On Thu, 3 Dec 2015, Mark Rivers wrote:
Hi Jon,
http://cars9.uchicago.edu/software/epics/modbusDoc.html
Supported Modbus data types
modbusDataType value drvUser field Description
0 UINT16 Unsigned 16-bit binary integers
4 INT16 16-bit signed (2's complement) integers. This data type extends the sign bit when converting to epicsInt32.
So modbusDataType=0 is UINT16, unsigned 16-bit integer. That explains your problem, you should be using modbusDataType=4 (INT16) and your command line should be:
drvModbusAsynConfigure("CollimCouch", "AcromagCollimCouch",0,4,0,9,4,100,"AcromagXT1221")
That must be it. The referenced documentation is for Modbus release 2-7 and
we are still running 2-2, which only supports data type codes 0 - 3. When we try
code 4 in 2-2, RVAL is always 0. The 2-2 doc says:
Type 0 is used for binary numbers in twos-complement format. The data can either be signed or unsigned.
But, as we found, it isn't very helpful for signed integers.
Thanks for clearing this up.
Jon Jacky