Hi Ji Li,
OK that makes sense. The feedback is Off by default in the database, since it can be very dangerous to start running it when the IOC boots. The user must explicitly turn the feedback on.
[email protected]>
Sent: Thursday, August 5, 2021 11:24 AM
To: Mark Rivers
Cc:
[email protected]
Subject: Re: How to find out PVs preventing SSCAN from running?
Hi Mark,
I think it is working. I didn't see the readback change during the test, but Matt said he saw the load going up towards the final load, so I assume the PID is good. What I did was turning on the feedback. The PID record was set to scan at 1 second in the database.
Best,
Ji Li
[email protected]>
Sent: Thursday, August 5, 2021 12:03
To: Li, Ji <
[email protected]>
Cc:
[email protected] <
[email protected]>
Hi Ji Li,
I am not quite sure what you are saying. Is it working correctly now? If so, what did you change so that OUT is now updating? Was it turning feedback On, changing the SCAN rate of the epid record from Passive to 1 second, or something else?
[email protected]>
Sent: Thursday, August 5, 2021 10:49 AM
To: Mark Rivers
Cc:
[email protected]
Hi Mark,
Here's the screen of the pressure control and PID.
[cid:48aa5b9d-783a-4ae2-8402-c5f6b55d7de8]
Now I see the output changing (1.401 below the Stop motor button in the screenshot).
After setting XF:28IDD-CTPress_PID.TPRO to 1, the IOC shell started to print trace information as XF:28IDD-CTPress_PID.SCAN was set to "1 second".
scan-1: dbProcess of 'XF:28IDD-CTPress_PID'
And
epics> dbpr XF:28IDD-CTPress_PID 2
ACKS: INVALID ACKT: YES ADEL: 0 ASG :
BKPT: 00 CVAL: 0 CVLP: 0 D : 0
DESC: DISA: 0 DISP: 0 DISS: NO_ALARM
DISV: 1 DP : 0 DRVH: 5 DRVL: -2
DT : 1.000027299 DTP : 1.000027299 DTYP: Soft Channel EGU :
ERR : 0.21021021021021 ERRP: 0.21021021021021
EVNT: FBON: On FBOP: On FLNK: CONSTANT
FMOD: PID HHSV: NO_ALARM HIGH: 0 HIHI: 0
HOPR: 501 HSV : NO_ALARM HYST: 0 I : 0
INP : DB_LINK XF:28IDD-CTPress_Value NPP NMS IP : 0
KD : 0 KI : 0 KP : 20 LCNT: 0
LLSV: NO_ALARM LOLO: 0 LOPR: 0 LOW : 0
LSV : NO_ALARM MDEL: 0 MDT : 0
NAME: XF:28IDD-CTPress_PID NSEV: NO_ALARM NSTA: NO_ALARM
ODEL: 0 OUTL: CA_LINK XF:28IDD-CT{ES-AO}1_11_0 PP NMS
OVAL: 4.2042042042042 P : 4.2042042042042
PACT: 0 PHAS: 0 PINI: NO
PP : 4.2042042042042 PREC: 3 PRIO: LOW
PUTF: 0 RPRO: 0 SCAN: 1 second SDIS: CONSTANT
SEVR: NO_ALARM SMSL: supervisory STAT: NO_ALARM STPL: CONSTANT
TIME: 2021-08-05 11:21:46.531743868 TPRO: 1 TRIG: CONSTANT
TSE : 0 TSEL: CONSTANT TVAL: 0 UDF : 0
UDFS: INVALID VAL : 0.21521521521522
Best,
Ji Li
[email protected]>
Sent: Wednesday, August 4, 2021 23:51
To: Li, Ji <
[email protected]>
Cc:
[email protected] <
[email protected]>
the scan ran, $(P)$(R)PID value increased, but $(P)$(OUT) wasn't changed. Seems $(P)$(R)PID was not processed.
The fact that OUT did not change does not necessarily mean that the record did not process. Other possibilities include:
- Feedback is turned off
- The PID coefficients are such that OUT does not change
- The OUT field is being limited by DRVL or DRVH
You can set the TPRO field in the epid record to see if it is processing.
