1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  <2022>  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  <2022>  2023  2024  2025  2026
Subject: Re: Understanding EPICS_CA_ADDR_LIST and caget
From: Jörn Dreyer via Tech-talk <[email protected]>
Date: Thu, 08 Sep 2022 11:40:11 +0200
Hi Sean,
some more suggestions on the network issue. Normally between two subnets there
is a firewall setup that blocks all traffic besides some ports and all
broadcasts. To figure out if you can reach the IOC you could use nmap like
this:
nmap -p 5064  195.194.120.115
If that does not find the port to be in open state, you will either need to ask
your IT to open that port on the firewall, or set up an EPICS gateway on a PC
that has two NICs into the two subnets.
Issue the nmap command on both machines. At least on the machine running the
IOC the port should be reported to be open.
This would be my first tests in such a case.
Regards
Jörn
Am Donnerstag, 8. September 2022, 11:23:37 CEST schrieb Jure Varlec via Tech-
talk:
> Hello Sean,
> As long as you have EPICS_CA_AUTO_ADDR_LIST set to YES, broadcast searches
> will be done in addition to what you have specified in EPICS_CA_ADDR_LIST.
> In other words, both broadcast searches to broadcast-capable interfaces and
> unicast searches to explicitly listed addresses will happen. More
> information on how this works is available in the CA Reference Manual,
> which is linked at the bottom of the page that you referenced in your
> message. And also below 🙂
> https://epics.anl.gov/base/R3-14/12-docs/CAref.html#EPICS
> This explains why you still see broadcast searches done on your first
> interface. You should also see broadcasts on the other interfaces, and
> unicast searches as well. But you do not, because tcpdump will only listen
> on the first interface by default. You should tell it to listen on any
> interface, it will give you a wider picture of what's going on.
> Best,
> Jure
> ________________________________
> From: Tech-talk <[email protected]> on behalf of Sean Leavey via
 Sent: Thursday, September 8, 2022 10:20
> To: [email protected] <[email protected]>
> Subject: Understanding EPICS_CA_ADDR_LIST and caget
> Caution: This email originated from outside of Cosylab.
> Hi tech talkers,
> I don't seem to be able to change the behaviour of caget using
> EPICS_CA_ADDR_LIST. I'm probably misunderstanding something.
> I've got EPICS Base installed on my machine. In one terminal I've got
> tcpdump monitoring port 5064. In another terminal I run caget with a
> made-up channel. Here's their output after I run caget:
> $ caget FAKE:CHANNEL
> Channel connect timed out: 'FAKE:FAKE' not found.
> $ tcpdump port 5064
> tcpdump: verbose output suppressed, use -v[v]... for full protocol decode
> listening on wlan0, link-type EN10MB (Ethernet), snapshot length 262144
> bytes
> 09:11:07.345310 IP totoro.41026 > 172.16.15.255.ca-1: UDP, length 48
> 09:11:07.377158 IP totoro.41026 > 172.16.15.255.ca-1: UDP, length 48
> 09:11:07.441438 IP totoro.41026 > 172.16.15.255.ca-1: UDP, length 48
> 09:11:07.569269 IP totoro.41026 > 172.16.15.255.ca-1: UDP, length 48
> 09:11:07.825253 IP totoro.41026 > 172.16.15.255.ca-1: UDP, length 48
> So far, so good? Looks like caget is sending 5 broadcast packets then
> giving up. 172.16.15.255 is my link's broadcast address, verified with
> `ip addr`.
> But what if I know the IP of the IOC that hosts a channel, and want to
> specify it directly? I read in [1]:
>  > To reach IOCs on one or more additional subnets, the environment
> variable EPICS_CA_ADDR_LIST needs to be configured. It can list either
> the specific IP addresses of each IOC, or the broadcast address of their
> subnet. Note, however, that routers will often not forward broadcast
> requests, which suggests using specific IP addresses.
> This sounds useful to me because my IOC is in a different subnet. From
> the quoted text above, I understand that, by setting EPICS_CA_ADDR_LIST
> to the IP of my IOC, caget should talk directly to it. But apparently
> this is not the case. Keeping tcpdump open, and running the caget
> command again but this time with the address of my IOC set in
> EPICS_CA_ADDR_LIST, I get the same output:
> $ EPICS_CA_ADDR_LIST=195.194.120.115 caget FAKE:FAKE
> $ tcpdump port 5064
> 09:14:18.995465 IP totoro.35942 > 172.16.15.255.ca-1: UDP, length 48
> 09:14:19.027341 IP totoro.35942 > 172.16.15.255.ca-1: UDP, length 48
> 09:14:19.091486 IP totoro.35942 > 172.16.15.255.ca-1: UDP, length 48
> 09:14:19.219462 IP totoro.35942 > 172.16.15.255.ca-1: UDP, length 48
> 09:14:19.475597 IP totoro.35942 > 172.16.15.255.ca-1: UDP, length 48
> Clearly I'm misunderstanding how all of this works. Can someone shed
> some light on what EPICS_CA_ADDR_LIST does in the context of caget, if
> anything?
> Cheers,
> Sean
> [1]
> https://epics-controls.org/resources-and-support/documents/howto-documents/c
> onfigure-channel-access/#IOCs_on_different_subnets
> This email and any attachments are intended solely for the use of the named
> recipients. If you are not the intended recipient you must not use,
> disclose, copy or distribute this email or any of its attachments and
> should notify the sender immediately and delete this email from your
> system. UK Research and Innovation (UKRI) has taken every reasonable
> precaution to minimise risk of this email or any attachments containing
> viruses or malware but the recipient should carry out its own virus and
> malware checks before opening the attachments. UKRI does not accept any
> liability for any losses or damages which the recipient may sustain due to
> presence of any viruses.
Re: Understanding EPICS_CA_ADDR_LIST and caget Sean Leavey via Tech-talk
Re: Understanding EPICS_CA_ADDR_LIST and caget Jure Varlec via Tech-talk
Prev: Re: Understanding EPICS_CA_ADDR_LIST and caget Jure Varlec via Tech-talk
Next: Getting a time series of some NDPluginStats Iain Marcuson via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  <2022>  2023  2024  2025  2026
Next: Re: Understanding EPICS_CA_ADDR_LIST and caget Sean Leavey via Tech-talk