1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  <2015>  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  <2015>  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Subject: RE: ai RVAL via asyn + modbus: getting unsigned integer
Date: Mon, 14 Dec 2015 19:56:33 +0000
Hi Jon,
I believe I may have found your problem.  This is from your original post:
record(ai, "$(ROOM="Iso"):$(SUBSYSTEM):$(SETTING):Actual") {
  field(DESC, "$(DESC)")
  field(SCAN, "I/O Intr")
  field(DTYP, "asynInt32")
  field(INP, "@asynMask(CollimCouch, $(OFFSET), 16, 1000)MODBUS_DATA")
  field(LINR, "SLOPE")
  field(ESLO, "$(ESLO=1.0)")
  field(EOFF, "$(EOFF=0.0)")
In particular:
So you are using asynInt32 device support with the asynMask link syntax.
This is the documentation from for asynInt32 and asynMask from  http://cars9.uchicago.edu/software/epics/modbusDoc.html
field(INP,"@asynMask(portName,offset,nbits,timeout)drvUser")
The asynMask syntax is used for analog I/O devices, in order to specify the number of bits in the device. This is required for Modbus because the driver only knows that it is returning a 16-bit register, but not the actual number of bits in the device, and hence cannot return meaningful data with asynInt32->getBounds().
nbits>0 for a unipolar device. For example, nbits=12 means unipolar 12-bit device, with a range of 0 to 4095. nbits<0 for a bipolar device. For example, nbits=-12 means bipolar 12-bit device, with a range of -2048 to 2047)
So you have set nbits=16.  But the documentation explains the nbits>0 is for unipolar devices.  Yours is not a unipolar device, it is a bipolar device, so you should be setting nbits=-16.
I believe that will fix your problem.
Sent: Monday, December 14, 2015 1:22 PM
To: Mark Rivers
Cc: [email protected]
I did the experiment Mark suggested and found that drvModbusAsyn.c is working as
expected - it returns small negative integers when small negative voltages are applied to the converter.  BUT in those cases RVAL is still reported as a large positive integer.  Details follow:
On Sat, 12 Dec 2015, Mark Rivers wrote:
> You could add the following printf statement to drvModbusAsyn.c::readPlcInt and see what the output is for that value.
>        case dataTypeInt16:
>        result = (epicsInt16)value;
> printf("readPlcInt, offset=%d, value=0x%x, result=%d (0x%x)\n", offset, value, result, result);
>        break;
I did that and got these results.  When Vin is a small positive value +0.002 V,
value is a small positive integer and RVAL is a small positive integer:
readPlcInt, offset=0, value=0x1, result=1 (0x1)
dbgf Iso:GantryCouch:Collimator:Actual.RVAL
DBR_LONG:           6         0x6
(the voltage varies slightly between the printf and dbgf outputs)
But when Vin is -0.008 V, value is a small negative integer BUT RVAL is
a large positive integer:
  readPlcInt, offset=0, value=0xfff4, result=-12 (0xfffffff4)
DBR_LONG:           65524     0xfff4
So it seems RVAL is handled differently than value.  Is there some way to make
RVAL behave like value?
Jon Jacky
PS - here are answers to Mark's other questions about MODBUS_DATA and asynReport
> In your database for the ai record what is the drvInfo field in the INP link? Is it still MODBUS_DATA? If so, that should be fine.
Yes, dbpr reports the INP field is INP:INST_IO @asynMask(CollimCouch, 0, 16, 1000)MODBUS_DATA
> Please send the output of the following command:
> asynReport(1, "CollimCouch")
I believe addr 0 is connected to Vin in the output shown above.
epics> asynReport(1, "CollimCouch")
CollimCouch multiDevice:Yes canBlock:Yes autoConnect:Yes
     enabled:Yes connected:Yes numberConnects 1
     nDevices 6 nQueued 0 blocked:No
     asynManagerLock:No synchronousLock:No
     exceptionActive:No exceptionUsers 0 exceptionNotifys 0
     traceMask:0x1 traceIOMask:0x0 traceInfoMask:0x1
     addr 0 autoConnect Yes enabled Yes connected No exceptionActive No
         exceptionActive No exceptionUsers 0 exceptionNotifys 0
         blocked No
     addr 5 autoConnect Yes enabled Yes connected No exceptionActive No
         blocked No
     addr 3 autoConnect Yes enabled Yes connected No exceptionActive No
         blocked No
     addr 4 autoConnect Yes enabled Yes connected No exceptionActive No
         blocked No
     addr 2 autoConnect Yes enabled Yes connected No exceptionActive No
         blocked No
     addr 1 autoConnect Yes enabled Yes connected No exceptionActive No
         blocked No
modbus port: CollimCouch
     asynOctet server:   AcromagCollimCouch
     modbusSlave:        0
     modbusFunction:     4
     modbusStartAddress: 00
     modbusLength:       011
     plcType:            AcromagXT1221
     I/O errors:         0
     Read OK:            2207
     Write OK:           0
     pollDelay:          0.100000
     Time for last I/O   1 msec
     Max. I/O time:      7 msec
     Time per hist. bin: 1 msec
RE: ai RVAL via asyn + modbus: getting unsigned integer jon
RE: ai RVAL via asyn + modbus: getting unsigned integer Mark Rivers
Prev: Re: ai RVAL via asyn + modbus: getting unsigned integer Mark Rivers
Next: Re: MEDM Extension Make Failed on Ubuntu 15.10 Jeong Han Lee
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  <2015>  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Next: RE: ai RVAL via asyn + modbus: getting unsigned integer jon