name=PROFILE_TIME_MODE, value is undefined
> Parameter 46 type=asynFloat64, name=PROFILE_FIXED_TIME, value is undefined
> Parameter 47 type=asynFloat64Array, name=PROFILE_TIME_ARRAY, value is undefined
> Parameter 48 type=asynFloat64, name=PROFILE_ACCELERATION, value is undefined
> Parameter 49 type=asynInt32, name=PROFILE_BUILD, value is undefined
> Parameter 50 type=asynInt32, name=PROFILE_BUILD_STATE, value is undefined
> Parameter 51 type=asynInt32, name=PROFILE_BUILD_STATUS, value is undefined
> Parameter 52 type=string, name=PROFILE_BUILD_MESSAGE, value is undefined
> Parameter 53 type=asynInt32, name=PROFILE_EXECUTE, value is undefined
> Parameter 54 type=asynInt32, name=PROFILE_EXECUTE_STATE, value=0, status=0
> Parameter 55 type=asynInt32, name=PROFILE_EXECUTE_STATUS, value is undefined
> Parameter 56 type=string, name=PROFILE_EXECUTE_MESSAGE, value is undefined
> Parameter 57 type=asynInt32, name=PROFILE_ABORT, value is undefined
> Parameter 58 type=asynInt32, name=PROFILE_READBACK, value is undefined
> Parameter 59 type=asynInt32, name=PROFILE_READBACK_STATE, value is undefined
> Parameter 60 type=asynInt32, name=PROFILE_READBACK_STATUS, value is undefined
> Parameter 61 type=string, name=PROFILE_READBACK_MESSAGE, value is undefined
> Parameter 62 type=asynInt32, name=PROFILE_USE_AXIS, value is undefined
> Parameter 63 type=asynFloat64Array, name=PROFILE_POSITIONS, value is undefined
> Parameter 64 type=asynFloat64Array, name=PROFILE_READBACKS, value is undefined
> Parameter 65 type=asynFloat64Array, name=PROFILE_FOLLOWING_ERRORS, value is undefined
> Parameter 66 type=asynFloat64, name=PROFILE_MOTOR_RESOLUTION, value is undefined
> Parameter 67 type=asynInt32, name=PROFILE_MOTOR_DIRECTION, value is undefined
> Parameter 68 type=asynFloat64, name=PROFILE_MOTOR_OFFSET, value is undefined
> Parameter 69 type=asynFloat64, name=XPS_MIN_JERK, value=0.005000, status=0
> Parameter 70 type=asynFloat64, name=XPS_MAX_JERK, value=0.050000, status=0
> Parameter 71 type=asynFloat64, name=XPS_PROFILE_MAX_VELOCITY, value is undefined
> Parameter 72 type=asynFloat64, name=XPS_PROFILE_MAX_ACCELERATION, value is undefined
> Parameter 73 type=asynFloat64, name=XPS_PROFILE_MIN_POSITION, value is undefined
> Parameter 74 type=asynFloat64, name=XPS_PROFILE_MAX_POSITION, value is undefined
> Parameter 75 type=string, name=XPS_PROFILE_GROUP_NAME, value is undefined
> Parameter 76 type=string, name=XPS_TRAJECTORY_FILE, value is undefined
> Parameter 77 type=asynInt32, name=XPS_STATUS, value=11, status=0
> int32 callback client address=0xd42c8, addr=0, reason=77, userPvt=0x5935c8
> float64 callback client address=0xdf1cc, addr=0, reason=8, userPvt=0x596aa0
> genericPointer callback client address=0x927a8, addr=0, reason=20, userPvt=0x597728