Hello, EPICS mates, I started to implement the “Model 3” driver for nanoFaktur EBD-060310 piezo controller. The attached files(.cpp and .h) are the work-in-progress source code. Not finished yet. I have some questions. 1. In asynMotorController.h, the data type of motorPosition_ and motorEncoderPosition_ are ints. But in derived class of asynMotorcontroller(like smarActMCSMotorDriver.cpp and ACRMotorDriver.cpp), the function setDoubleParam is used to set the above parameters. Why is that? 2. I can read the position(unit um, range 0 to 40) and voltage(unit volts, range -30 to 130) from the controller. But which one should I set to
motorPosition_and
motorEncoderPosition_? I don't quite understand. 3. The values of position and voltage from the controller are float values. When setting, say 2.123456, to motorEncoderPosition, it will become 2 (which is an int). How to handle this situation? Should I do some kind of transformation? For example, multiply by 1000,000? 4. In the member function: asynStatus poll(bool* moving_p), I need to set the moving/done status of the stage to moving_p and motorStatusDone_. But there is no such exact suitable command provided by thhe controller. A possible candidate is "get on-target status" meaning in closed-loop mode(servo ON), whether the position(from sensor) approached the set target or not. 5. The controller has two modes: closed-loop mode(servo ON), users set the desired potion(unit um). open-loop mode(servo OFF), uses set the voltage(unit volts). What should I set to motorPosition_? I think it should be something like "motor pulse". what should I set to motorEncoderPosition_.? I think it should be something like "encoder value". ps The controller uses binary communication protocol. The following example is to read the position(in um) of channel 0: hexadecimal bytes in little-endian: 10 00 01 20 02 00 20 00 00 ac 01 00 00 00 00 fe 10 00: total length, 16 bytes 01 20: command ID, 0x2001 means "get position" 02 00: custom ID, used to distinguish different client programs. 20: option, 0x20 means "read" 00: sequence number, Used in very long responses. Not used in commands. 00: interface id, RS-232 or USB or Ethernet. Not used in commands. ac: header checksum 01: data format, 01 means 32-bit unsigned int 00 00 00 00: data, channel 0 fe: checksum The response: 13 00 01 20 02 00 10 00 01 b8 00 00 02 70 74 6a 3e 13 00: total length, 19 bytes 01 20: command ID, 0x2001 means "get position" 02 00: custom ID, used to distinguish different client programs. 10: option, 0x10 means "final, no more". 00: sequence number, 01: interface id, 0x01 means RS-232. b8: header checksum 00: data format, 00 means 8-bit unsigned int 00: data, channel 0 02: data format, 02 means float 70 74 6a 3e: data, 0.228960 (position in um) 3e: checksum Any suggestions and responses are appreciated. Thank you. On Thu, Apr 24, 2025 at 5:31 AM Mark Rivers <rivers at cars.uchicago.edu> wrote:
/* Motor driver support for nanoFAKTUR EBD-060310 Piezo Controller */
/* Derived from ACRMotorDriver.cpp by Mark Rivers, 2011/3/28 */
/* Derived from smarActMCSMotorDriver.cpp Till Straumann <strauman at slac.stanford.edu>, 9/11 */
/* Author: LiangChih Chiang <chiang.lc at nsrrc.org.tw>, 2026/01/21 */
#include <nanoFakturEBDDriver.h>
#include <stdio.h>
#include <stdlib.h>
#include <string.h>
#include <math.h>
#include <iocsh.h>
#include <epicsString.h>