Sent from my iPhone
On Aug 4, 2021, at 10:17 PM, Li, Ji <
[email protected]> wrote:
Hi Mark, Michael,
The test scan with the following definition of related records turned out that, the scan ran, $(P)$(R)PID value increased, but $(P)$(OUT) wasn't changed. Seems $(P)$(R)PID was not processed.
grecord(sscan,"$(P)$(R)RampScan") {
field(DESC,"Load ramp")
field(PINI,"YES")
field(PRIO,"HIGH")
field(MPTS,"1000")
field(NPTS,"1000")
field(FPTS,"FREEZE")
field(D01PV,"$(P)$(R)Value")
field(P1PV,"$(P)$(R)PID.VAL")
grecord(epid,"$(P)$(R)PID") {
field(INP,"$(P)$(R)Value")
field(OUTL,"$(P)$(OUT) PP NMS")
field(KP,"$(KP)")
field(KI,"$(KI)")
field(KD,"$(KD)")
field(LOPR,"0")
field(HOPR,"501")
field(DRVL,"-100")
field(DRVH,"100")
field(PREC,"3")
Best,
Ji Li
[email protected]> on behalf of Li, Ji via Tech-talk <
[email protected]>
Sent: Wednesday, August 4, 2021 20:55
To: Mark Rivers <
[email protected]>
Cc:
[email protected] <
[email protected]>
Hi Mark,
This is a legacy IOC inherited from X17B beamline at NSLS. I don't know much about the details yet, but from reading the database, XF:28IDD-CTPress_PID is a epid record that writes to a DAC to controls the pressure on the MAXPD endstation at 28ID. I will ask
the beamline scientist to run a test with the current configuration. Thank you.
Best,
Ji Li
[email protected]>
Sent: Wednesday, August 4, 2021 20:25
To: Li, Ji <
[email protected]>
Cc:
[email protected] <
[email protected]>
Hi Ji Li,
I have used the scan record a lot, and I have never put "PP MS" after a PV name, and it always has processed the record with no problem. For example if the positioner is a D/A converter it writes to the device, if it is a motor .VAL field it moves the motor,
etc. without specifying "PP MS".
What type of record is XF:28IDD-CTPress_PID? Is it an epid record (which the name suggests), or some other type of record? What does that record do when you write to its VAL field?
[email protected]>
Sent: Wednesday, August 4, 2021 6:42 PM
To: Mark Rivers
Cc:
[email protected]
I see. The original definition of P1PV was
field(P1PV,"$(P)$(R)PID.VAL PP MS")
and it worked in base 3.14.
Now we are running base 7.0.5, and changing P1PV to
brought P1NV to PV OK and enabled the scan. But $(P)$(R)PID doesn't get processed when written. How to define the PV as PP in such fields in base 7.0.5?
Best,
Ji Li
[email protected]>
Sent: Wednesday, August 4, 2021 18:59
