1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  <20192020  2021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  <20192020  2021  2022  2023  2024  2025  2026
Subject: Re: Record for a running sum
To: Donny Domagoj Cosic <[email protected]>, "[email protected]" <[email protected]>
Date: Thu, 5 Dec 2019 21:14:26 +0000
Hi Donny,
I did similar applications at NSLS-II: calculate hourly, daily, monthly, yearly cumulative beam current in the Storage Ring.
Here is one example to test the cumulative dosage in one minute: "DosagePV" is a simulated PV;  "Dosage:1h" is the cumulative dosage; Whenever one minute passes, the value of “TimeStamp” (@%M) will change and "Dosage:1h-Reset_" will set "Dosage:1h" to 0.
To calculate hourly, daily, monthly, yearly dosage, simply change %M in field(INP, "@%M") to %H, %d, %b, %Y.
To preserve the cumulative dosage, you should use EPICS AutoSave (info(autosaveFields_pass0, "VAL")). Otherwise, the value will be 0 after your IOC is rebooted.
record(calc, "DosagePV") {
    field(INPA, "DosagePV")
    field(SCAN, "1 second")
    field(CALC, "A+1")
    field(FLNK, "TimeStamp")
record(stringin, "TimeStamp")
    field(DTYP, "Soft Timestamp")
    field(PINI,"YES")
    #field(INP, "@%b %d, %Y %H:%M:%S.%03f")
    field(INP, "@%M")
record(calcout, "Dosage:1h-Reset_")
    field(INPA, "TimeStamp CP")
    field(CALC, "0")
    field(OUT,  "Dosage:1h PP")
record(calcout, "Dosage:1h-Calc_")
    field(INPA, "Dosage:1h")
    field(INPB, "DosagePV CP")
    field(CALC, "A+B")
record(ai, "Dosage:1h")
    field(PREC, "3")
    field(EGU,  "blabla")
    field(PINI,"YES")
There are other ways to calculate the cumulative dosage: use compress record.
I prefer the first approach above. The approach below works only if “DosagePV” updates at a regular rate (i.e. 1Hz).
record(compress,"Dosage:1h-Com_")
        field(INP,"DosagePV CP")
        field(ALG,"N to 1 Average")
        field(NSAM,"1")
        field(N,"3600")
        field(PREC,"3")
        field(FLNK,"Dosage:1h_")
record(calc, "Dosage:1h_")
        field(INPA,  "Dosage:1h-Com_")
        field(CALC, "3600*A")
        field(PREC, "3")
HTH,
Yong Hu
NSLS-II Controls Group
From: Tech-talk <[email protected]> on behalf of "[email protected]" <[email protected]>
Organization: Institut Ruđer Bošković
Reply-To: Donny Domagoj Cosic <[email protected]>
Date: Thursday, December 5, 2019 at 9:20 AM
Subject: Record for a running sum
Hello,
I developed an IOC for the radiation monitors found throughout our
laboratory. Through this IOC I am able to read in the values of each
probe and display them nicely using CS-Studio. However I would like to
add the ability to the IOC to keep a running sum so I can calculate the
cumulative monthly and yearly doses throughout the laboratory but I am
not sure how to implement this. I tried searching for similar projects
of examples, but without any luck. Would you be able to provide me with
some pointers onto how to implement such a feature?
Donny
Donny Domagoj Cosic
  Institut Ruđer Bošković, Bijenička cesta 54, 10000 Zagreb, Croatia
Re: Record for a running sum Donny Domagoj Cosic via Tech-talk
Prev: Re: Record for a running sum William Layne via Tech-talk
Next: Linker error with vendor library Mark Rivers via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  <20192020  2021  2022  2023  2024  2025  2026
Next: Re: Record for a running sum Donny Domagoj Cosic via Tech-talk
ANJ, 11 Dec 2019 · Home · News · About · Talk · Base · Modules · Extensions ·