#include <epicsExport.h>
#include <asynOctetSyncIO.h>
#include <errlog.h>
/* Static configuration parameters (compile-time constants) */
// #undef DEBUG
#define DEBUG
/* The asyn motor driver apparently can't cope with exceptions */
#undef ASYN_CANDO_EXCEPTIONS
// #define ASYN_CANDO_EXCEPTIONS
/* Define this if exceptions should be thrown and it is OK to abort the application */
#undef DO_THROW_EXCEPTIONS
// #define DO_THROW_EXCEPTIONS
#if defined(ASYN_CANDO_EXCEPTIONS) || defined(DO_THROW_EXCEPTIONS)
#define THROW_(e) throw e
#else
#define THROW_(e) epicsPrintf("%s\n",e.what());
#endif
#define DEFAULT_TIMEOUT 2.0
/* endian, byte order; start */
#define FLOAT_SIZE 4
#define DOUBLE_SIZE 8
// determine the endian of the platform
static int is_little_endian() {
uint32_t test = 1;
return *(uint8_t*)&test == 1;
// reverse byte order
static void reverse_bytes(uint8_t* bytes, size_t len) {
size_t i;
for (i = 0; i < len / 2; i++) {
uint8_t temp = bytes[i];
bytes[i] = bytes[len - 1 - i];
bytes[len - 1 - i] = temp;
// little-endian 4-bytes to float(of the platform-endian)
static float le_bytes_to_float(const uint8_t* le_bytes) {
uint8_t temp[FLOAT_SIZE];
float result;
memcpy(temp, le_bytes, FLOAT_SIZE); // copy to a temporary buffer
if (!is_little_endian()) { // reverse byte order if it's big-endian
reverse_bytes(temp, FLOAT_SIZE);
memcpy(&result, temp, FLOAT_SIZE); // platform-endian
return result;
// float(of the platform-endian) to little-endian 4-bytes
static void float_to_le_bytes(float value, uint8_t* le_bytes) {
memcpy(temp, &value, FLOAT_SIZE);
memcpy(le_bytes, temp, FLOAT_SIZE);
// little-endian 8-bytes to double(of the platform-endian)
static double le_bytes_to_double(const uint8_t* le_bytes) {
uint8_t temp[DOUBLE_SIZE];
double result;
memcpy(temp, le_bytes, DOUBLE_SIZE);
reverse_bytes(temp, DOUBLE_SIZE);
memcpy(&result, temp, DOUBLE_SIZE);
return result;
// double(of the platform-endian) to little-endian 8-bytes
static void double_to_le_bytes(double value, uint8_t* le_bytes) {
memcpy(temp, &value, DOUBLE_SIZE);
memcpy(le_bytes, temp, DOUBLE_SIZE);
/* endian, byte order; end */
/* nanaFaktur EBD; start */
// command id; consult nankFaktur EBD controller manual for details
#define CMD_CMD_LEVEL 0xFFF0
#define CMD_STOP_MOTION 0x2043
#define CMD_SERVO_ON 0x2040
#define CMD_CURRENT_CTRL_TARGET 0x2015
#define CMD_CURRENT_CTRL_VOLT 0x2014
#define CMD_CURRENT_POS_ERROR 0x2013
#define CMD_CURRENT_TARGET 0x2012
#define CMD_OVERFLOW_STATUS 0x2011
#define CMD_ON_TARGET_STATUS 0x2010
#define CMD_OPEN_LOOP_TARGET_REL 0x2005
#define CMD_OPEN_LOOP_TARGET 0x2004
#define CMD_CLOSE_LOOP_TARGET_REL 0x2003
#define CMD_CLOSE_LOOP_TARGET 0x2002
#define CMD_GET_POS 0x2001
// command and response use the same binary package definition;
// byte order is little-endian;
// a package contains a header and zero-to-multiple parameters(data)
// uint16_t len; // total package size
// uint16_t CmdId; // command ID
// uint16_t CustomId; // value will be just returned (can be used for software-routinue)
// uint8_t opt; // option: e.g. controller should acknowledge, CRC or check-sum, etc.
// uint8_t seq; // sequence number: set by controller for response
// uint8_t IntfId; // interface ID: set by controller
// uint8_t ChkSumHeader; // checksum for the header
// uint8_t param0_fmt; // parameters
// param0_data // size of data depends on the format
// uint8_t param1_fmt;
// param1_data
// etc..