To: Li, Ji <
[email protected]>
Cc:
[email protected] <
[email protected]>
P1NV is “PV BAD”. Something looks wrong.
Sent from my iPhone
On Aug 4, 2021, at 5:50 PM, Li, Ji <
Hi Mark,
How do I access these screens? I did check the level 2 output of dbpr:
epics> dbpr XF:28IDD-CTPress_RampScan 2
A1CD: 1 A1NV: No PV A1PV: AAWAIT: NO
ACKS: NO_ALARM ACKT: YES ACQM: NORMAL ACQT: SCALAR
ALRT: 0 ASCD: 1 ASG : ASNV: No PV
ASPV: ASWAIT: Wait ATIME: 0 AWAIT: 0
AWCT: 0 BCPT: 0 BKPT: 00 BSCD: 1
BSNV: No PV BSPV: BSWAIT: Wait BUSY: 0
CMND: Clear msg COPYTO: 0 CPT : 0 D01CA: PTR (nil)
D01CV: 0 D01DA: PTR 0x147ed20 D01EU:
D01HR: 0 D01LR: 0 D01LV: 0 D01NE: 0
D01NV: PV OK D01PR: 1 D01PV: XF:28IDD-CTPress_Value
D02CA: PTR (nil) D02CV: 0 D02DA: PTR 0x1480c80
D02EU: D02HR: 0 D02LR: 0 D02LV: 0
D02NE: 0 D02NV: No PV D02PR: 0 D02PV:
D03CA: PTR (nil) D03CV: 0 D03DA: PTR 0x1482be0
D03EU: D03HR: 0 D03LR: 0 D03LV: 0
D03NE: 0 D03NV: No PV D03PR: 0 D03PV:
D04CA: PTR (nil) D04CV: 0 D04DA: PTR 0x1484b40
D04EU: D04HR: 0 D04LR: 0 D04LV: 0
D04NE: 0 D04NV: No PV D04PR: 0 D04PV:
D05CA: PTR (nil) D05CV: 0 D05DA: PTR 0x147cdc0
D05EU: D05HR: 0 D05LR: 0 D05LV: 0
D05NE: 0 D05NV: No PV D05PR: 0 D05PV:
D06CA: PTR (nil) D06CV: 0 D06DA: PTR 0x147cdc0
D06EU: D06HR: 0 D06LR: 0 D06LV: 0
D06NE: 0 D06NV: No PV D06PR: 0 D06PV:
D07CA: PTR (nil) D07CV: 0 D07DA: PTR 0x147cdc0
D07EU: D07HR: 0 D07LR: 0 D07LV: 0
D07NE: 0 D07NV: No PV D07PR: 0 D07PV:
D08CA: PTR (nil) D08CV: 0 D08DA: PTR 0x147cdc0
D08EU: D08HR: 0 D08LR: 0 D08LV: 0
D08NE: 0 D08NV: No PV D08PR: 0 D08PV:
D09CA: PTR (nil) D09CV: 0 D09DA: PTR 0x147cdc0
D09EU: D09HR: 0 D09LR: 0 D09LV: 0
D09NE: 0 D09NV: No PV D09PR: 0 D09PV:
D10CA: PTR (nil) D10CV: 0 D10DA: PTR 0x147cdc0
D10EU: D10HR: 0 D10LR: 0 D10LV: 0
D10NE: 0 D10NV: No PV D10PR: 0 D10PV:
D11CA: PTR (nil) D11CV: 0 D11DA: PTR 0x147cdc0
D11EU: D11HR: 0 D11LR: 0 D11LV: 0
D11NE: 0 D11NV: No PV D11PR: 0 D11PV:
D12CA: PTR (nil) D12CV: 0 D12DA: PTR 0x147cdc0
D12EU: D12HR: 0 D12LR: 0 D12LV: 0
D12NE: 0 D12NV: No PV D12PR: 0 D12PV:
D13CA: PTR (nil) D13CV: 0 D13DA: PTR 0x147cdc0
D13EU: D13HR: 0 D13LR: 0 D13LV: 0
D13NE: 0 D13NV: No PV D13PR: 0 D13PV:
D14CA: PTR (nil) D14CV: 0 D14DA: PTR 0x147cdc0
D14EU: D14HR: 0 D14LR: 0 D14LV: 0
D14NE: 0 D14NV: No PV D14PR: 0 D14PV:
D15CA: PTR (nil) D15CV: 0 D15DA: PTR 0x147cdc0
D15EU: D15HR: 0 D15LR: 0 D15LV: 0
D15NE: 0 D15NV: No PV D15PR: 0 D15PV:
D16CA: PTR (nil) D16CV: 0 D16DA: PTR 0x147cdc0
D16EU: D16HR: 0 D16LR: 0 D16LV: 0
D16NE: 0 D16NV: No PV D16PR: 0 D16PV:
D17CA: PTR (nil) D17CV: 0 D17DA: PTR 0x147cdc0
D17EU: D17HR: 0 D17LR: 0 D17LV: 0
D17NE: 0 D17NV: No PV D17PR: 0 D17PV:
D18CA: PTR (nil) D18CV: 0 D18DA: PTR 0x147cdc0
D18EU: D18HR: 0 D18LR: 0 D18LV: 0
D18NE: 0 D18NV: No PV D18PR: 0 D18PV:
D19CA: PTR (nil) D19CV: 0 D19DA: PTR 0x147cdc0
D19EU: D19HR: 0 D19LR: 0 D19LV: 0
D19NE: 0 D19NV: No PV D19PR: 0 D19PV:
D20CA: PTR (nil) D20CV: 0 D20DA: PTR 0x147cdc0
D20EU: D20HR: 0 D20LR: 0 D20LV: 0
D20NE: 0 D20NV: No PV D20PR: 0 D20PV:
D21CA: PTR (nil) D21CV: 0 D21DA: PTR 0x147cdc0
D21EU: D21HR: 0 D21LR: 0 D21LV: 0
D21NE: 0 D21NV: No PV D21PR: 0 D21PV:
D22CA: PTR (nil) D22CV: 0 D22DA: PTR 0x147cdc0
D22EU: D22HR: 0 D22LR: 0 D22LV: 0
D22NE: 0 D22NV: No PV D22PR: 0 D22PV:
D23CA: PTR (nil) D23CV: 0 D23DA: PTR 0x147cdc0
D23EU: D23HR: 0 D23LR: 0 D23LV: 0
D23NE: 0 D23NV: No PV D23PR: 0 D23PV:
D24CA: PTR (nil) D24CV: 0 D24DA: PTR 0x147cdc0
D24EU: D24HR: 0 D24LR: 0 D24LV: 0
D24NE: 0 D24NV: No PV D24PR: 0 D24PV:
D25CA: PTR (nil) D25CV: 0 D25DA: PTR 0x147cdc0
D25EU: D25HR: 0 D25LR: 0 D25LV: 0
D25NE: 0 D25NV: No PV D25PR: 0 D25PV:
D26CA: PTR (nil) D26CV: 0 D26DA: PTR 0x147cdc0
D26EU: D26HR: 0 D26LR: 0 D26LV: 0
D26NE: 0 D26NV: No PV D26PR: 0 D26PV:
D27CA: PTR (nil) D27CV: 0 D27DA: PTR 0x147cdc0
D27EU: D27HR: 0 D27LR: 0 D27LV: 0
D27NE: 0 D27NV: No PV D27PR: 0 D27PV:
D28CA: PTR (nil) D28CV: 0 D28DA: PTR 0x147cdc0
D28EU: D28HR: 0 D28LR: 0 D28LV: 0
D28NE: 0 D28NV: No PV D28PR: 0 D28PV:
D29CA: PTR (nil) D29CV: 0 D29DA: PTR 0x147cdc0
D29EU: D29HR: 0 D29LR: 0 D29LV: 0
D29NE: 0 D29NV: No PV D29PR: 0 D29PV:
D30CA: PTR (nil) D30CV: 0 D30DA: PTR 0x147cdc0
D30EU: D30HR: 0 D30LR: 0 D30LV: 0
D30NE: 0 D30NV: No PV D30PR: 0 D30PV:
D31CA: PTR (nil) D31CV: 0 D31DA: PTR 0x147cdc0
D31EU: D31HR: 0 D31LR: 0 D31LV: 0
D31NE: 0 D31NV: No PV D31PR: 0 D31PV:
D32CA: PTR (nil) D32CV: 0 D32DA: PTR 0x147cdc0
D32EU: D32HR: 0 D32LR: 0 D32LV: 0
D32NE: 0 D32NV: No PV D32PR: 0 D32PV:
D33CA: PTR (nil) D33CV: 0 D33DA: PTR 0x147cdc0
D33EU: D33HR: 0 D33LR: 0 D33LV: 0
D33NE: 0 D33NV: No PV D33PR: 0 D33PV:
D34CA: PTR (nil) D34CV: 0 D34DA: PTR 0x147cdc0
D34EU: D34HR: 0 D34LR: 0 D34LV: 0
D34NE: 0 D34NV: No PV D34PR: 0 D34PV:
D35CA: PTR (nil) D35CV: 0 D35DA: PTR 0x147cdc0
D35EU: D35HR: 0 D35LR: 0 D35LV: 0
D35NE: 0 D35NV: No PV D35PR: 0 D35PV:
