Subject: crash in CAS-event (high load?)
From: Heinz Junkes via Tech-talk <[email protected]>
To: EPICS Tech Talk <[email protected]>
Date: Tue, 21 Sep 2021 12:03:45 +0200
I am having problems with an RTEMS system (5.1) running Epics 7.
The system runs with a MVME6100.
With 10 Hz a Struck SIS3316 (digitizer, 16 channels) is read out.
The data is stored in PVs (4000 values, DOUBLE, per channel).
(ca. 5 MByte/s)
Several clients subscribe to these PVs.
Unfortunately, there is a crash after some time (variable, sometimes after 5 minutes,
sometimes after 2 hours).
It looks to me that the crash happens in a CAS event - task.
I don't know the best way to resolve the problem (debug, how?).
Setting CASDEBUG outputs too much and I can not cope with this.
Gruss Heinz
         CAS-TCP      0x1bf14d8    184614936     18      46       OK
         CAS-UDP      0x1bf1640    184614937     16      41       OK
      CAS-beacon      0x1bf19c0    184614938     17      44       OK
       CAS-event      0x1d85440    184614939     19      49       OK
      CAS-client      0x1d855b0    184614940     20      51       OK
    save_restore       0xc8f208    184614941     20      51       OK
       CAS-event      0x1fcac68    184614942     35      89       OK
      CAS-client      0x1fcb260    184614943     36      92       OK
       CAS-event      0x1fda060    184614944     19      49       OK
      CAS-client      0x1fda1d0    184614914     20      51       OK
       CAC-event      0x1fd84e8    184614918     21      54       OK
       CAS-event      0x202fcf8    184614919     19      49       OK
      CAS-client      0x202fe68    184614945     20      51       OK
! The dump does not match the thread IDs from above, the dump is from a previous crash
! 0x0b010024 was a CAS-event thread
> fatal source: INTERNAL_ERROR_CORE
bsp_fatal_extension(): RTEMS terminated -- no way back to MotLoad so I reset the card
Printing a stack trace for your convenience :-)
fatal source: RTEMS_FATAL_SOURCE_EXCEPTION
exception vector 3 (0x3)
  next PC or address of fault = 0x00230314
  saved MSR = 0x02009032
  context = interrupt, ISR nest level = 1
  thread dispatch disable level = 2
  R0  = 0x0022a67c R1  = 0x002fe690 R2  = 0x00000000 R3  = 0x00000030
  R4  = 0x0000000a R5  = 0x0028b37c R6  = 0x002fe6e8 R7  = 0x002272c4
  R8  = 0x002fe6c8 R9  = 0xa5a5a5a5 R10 = 0x002fe6c8 R11 = 0x00000000
  R12 = 0x40842202 R13 = 0x002bfc98 R14 = 0x002f4e00 R15 = 0x002c0000
  R16 = 0x00000000 R17 = 0x00000055 R18 = 0x002f4648 R19 = 0x002f0000
  R20 = 0x00000019 R21 = 0x0028ce74 R22 = 0x00000004 R23 = 0x002b8d50
  R24 = 0x002f6814 R25 = 0x00000000 R26 = 0x002747e0 R27 = 0x0014cdf0
  R28 = 0x002fe7c8 R29 = 0x002fe698 R30 = 0x0027484c R31 = 0x01fe9208
  CR  = 0x40842208
  CTR = 0x0000001b
