1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  <2024>  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  <2024>  2025  2026
Subject: Re: AW: Readback of output variables in adsDriver
From: Torsten Bögershausen via Tech-talk <[email protected]>
To: "Meyer, Markus" <[email protected]>, "[email protected]" <[email protected]>
Date: Mon, 22 Apr 2024 06:12:10 +0200
Hej again,
I haven't manage to find the time to set up a test system yet -
hope that you have more luck.
Here are the good news.
After chatting with out expert:
epics-twincat-ads does support read back of output records !
One precondition is the '?' at the end of the OUT field:
<https://urldefense.us/v3/__https://github.com/EuropeanSpallationSource/epics-twincat-ads/blob/045f40f2e80057025befe015b89b80288157c479/adsExApp/Db/adsTestAsyn.db*L12__;Iw!!G_uCfscf7eWS!a7O2n5uR7qlxzkr_aV81uRdqnKyuvf9l5qwggdWT010Ihel6kTj_imLAZsLVjZxb-MOwsMHmnOk00TXTcII$ >
The "SetFAmplitudeRB" record should do what you ask for:
Writing to the EPICS PV changes the value in the PLC.
Once the value in the PLC is changed, that change should be
seen in the output record.
HTH - and please let us know, how it goes.
On 2024-04-15 18:21, Torsten Bögershausen via Tech-talk wrote:
Hej all,
I did have a short look into the driver -
adsTestAsyn.db does have a READBACK, but I couldn't find anything
in the code, to switch it on or off.
But I know for sure, that people from SLAC have contributed a bulk read,
so far only 1Hz.
Similar to Jure's driver, so far nobody had asked seriously enough
for READBACK so no time had been invested here.
Having said that, why do you not get any data ?
Wrong "ads port" ?
I sometimes run wireshark to find out, what is going on.
/Torsten
On 2024-04-15 16:54, Meyer, Markus via Tech-talk wrote:
Hello Jure, Mark and Torsten,
Thank you all for your responses and explanations of the 2 cases.
I kindly ask you to open a pair of issues on the Github repo. I can't say when we we'll be able to take a closer look (we're stretched pretty thin right now), but having open issues helps raise the priority.
I will do that and maybe I can help with some code after I have finished my evaluation of the other available drivers.
Case 2, at least, is probably not that hard to implement. Case 1, on the other hand, is a bit thornier because of the design of the driver.
It may be OK to do the readback after iocInit only in a cyclic interval.
We here at ESS use a different driver for ADS, and if that one can do the readback ? I haven't checked - but I highly suspect that it doesn't.
I have compiled the latest source of the driver from ESS [1] and can connect to my plc but unfortunately I get no values from the plc at all. I am still investigating what I am doing wrong here. I expect a readback because it's explicitly mentioned in the adsTestAsyn.db of adsExApp.
Markus
[1] https://urldefense.us/v3/__https://github.com/EuropeanSpallationSource/epics-twincat-ads__;!!G_uCfscf7eWS!cWY-oNbq-4U-gg1N5Q8SvI_E4DLNAd9tVgk5xrioIeV8ejfmVohmnmNpsp_rKDUJGlJGz2RJXqJ_poyPHDdx8g$
-----Ursprüngliche Nachricht-----
Von: Tech-talk <[email protected]> Im Auftrag von Jure Varlec via Tech-talk
Gesendet: Montag, 15. April 2024 12:49
An: [email protected]
Betreff: Re: Readback of output variables in adsDriver
Hello Markus,
Mark made a nice breakdown of the two cases. Right now, the adsDriver module supports neither. We are aware of this, but honestly, nobody has needed it badly enough yet :) . I kindly ask you to open a pair of issues on the Github repo. I can't say when we we'll be able to take a closer look (we're stretched pretty thin right now), but having open issues helps raise the priority.
Case 2, at least, is probably not that hard to implement. Case 1, on the other hand, is a bit thornier because of the design of the driver. It is focused on doing bulk reads, which are needed to get sufficient performance with lots of variables. But such reads can only be done after all the records are initialized and ADS variables made known to the driver. So, initial readbacks were disabled for simplicity. They can be added for sure, but it won't be a simple bolt-on.
Cheers,
Jure
On 4/12/24 18:11, Mark Rivers via Tech-talk wrote:
Caution: This email originated from outside of Cosylab.
Hi Markus,
There are 2 separate cases here:
1) The PV value getting set to the PLC value during iocInit.
2) The PV value getting set to the PLC value when the PLC values changes after iocInit.
Case 1 is handled as follows:
- During iocInit the ao record device support (devAsynFloat64.c) does a read from the driver to get the current PLC value.  If that read operation returns asynSuccess then the PV should be set to the PLC value, otherwise it is not changed.  This definitely works fine with the Modbus driver, for example.  I am not sure about the adsDriver, since I have not used it.  You can add debugging to the driver to track that down.
Case 2 is handled by adding the line you did to database:
      info(asyn:READBACK, "1")
That should make the ao record value update to match the PLC value when the PLC value is changed outside of EPICS.  Note that this line is NOT required for getting the behavior described in Case 1 above.
-----Original Message-----
From: Tech-talk <[email protected]> On Behalf Of Meyer,
Sent: Friday, April 12, 2024 10:25 AM
To: [email protected]
Subject: Readback of output variables in adsDriver
Dear all,
I am evaluating possibilities to communicate with a plc and other
hardware from beckhoff. I have successfully build the adsDriver [1]
device support and it seems to work very well for input variables. I
can also write output variables, but if the value gets changed on the
plc itself (e.g. by the interlock logic or by another connected
protocol) it is not synced back to the pv. It also seems that the
current value is not initially read on startup of the IOC.
For example, this is the pv definition:
record(ao, "$(P):IC:CB01-SSet") {
      field(DTYP, "asynFloat64")
      field(PREC, "2")
      field(EGU,  "%")
      field(DRVH, "100")
      field(DRVL, "-100")
      field(OUT,  "@asyn($(PORT) 0 0) REAL W P=PLC_TC3 V=HMI.IC.CB01.SSet")
Before I start the IOC, the plc value is set to 2. If I start the IOC,
the value of the pv is set to 0. The Timestamp is updated. The value
in the plc gets not changed. I expected, that the pv value is also set
to 2. Writing a value to the pv is working as expected.
Did I miss something here? What can I do to subscribe for changes of
output variables?
Markus
[1]
https://urldefense.us/v3/__https://github.com/Cosylab/adsDriver__;!!G_
uCfscf7eWS!eovU-aYXFfsZIvbTx6Y3tTGma4zwbWLi1xy-LUyW3RghomFH88t9jP45toK
nZq8oo1pt5gT5tQhGnPd9QXmCruzGkJg$
AW: AW: Readback of output variables in adsDriver Meyer, Markus via Tech-talk
Re: AW: Readback of output variables in adsDriver Torsten Bögershausen via Tech-talk
Prev: Re: Epics Integration with Allen Bradley 1769-L33ER PLC John Dobbins via Tech-talk
Next: behavior of PINI Di Wang via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  <2024>  2025  2026
Prev: Re: AW: Readback of output variables in adsDriver Torsten Bögershausen via Tech-talk
Next: AW: AW: Readback of output variables in adsDriver Meyer, Markus via Tech-talk