D36CA: PTR (nil) D36CV: 0 D36DA: PTR 0x147cdc0
D36EU: D36HR: 0 D36LR: 0 D36LV: 0
D36NE: 0 D36NV: No PV D36PR: 0 D36PV:
D37CA: PTR (nil) D37CV: 0 D37DA: PTR 0x147cdc0
D37EU: D37HR: 0 D37LR: 0 D37LV: 0
D37NE: 0 D37NV: No PV D37PR: 0 D37PV:
D38CA: PTR (nil) D38CV: 0 D38DA: PTR 0x147cdc0
D38EU: D38HR: 0 D38LR: 0 D38LV: 0
D38NE: 0 D38NV: No PV D38PR: 0 D38PV:
D39CA: PTR (nil) D39CV: 0 D39DA: PTR 0x147cdc0
D39EU: D39HR: 0 D39LR: 0 D39LV: 0
D39NE: 0 D39NV: No PV D39PR: 0 D39PV:
D40CA: PTR (nil) D40CV: 0 D40DA: PTR 0x147cdc0
D40EU: D40HR: 0 D40LR: 0 D40LV: 0
D40NE: 0 D40NV: No PV D40PR: 0 D40PV:
D41CA: PTR (nil) D41CV: 0 D41DA: PTR 0x147cdc0
D41EU: D41HR: 0 D41LR: 0 D41LV: 0
D41NE: 0 D41NV: No PV D41PR: 0 D41PV:
D42CA: PTR (nil) D42CV: 0 D42DA: PTR 0x147cdc0
D42EU: D42HR: 0 D42LR: 0 D42LV: 0
D42NE: 0 D42NV: No PV D42PR: 0 D42PV:
D43CA: PTR (nil) D43CV: 0 D43DA: PTR 0x147cdc0
D43EU: D43HR: 0 D43LR: 0 D43LV: 0
D43NE: 0 D43NV: No PV D43PR: 0 D43PV:
D44CA: PTR (nil) D44CV: 0 D44DA: PTR 0x147cdc0
D44EU: D44HR: 0 D44LR: 0 D44LV: 0
D44NE: 0 D44NV: No PV D44PR: 0 D44PV:
D45CA: PTR (nil) D45CV: 0 D45DA: PTR 0x147cdc0
D45EU: D45HR: 0 D45LR: 0 D45LV: 0
D45NE: 0 D45NV: No PV D45PR: 0 D45PV:
D46CA: PTR (nil) D46CV: 0 D46DA: PTR 0x147cdc0
D46EU: D46HR: 0 D46LR: 0 D46LV: 0
D46NE: 0 D46NV: No PV D46PR: 0 D46PV:
D47CA: PTR (nil) D47CV: 0 D47DA: PTR 0x147cdc0
D47EU: D47HR: 0 D47LR: 0 D47LV: 0
D47NE: 0 D47NV: No PV D47PR: 0 D47PV:
D48CA: PTR (nil) D48CV: 0 D48DA: PTR 0x147cdc0
D48EU: D48HR: 0 D48LR: 0 D48LV: 0
D48NE: 0 D48NV: No PV D48PR: 0 D48PV:
D49CA: PTR (nil) D49CV: 0 D49DA: PTR 0x147cdc0
D49EU: D49HR: 0 D49LR: 0 D49LV: 0
D49NE: 0 D49NV: No PV D49PR: 0 D49PV:
D50CA: PTR (nil) D50CV: 0 D50DA: PTR 0x147cdc0
D50EU: D50HR: 0 D50LR: 0 D50LV: 0
D50NE: 0 D50NV: No PV D50PR: 0 D50PV:
D51CA: PTR (nil) D51CV: 0 D51DA: PTR 0x147cdc0
D51EU: D51HR: 0 D51LR: 0 D51LV: 0
D51NE: 0 D51NV: No PV D51PR: 0 D51PV:
D52CA: PTR (nil) D52CV: 0 D52DA: PTR 0x147cdc0
D52EU: D52HR: 0 D52LR: 0 D52LV: 0
D52NE: 0 D52NV: No PV D52PR: 0 D52PV:
D53CA: PTR (nil) D53CV: 0 D53DA: PTR 0x147cdc0
D53EU: D53HR: 0 D53LR: 0 D53LV: 0
D53NE: 0 D53NV: No PV D53PR: 0 D53PV:
D54CA: PTR (nil) D54CV: 0 D54DA: PTR 0x147cdc0
D54EU: D54HR: 0 D54LR: 0 D54LV: 0
D54NE: 0 D54NV: No PV D54PR: 0 D54PV:
D55CA: PTR (nil) D55CV: 0 D55DA: PTR 0x147cdc0
D55EU: D55HR: 0 D55LR: 0 D55LV: 0
D55NE: 0 D55NV: No PV D55PR: 0 D55PV:
D56CA: PTR (nil) D56CV: 0 D56DA: PTR 0x147cdc0
D56EU: D56HR: 0 D56LR: 0 D56LV: 0
D56NE: 0 D56NV: No PV D56PR: 0 D56PV:
D57CA: PTR (nil) D57CV: 0 D57DA: PTR 0x147cdc0
D57EU: D57HR: 0 D57LR: 0 D57LV: 0
D57NE: 0 D57NV: No PV D57PR: 0 D57PV:
D58CA: PTR (nil) D58CV: 0 D58DA: PTR 0x147cdc0
D58EU: D58HR: 0 D58LR: 0 D58LV: 0
D58NE: 0 D58NV: No PV D58PR: 0 D58PV:
D59CA: PTR (nil) D59CV: 0 D59DA: PTR 0x147cdc0
D59EU: D59HR: 0 D59LR: 0 D59LV: 0
D59NE: 0 D59NV: No PV D59PR: 0 D59PV:
D60CA: PTR (nil) D60CV: 0 D60DA: PTR 0x147cdc0
D60EU: D60HR: 0 D60LR: 0 D60LV: 0
D60NE: 0 D60NV: No PV D60PR: 0 D60PV:
D61CA: PTR (nil) D61CV: 0 D61DA: PTR 0x147cdc0
D61EU: D61HR: 0 D61LR: 0 D61LV: 0
D61NE: 0 D61NV: No PV D61PR: 0 D61PV:
D62CA: PTR (nil) D62CV: 0 D62DA: PTR 0x147cdc0
D62EU: D62HR: 0 D62LR: 0 D62LV: 0
D62NE: 0 D62NV: No PV D62PR: 0 D62PV:
D63CA: PTR (nil) D63CV: 0 D63DA: PTR 0x147cdc0
D63EU: D63HR: 0 D63LR: 0 D63LV: 0
D63NE: 0 D63NV: No PV D63PR: 0 D63PV:
D64CA: PTR (nil) D64CV: 0 D64DA: PTR 0x147cdc0
D64EU: D64HR: 0 D64LR: 0 D64LV: 0
D64NE: 0 D64NV: No PV D64PR: 0 D64PV:
D65CA: PTR (nil) D65CV: 0 D65DA: PTR 0x147cdc0
D65EU: D65HR: 0 D65LR: 0 D65LV: 0
D65NE: 0 D65NV: No PV D65PR: 0 D65PV:
D66CA: PTR (nil) D66CV: 0 D66DA: PTR 0x147cdc0
D66EU: D66HR: 0 D66LR: 0 D66LV: 0
D66NE: 0 D66NV: No PV D66PR: 0 D66PV:
D67CA: PTR (nil) D67CV: 0 D67DA: PTR 0x147cdc0
D67EU: D67HR: 0 D67LR: 0 D67LV: 0
D67NE: 0 D67NV: No PV D67PR: 0 D67PV:
D68CA: PTR (nil) D68CV: 0 D68DA: PTR 0x147cdc0
D68EU: D68HR: 0 D68LR: 0 D68LV: 0
D68NE: 0 D68NV: No PV D68PR: 0 D68PV:
D69CA: PTR (nil) D69CV: 0 D69DA: PTR 0x147cdc0
D69EU: D69HR: 0 D69LR: 0 D69LV: 0
D69NE: 0 D69NV: No PV D69PR: 0 D69PV:
D70CA: PTR (nil) D70CV: 0 D70DA: PTR 0x147cdc0
D70EU: D70HR: 0 D70LR: 0 D70LV: 0
D70NE: 0 D70NV: No PV D70PR: 0 D70PV:
DATA: 1 DDLY: 0 DESC: Load ramp DISA: 0
DISP: 0 DISS: NO_ALARM DISV: 1 DPT : 0
DSTATE: POSTED DTYP: <nil> EVNT: EXSC: 0
FAZE: IDLE FFO : USE F-FLAGS FLNK: CONSTANT FPTS: FREEZE
KILL: 0 LCNT: 0 LPAU: GO MPTS: 1000
NAME: XF:28IDD-CTPress_RampScan NPTS: 1000 NSEV: NO_ALARM
NSTA: NO_ALARM P1AR: ABSOLUTE P1CA: PTR (nil) P1CP: 0
P1CV: 0 P1DV: 0 P1EP: 0 P1EU:
P1FC: NO P1FE: NO P1FI: NO P1FS: NO
P1FW: NO P1HR: 0 P1LR: 0 P1LV: 0
P1NV: PV BAD P1PA: PTR 0x1465600 P1PP: 0 P1PR: 0
P1PV: XF:28IDD-CTPress_PID.VAL PP MS P1RA: PTR 0x146d340 P1SI: 0
P1SM: LINEAR P1SP: 0 P1WD: 0 P2AR: ABSOLUTE
P2CA: PTR (nil) P2CP: 0 P2CV: 0 P2DV: 0