  XER = 0x00000000
  LR  = 0x0022a680
  DAR = 0xa5a5a5a9
  executing thread ID = 0x0b010024, name =
Stack Trace:
  IP: 0x00230314, LR: 0x0022a680
--^ 0x0022a67c--^ 0x0014ceb0--^ 0x0014d0ec--^ 0x0014d144--^ 0x00149df8
--^ 0x00142e50--^ 0x001217c0--^ 0x0011a704--^ 0x00231b64--^ 0x0022b0ec
--^ 0x002272c4fatal source: RTEMS_FATAL_SOURCE_EXCEPTION
  next PC or address of fault = 0x002267dc
  saved MSR = 0x02001032
  R0  = 0x002267e8 R1  = 0x002fe380 R2  = 0x00000000 R3  = 0x0028a594
  R4  = 0x00000034 R5  = 0x00000000 R6  = 0x80000000 R7  = 0x0028a59f
  R8  = 0x0028a59e R9  = 0xa5a5a5a5 R10 = 0xf1120005 R11 = 0x00000000
  R12 = 0x40442804 R13 = 0x002bfc98 R14 = 0x002fe460 R15 = 0x002c0000
  R24 = 0x002f6814 R25 = 0x00000000 R26 = 0x002747e0 R27 = 0x0024ff10
  R28 = 0xcccccccd R29 = 0x0028a594 R30 = 0x002fe950 R31 = 0x0000000c
  CR  = 0x40442808
  CTR = 0x0021f9c8
  XER = 0x20000000
  LR  = 0x002267e8
  DAR = 0xa5a5a5a9
Stack Trace:
  IP: 0x002267dc, LR: 0x002267e8
--^ 0x0021f4ec--^ 0x0014ceb0--^ 0x0014d0ec--^ 0x00230914--^ 0x00227438
--^ 0x40842202--^ 0x0022a67c--^ 0x0014ceb0--^ 0x0014d0ec--^ 0x0014d144
--^ 0x00149df8--^ 0x00142e50--^ 0x001217c0--^ 0x0011a704--^ 0x00231b64
--^ 0x0022b0ec--^ 0x002272c4fatal source: RTEMS_FATAL_SOURCE_EXCEPTION
  R0  = 0x002267e8 R1  = 0x002fe070 R2  = 0x00000000 R3  = 0x0028a594
  R12 = 0x40442804 R13 = 0x002bfc98 R14 = 0x002fe150 R15 = 0x002c0000
  R28 = 0xcccccccd R29 = 0x0028a594 R30 = 0x002fe950 R31 = 0x00000012
  CR  = 0x40442808
  CTR = 0x0021f9c8
  XER = 0x20000000
  LR  = 0x002267e8
  DAR = 0xa5a5a5a9
Stack Trace:
--^ 0x002267e8--^ 0x0021f4ec--^ 0x0014ceb0--^ 0x0014d0ec--^ 0x00230914
--^ 0x00227438--^ 0x40842202--^ 0x0022a67c--^ 0x0014ceb0--^ 0x0014d0ec
--^ 0x0014d144--^ 0x00149df8--^ 0x00142e50--^ 0x001217c0--^ 0x0011a704
--^ 0x00231b64--^ 0x0022b0ec--^ 0x002272c4fatal source: RTEMS_FATAL_SOURCE_EXCEPTION
  R0  = 0x002267e8 R1  = 0x002fdd60 R2  = 0x00000000 R3  = 0x0028a594
  R12 = 0x40442804 R13 = 0x002bfc98 R14 = 0x002fde40 R15 = 0x002c0000
  R28 = 0xcccccccd R29 = 0x0028a594 R30 = 0x002fe950 R31 = 0x00000018
  CR  = 0x40442808
  CTR = 0x0021f9c8
  XER = 0x20000000
  LR  = 0x002267e8
  DAR = 0xa5a5a5a9
Stack Trace:
--^ 0x00227438--^ 0x002267e8--^ 0x0021f4ec--^ 0x0014ceb0--^ 0x0014d0ec
--^ 0x00230914--^ 0x00227438--^ 0x40842202--^ 0x0022a67c--^ 0x0014ceb0
--^ 0x0014d0ec--^ 0x0014d144--^ 0x00149df8--^ 0x00142e50--^ 0x001217c0
--^ 0x0011a704--^ 0x00231b64--^ 0x0022b0ec--^ 0x002272c4fatal source: RTEMS_FATAL_SOURCE_EXCEPTION
  R0  = 0x002267e8 R1  = 0x002fda50 R2  = 0x00000000 R3  = 0x0028a594
  R12 = 0x40442804 R13 = 0x002bfc98 R14 = 0x002fdb30 R15 = 0x002c0000
  R28 = 0xcccccccd R29 = 0x0028a594 R30 = 0x002fe950 R31 = 0x0000001e
  CR  = 0x40442808
  CTR = 0x0021f9c8
  XER = 0x20000000
