1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  <2025>  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  <2025>  2026
Subject: Re: Modbus-TCP "authorization"
From: Виталий Балакин via Tech-talk <[email protected]>
Date: Mon, 1 Dec 2025 10:23:53 +0700
Thanks for the idea!
I will test it and then let you know the result.
With gratitude,
Vitalii
вт, 25 нояб. 2025 г. в 23:48, Mark Rivers <[email protected]>:
Hi Vitalii,
I think I see a way you can do this, though I have not tested it.
  • Set the underlying asyn TCP driver to have disconnectOnReadTimeout=Y.
  • Create one Modbus port that only does the authentication with a dedicated database for that.
  • Load an asyn record on the TCP driver port and on each of the Modbus asyn ports.
  • Set the Modbus asyn ports to have autoConnect=0.  That way they will only connect when explicitly commanded to.
  • Have one calcout record that monitors the CNCT field of the TCP port asyn record
  • When CNCT makes a transition from 0 to 1 (i.e. a connect event) then it triggers processing of a seq record that does the following:
    • Set CNCT of the Modbus authentication port asyn record to 1.  It will then connect.
    • Process the authentication records.
    • Set the CNCT fields of the remaining Modbus port asyn records to 1. Normal I/O will then start.
  • When CNCT makes a transition from 1 to 0 (i.e. a disconnect event) then it triggers processing of a seq record that does the following:
    • Set CNCT of all the Modbus ports asyn records including the authentication port to 0
From: Tech-talk <[email protected]> On Behalf Of Виталий Балакин via Tech-talk
Sent: Tuesday, November 25, 2025 9:38 AM
To: Abdalla Ahmad <[email protected]>
Cc: [email protected]
The problem is not in the sequence, but rather how to *trigger* it upon
connect.  I.e.:
1. Perform Modbus reads and writes *immediately* after connect() success.
2. *Before* any other I/O takes place.
3. Repeat it upon further reconnects (also before any other I/O).
Looking at
https://epics-modules.github.io/modbus/ I can't find any way to
achieve this.
With appreciation,
Vitalii
вт, 18 нояб. 2025 г. в 14:25, Abdalla Ahmad <[email protected]>:
You can try writing a record for each authorization step with passive scan (or no SCAN) and then each record process the next with FLNK, with this you can only process the first record and the rest are processed sequentially. We do have a similar situation where a Modbus device requires setting a password for administrator access, we made a record that just writes a value to a certain address and we have admin access to the device.
Best Regards,
Abdalla Al-Dalleh
Control Engineer
SESAME
From: Tech-talk <[email protected]> On Behalf Of ??????? ??????? via Tech-talk
Sent: Tuesday, November 18, 2025 6:33 AM
To: [email protected]
Subject: Modbus-TCP "authorization"
Hi!
I have a Modbus-TCP device which requires a so called "authorization" to
be performed BEFORE any actual I/O can take place; without such an
authorization all register writes and even reads result in exception 2
("illegal data address").
The "authorization" consists of several register reads and writes, in
specific order:
   1. Write INT32_LE:0x89ABCDEF to holding registers 0x2100,0x2101
   2. Write INT32_LE:0x01234567 to holding registers 0x2102,0x2103
   3. Write 0 to holding register 0x2104
   4. Read discrete input 0x2200
Is there some mechanism to perform this sequence immediately upon connect?
Looking at "modbus" module documentation, I see nothing relevant.
Thanks in advance!
Vitalii
Modbus-TCP "authorization" Виталий Балакин via Tech-talk
RE: Modbus-TCP "authorization" Abdalla Ahmad via Tech-talk
Re: Modbus-TCP "authorization" Виталий Балакин via Tech-talk
RE: Modbus-TCP "authorization" Mark Rivers via Tech-talk
Prev: quadEM R9-6 released Mark Rivers via Tech-talk
Next: Further OMS PC78 questions James P. Withrow via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  <2025>  2026
Prev: RE: Modbus-TCP "authorization" Mark Rivers via Tech-talk
Next: Streaming from quadEM to HDF5 Graeme Winter via Tech-talk