// uint8_t ChkSumData; // checksum for parameters
// from nF_common.h
#define MAX_PACKAGE_LEN 1024 //!< maximal comamnd/response package size
#define MAX_CMDIN_PARAMETER_NUM 128 //!< maximal number of parameters in command package (to controller)
#define MAX_RSP_PARAMETER_NUM 512 //!< maximal number of parameters in response package (from controller)
#define MAX_PARAMETER_STRLEN 32 //!< maximal string length for controller's paramaters
// define lesser value which is ok if no need to process a response
// containing a lot of strings
#define MAX_PARAM_COUNT 6
// parameters union; modified from nF_interface.h
union ParamVal{
double dData; // double
float fData; // float
uint32_t uData; // unsigned int
int32_t nData; // signed int
char sData[MAX_PARAMETER_STRLEN]; // space reserved for string
// package header
#define HEADER_AND_CHECKSUM_SIZE (10)
#define HEADER_SIZE (HEADER_AND_CHECKSUM_SIZE - 1)
#define HEADER_START_I (0)
#define HEADER_CHECKSUM_I (HEADER_START_I + HEADER_SIZE)
// package params(data)
// params_and_checksum_size = package_size - HEADER_AND_CHECKSUM_SIZE
// params_size = params_and_checksum_size - 1
#define PARAMS_START_I HEADER_AND_CHECKSUM_SIZE
// params_checksum_i = package_size - 1
// from nF_common.h; params(data) format
#define CMD_DATA_FMT_U8 0 // unsigned char (Byte)
#define CMD_DATA_FMT_U32 1 // unsigned int (D-Word)
#define CMD_DATA_FMT_FLOAT 2 // float
#define CMD_DATA_FMT_DOUBLE 3 // double
#define CMD_DATA_FMT_STRING 4 // string
#define CMD_DATA_FMT_S32 5 // int
#define CMD_DATA_FMT_CHAR 6 // char
#define CMD_DATA_FMT_U16 7 // unsigned short (Word)
#define CMD_DATA_FMT_S16 8 // short
#define CMD_DATA_FMT_ARRAY 9 // array of data: (fmt_array, ArrSize, dataFmt, data[])
#define CMD_DATA_FMT_LF 10 // for host software: show a line-feed
#define CMD_DATA_FMT_INVALID 0xFF
typedef struct {
uint16_t len;
uint16_t cmdId;
uint16_t customId;
uint8_t opt;
uint8_t seq;
uint8_t intfId;
uint16_t checksumHeader;
size_t paramsCount; // not in actual package
uint8_t fmts[MAX_PARAM_COUNT]; // parameter formats
ParamVal vals[MAX_PARAM_COUNT]; // parameter values
uint16_t checksumParams;
} nfPackageStruct;
// note: nFControl.exe uses 0x0001
// Command Terminal in nFControl.exe uses 0x0002
#define CUSTOM_ID_EPICS 0x000E
#define OPT_CMD_READ 0x20
#define OPT_CMD_WRITE 0x21
#define OPT_RSP_READ_MORE 0x90
#define OPT_RSP_READ_END 0x10
#define OPT_RSP_READ_ERROR 0x20
// ok or error
#define OPT_RSP_WRITE 0x21
// error code of response
// 0(zero) is ok; other values are errors
// as I know, error codes are all negative values.
