Subject: RE: QuadEM operation with parameters "Queued"
From: Iain Marcuson via Tech-talk <[email protected]>
Date: Thu, 21 Oct 2021 18:55:00 +0000
I wrapped the send/receive with semaphores, so that should stop any clobbering.  I still observed the weird behavior on PC1.  I then pointed EPICS to a different computer (PC2) running the middle layer, whereupon I was not seeing the message backlog.  I am wondering if either there was a change to the middle layer on PC2 that hasn’t been reflected to PC1, or if messages on PC1 were too fast, being localhost and a faster machine.  I did not see these problems on PC2.
Sent: Thursday, October 21, 2021 12:19 PM
To: Iain Marcuson <[email protected]>
Cc: [email protected]
You can add some asynPrint statements with before the member buffer is written to and see if one thread is clobbering the string before it is written.  Use ASYN_TRACEINFO_THREAD to see what thread is calling it.
Sent: Thursday, October 21, 2021 11:08 AM
I took a look, and it seems that I only call unlock() in a different thread that reads the data over its own socket, versus the command handling thread(s?) where I don’t do any locking.
Sent: Thursday, October 21, 2021 12:03 PM
  • I am assuming I am not doing ASYN_CANBLOCK, as I see no references to it in the code
Actually the base drvQuadEM class sets ASYN_CANBLOCK in its constructor, so you don’t need to worry about it.
One thing that could cause a problem is if your driver is calling unlock() after it writes to the member buffer but before the pasynOctetSyncIO functions are called.  Then another thread could get access to your member char buffer.
Sent: Thursday, October 21, 2021 9:34 AM
> asyn does queue both write and read operations if you create your driver with the ASYN_CANBLOCK flag.  Did you do that?
> How does your polling record work, i.e. is it going through your quadEM driver and then the underlying drvAsynIPPort driver?
The record has a SCAN field of 1 second.  When it is triggered, it invoke ::writeInt32(), which sets the output buffer to the empty string and then calls the function writeReadMeter() to write and read from the hardware.  writeReadMeter() skips the write on an empty string, and then reads the input buffer until empty.
> Changing parameter A and having no message sent does not make sense to me unless the asyn queueRequest is timing out.  Are there any messages on the IOC console when this happens?
I am having trouble reproducing the problem, but I don’t recall any messages like that.
> > All writes, which includes the 1 Hz record mentioned above, write to the same shared buffer that is then sent, so might there be contention there?
> Does your polling record write to a record which then results in your driver's writeOctet or similar method being called?  If so, then it should be OK because if you set ASYN_CANBLOCK then both the drvAsynIPPort driver lock, and the asynPortDriver lock for your quadEM driver will be held when writeOctet is called.  If you then write to the shared buffer and immediately call the underlying drvAsynIPPort->write() function then it should not be possible for 2 threads to be trying to use the shared buffer at the same time.
The polling record writes to a member char array and ultimately invokes pasynOctetSyncIO->write() and pasynOctetSyncIO->read().  There is no writing to another record.
From: Tech-talk <[email protected]> on behalf of Iain Marcuson via Tech-talk <[email protected]>
Sent: Thursday, October 21, 2021 8:52 AM
To:
[email protected]
Subject: QuadEM operation with parameters "Queued"
I am working on writing a new IOC for QuadEM device, and the IOC mostly works.  The IOC talks over TCP via asyn to a middle software layer that talks to the hardware.  The middle layer can send unsolicited messages to EPICS, so I implemented polling by having a record scan once a second and read the port.  Sometimes, however, I get a case where EPICS seems to be queueing writes, so I would get
Change parameter A -> No message send
Change parameter B -> Send A
Change parameter C -> Send B
Thank you,
Iain Marcuson
Software Engineer, Sydor Technologies
585.278.1168 | www.SydorTechnologies.com
Skype: [email protected]
This message has been scanned for malware by Forcepoint. www.forcepoint.com
Click here to report this email as spam.
RE: QuadEM operation with parameters "Queued" Iain Marcuson via Tech-talk
Re: QuadEM operation with parameters "Queued" Mark Rivers via Tech-talk
RE: QuadEM operation with parameters "Queued" Mark Rivers via Tech-talk
Prev: Re: motor module make error Johnson, Andrew N. via Tech-talk
Next: Re: Measurement Computing USB-1608G_2AO support Hu, Yong via Tech-talk
Prev: RE: QuadEM operation with parameters "Queued" Mark Rivers via Tech-talk
Next: RE: QuadEM operation with parameters "Queued" Iain Marcuson via Tech-talk
