1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  <20182019  2020  2021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  <20182019  2020  2021  2022  2023  2024  2025  2026
Subject: RE: Modbus Polling disable/enable
To: "'[email protected]'" <[email protected]>, "[email protected]" <[email protected]>
Date: Thu, 6 Sep 2018 13:42:53 +0000
Hi Emilio,
> I found two ways of achieving the goal:
>    1. Set pollMsec  to a value less or equal to 0 and add an extra record for each register that has periodic scan and writes to MODBUS_READ (disable button would disable this record)
>    2. Use absolute addressing (modbusStartAddress=-1) and change all the records to be periodic scanned
> The downside of the first solution is that I need to have double records for each modbus register.
That is not quite true.  You need an additional record for each contiguous block of registers that are read by a single Modbus asyn driver, not one record for each register.  In many cases there are just a few such blocks of registers that need to be read, so there are only a few new records required.
> The downside of the second solution is that this might be a feature of absolute addressing that might change, as documentation
> is not explicit on the point that absolute addressing mode disables the readPoller thread and calls doModbusIO on record's demand.
I think you can be certain that drivers using absolute addressing will never poll.  If they did poll they would need to poll the entire 64KB modus address space, which would require multiple read operations and be very slow.  This is because the driver cannot know what Modbus addresses will actually be read when a record processes.  Furthermore it would almost always result in Modbus errors because it would attempt to read Modbus addresses that are invalid for a particular piece of hardware.
So I think either method will work.  Method 1) may require fewer periodically scanned records to change their SCAN rates when you want to do a read.
-----Original Message-----
From: [email protected] <[email protected]> On Behalf Of [email protected]
Sent: Thursday, September 6, 2018 4:16 AM
To: [email protected]
Subject: Modbus Polling disable/enable
Hello Tech-talk
I'm currently working in a module which relies on the modbus module and I need to create a button in the user
interface that allows to disable the read polling.
As it is working now, readPoller still reads the values even if the associated record is disabled.
My question is:  what is the recommended way?
Best regards and thank you,
Emilio
Modbus Polling disable/enable [email protected]
Prev: Re: asking for help on s7nodave Mark Rivers
Next: asking for help on s7nodave =?gb18030?b?s8nN/rvG5a0=?=
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  <20182019  2020  2021  2022  2023  2024  2025  2026
Prev: Modbus Polling disable/enable [email protected]
Next: Problems with soft motors Mark Rivers
ANJ, 06 Sep 2018 · Home · News · About · Talk · Base · Modules · Extensions ·