  LR  = 0x002267e8
  DAR = 0xa5a5a5a9
Stack Trace:
--^ 0x00230914--^ 0x00227438--^ 0x002267e8--^ 0x0021f4ec--^ 0x0014ceb0
--^ 0x0014d0ec--^ 0x00230914--^ 0x00227438--^ 0x40842202--^ 0x0022a67c
--^ 0x0014ceb0--^ 0x0014d0ec--^ 0x0014d144--^ 0x00149df8--^ 0x00142e50
--^ 0x001217c0--^ 0x0011a704--^ 0x00231b64--^ 0x0022b0ec--^ 0x002272c4
  R0  = 0x00226808 R1  = 0x002fd740 R2  = 0x00000000 R3  = 0x0028a594
  R4  = 0x0000000a R5  = 0x0024ff10 R6  = 0x002fd6c8 R7  = 0x0024ff12
  R8  = 0x0024ff11 R9  = 0xa5a5a5a5 R10 = 0xf1120005 R11 = 0x00000000
  R12 = 0x40442202 R13 = 0x002bfc98 R14 = 0x002fd820 R15 = 0x002c0000
  R28 = 0xcccccccd R29 = 0x0028a594 R30 = 0x002fe950 R31 = 0x00000024
  CR  = 0x40442808
  CTR = 0x0021f9c8
  XER = 0x20000000
  LR  = 0x00226808
  DAR = 0xa5a5a5a9
Stack Trace:
  IP: 0x002267dc, LR: 0x00226808
--^ 0x0014d0ec--^ 0x00230914--^ 0x00227438--^ 0x002267e8--^ 0x0021f4ec
--^ 0x0014ceb0--^ 0x0014d0ec--^ 0x00230914--^ 0x00227438--^ 0x40842202
  R0  = 0x002267e8 R1  = 0x002fd430 R2  = 0x00000000 R3  = 0x0028a594
  R12 = 0x40442804 R13 = 0x002bfc98 R14 = 0x002fd510 R15 = 0x002c0000
  R28 = 0xcccccccd R29 = 0x0028a594 R30 = 0x002fe950 R31 = 0x0000002a
  CR  = 0x40442808
  CTR = 0x0021f9c8
  XER = 0x20000000
  LR  = 0x002267e8
  DAR = 0xa5a5a5a9
Stack Trace:
--^ 0x00226808--^ 0x0021f4ec--^ 0x0014ceb0--^ 0x0014d0ec--^ 0x00230914
--^ 0x0014ceb0--^ 0x0014d0ec--^ 0x00230914--^ 0x00227438--^ 0x002267e8
  R0  = 0x002267e8 R1  = 0x002fd120 R2  = 0x00000000 R3  = 0x0028a594
  R12 = 0x40442804 R13 = 0x002bfc98 R14 = 0x002fd200 R15 = 0x002c0000
  R28 = 0xcccccccd R29 = 0x0028a594 R30 = 0x002fe950 R31 = 0x00000030
  CR  = 0x40442808
  CTR = 0x0021f9c8
  XER = 0x20000000
  LR  = 0x002267e8
  DAR = 0xa5a5a5a9
Stack Trace:
--^ 0x00227438--^ 0x00226808--^ 0x0021f4ec--^ 0x0014ceb0--^ 0x0014d0ec
Too many stack frames (stack possibly corrupted), giving up...
0x02270848--> 0x02270844--> 0x01363632--> 0x01364204--> 0x02296084
0x02257976--> 0x02254824--> 0x02225388--> 0x01363632--> 0x01364204
0x02296084--> 0x02257976--> 0x02254824--> 0x02225388--> 0x01363632
0x01364204--> 0x02296084--> 0x02257976--> 0x02254856--> 0x02225388
0x01363632--> 0x01364204--> 0x02296084--> 0x02257976--> 0x02254824
0x02225388--> 0x01363632--> 0x01364204--> 0x02296084--> 0x02257976
0x02254824--> 0x02225388--> 0x01363632--> 0x01364204--> 0x02296084
Viele Grüße
Heinz Junkes
Experience directly varies with equipment ruined.
Attachment: smime.p7s
Description: S/MIME cryptographic signature
Re: crash in CAS-event (high load?) Michael Davidsaver via Tech-talk
Prev: Re: Allied Vision camera oddity Cobb, Tom (DLSLtd,RAL,LSCI) via Tech-talk
Next: Re: crash in CAS-event (high load?) Michael Davidsaver via Tech-talk
Prev: Re: Install EPICS on debian11 Florian Feldbauer via Tech-talk