P2EP: 0 P2EU: P2FC: NO P2FE: NO
P2FI: NO P2FS: NO P2FW: NO P2HR: 0
P2LR: 0 P2LV: 0 P2NV: No PV P2PA: PTR 0x1467550
P2PP: 0 P2PR: 0 P2PV: P2RA: PTR 0x14711e0
P2SI: 0 P2SM: LINEAR P2SP: 0 P2WD: 0
P3AR: ABSOLUTE P3CA: PTR (nil) P3CP: 0 P3CV: 0
P3DV: 0 P3EP: 0 P3EU: P3FC: NO
P3FE: NO P3FI: NO P3FS: NO P3FW: NO
P3HR: 0 P3LR: 0 P3LV: 0 P3NV: No PV
P3PA: PTR 0x14694a0 P3PP: 0 P3PR: 0 P3PV:
P3RA: PTR 0x1475080 P3SI: 0 P3SM: LINEAR P3SP: 0
P3WD: 0 P4AR: ABSOLUTE P4CA: PTR (nil) P4CP: 0
P4CV: 0 P4DV: 0 P4EP: 0 P4EU:
P4FC: NO P4FE: NO P4FI: NO P4FS: NO
P4FW: NO P4HR: 0 P4LR: 0 P4LV: 0
P4NV: No PV P4PA: PTR 0x146b3f0 P4PP: 0 P4PR: 0
P4PV: P4RA: PTR 0x1478f20 P4SI: 0 P4SM: LINEAR
P4SP: 0 P4WD: 0 PACT: 0 PASM: STAY
PAUS: GO PCPT: 0 PDLY: 0.04 PHAS: 0
PINI: YES PRIO: HIGH PUTF: 0 PXSC: 0
R1CV: 0 R1DL: 0 R1LV: 0 R1NV: No PV
R1PV: R2CV: 0 R2DL: 0 R2LV: 0
R2NV: No PV R2PV: R3CV: 0 R3DL: 0
R3LV: 0 R3NV: No PV R3PV: R4CV: 0
R4DL: 0 R4LV: 0 R4NV: No PV R4PV:
RDLY: 0 REFD: 1 RPRO: 0 SCAN: Passive
SDIS: CONSTANT SEVR: NO_ALARM SMSG: Killing scan (kill=1/3)
STAT: NO_ALARM T1CD: 1 T1NV: No PV T1PV:
T2CD: 1 T2NV: No PV T2PV: T3CD: 1
T3NV: No PV T3PV: T4CD: 1 T4NV: No PV
T4PV: TIME: <undefined> TLAP: 00 00 00 00 00 00 00 00
TOLP: 8e 6e 6c 3b 12 c6 39 20 TPRO: 0 TSE : 0
TSEL: CONSTANT UDF : 0 UDFS: INVALID VAL : 0
VERS: 5.53 WAIT: 0 WCNT: 0 WTNG: 0
XSC : 0
Best,
Ji Li
[email protected]>
Sent: Wednesday, August 4, 2021 18:31
To: Li, Ji <
[email protected]>
Cc:
[email protected] <
[email protected]>
Did you look at the screens for all 4 positioners and all 70 detectors to see if there is a disconnected PV?
Send the output of
dbpr scanrec 2
Sent from my iPhone
On Aug 4, 2021, at 5:04 PM, Li, Ji via Tech-talk <
We have an IOC doing ramps (1-D scan) using sscan record. It had been working properly in Debian 7 until recently we switched to RHEL8. When setting the EXSC field of the sscan record to 1, the scan didn't start as expected. The IOC reported:
Starting new scan with unexpected faze ('SCAN_PENDING').
The SMSG field or the sscan record read:
Waiting for PV's to connect
And the CPT field remained 0.
The sscan record has D01PV and P1PV associated with PVs also created in this IOC, both shown as connected, readable and writable from cainfo.
Is it possible to find out what PVs, or actually something else causing this problem?
Thanks for any comments.
Ji Li