#define RSP_ERR_OK 0
static const char *rsp_err_to_str(int32_t err) {
switch (err) {
case RSP_ERR_OK: return "no error";
case -1: return "internal system error";
case -2: return "internal memory error";
case -3: return "internal function error";
case -10: return "command package length error";
case -11: return "command package check-sum error";
case -12: return "command input timeout error";
case -20: return "unknown command";
case -21: return "command operation not allowed";
case -22: return "currently command level too low";
case -23: return "command input syntax error";
case -24: return "command index out-of-range";
case -25: return "command input-data-format error";
case -26: return "command input-data-value out-of-range";
case -27: return "invalid number of input-data";
case -28: return "command execution timeout";
case -30: return "unknown parameter";
case -31: return "parameter operation not allowed";
case -32: return "parameter needs higher command level";
case -33: return "parameter input syntax error";
case -34: return "parameter index out-of-range";
case -35: return "parameter data-format error";
case -36: return "parameter value out-of-range";
case -40: return "wave parameter not valid";
case -37: return "string length out-of-range";
case -50: return "command password error";
case -51: return "command/parameter is read-only";
case -52: return "internal no enough memory error";
case -70: return "macro not found";
case -71: return "macro open() error";
case -72: return "macro read() error";
case -73: return "macro write() error";
case -74: return "macro remove() error";
case -75: return "macro is running";
case -76: return "not allowed when receiving macro";
default: return "Unknown response error code";
// error code of parsing packages
typedef enum {
PKG_ERR_OK = 0,
PKG_ERR_LEN = -1,
PKG_ERR_HEADER_CHECKSUM = -2,
PKG_ERR_PARAMS_CHECKSUM = -3,
PKG_ERR_PARAMS_TYPE = -4,
} nfPkgErrCode;
static const char *pkg_err_to_str(nfPkgErrCode err) {
switch (err) {
case PKG_ERR_OK: return "Ok";
case PKG_ERR_LEN: return "Package length(size) error";
case PKG_ERR_HEADER_CHECKSUM: return "Header checksum error";
case PKG_ERR_PARAMS_CHECKSUM: return "Params checksum error";
case PKG_ERR_PARAMS_TYPE: return "Params data type error";
default: return "Unknown error code";
// calculate the checksum of package header and package params
static uint8_t checksum(const uint8_t *arr, size_t len){
size_t i;
uint8_t cks = 0;
for(i = 0; i < len; i++){
cks += arr[i];
cks = 0xFF - cks;
return cks;
// parse package bytes into nfPackageStruct
static nfPkgErrCode parse_pkg(uint8_t *pkg, size_t pkg_size, nfPackageStruct *ps){
nfPkgErrCode err = PKG_ERR_OK;
ps->len = pkg[0] | (pkg[1] << 8);
if(ps->len != pkg_size){
#ifdef DEBUG
printf("Error: package size check fail: in package %u, given size %lu\n", ps->len, pkg_size);
#endif
err = PKG_ERR_LEN;
return err;
ps->cmdId = pkg[2] | (pkg[3] << 8);
ps->customId = pkg[4] | (pkg[5] << 8);
ps->opt = pkg[6];
ps->seq = pkg[7];
ps->intfId = pkg[8];
ps->checksumHeader = pkg[HEADER_CHECKSUM_I];
const uint8_t checksumHeaderCalc = checksum(pkg, HEADER_SIZE);
if(ps->checksumHeader != checksumHeaderCalc){
#ifdef DEBUG
printf("Error: header checksum fail: in package 0x%02x, calculated 0x%02x.\n", ps->checksumHeader, checksumHeaderCalc);
#endif
err = PKG_ERR_HEADER_CHECKSUM;
return err;
// parameters
size_t i = PARAMS_START_I; // index into package bytes
const size_t params_checksum_i = pkg_size - 1;
size_t j = 0; // index into params
while(i < params_checksum_i){
ps->fmts[j] = pkg[i];
switch(pkg[i]){
case CMD_DATA_FMT_U8:
ps->vals[j].uData = pkg[i+1];
i += (1+1);
break;
case CMD_DATA_FMT_U32:
ps->vals[j].uData = pkg[i+1] | (pkg[i+2] << 8) | (pkg[i+3] << 16) | (pkg[i+4] << 24);
i += (1+4);
break;
case CMD_DATA_FMT_FLOAT:
memcpy(&ps->vals[j].fData, &pkg[i+1], FLOAT_SIZE);
i += (1+FLOAT_SIZE);
break;
case CMD_DATA_FMT_DOUBLE:
memcpy(&ps->vals[j].dData, &pkg[i+1], DOUBLE_SIZE);
i += (1+DOUBLE_SIZE);
break;
case CMD_DATA_FMT_STRING:
strcpy(ps->vals[j].sData, (const char *)&pkg[i+1]);
i += (1 + strlen((const char *)&pkg[i+1]) + 1); // include NULL
break;
case CMD_DATA_FMT_S32:
ps->vals[j].nData = pkg[i+1] | (pkg[i+2] << 8) | (pkg[i+3] << 16) | (pkg[i+4] << 24);
i += (1+4);
break;
case CMD_DATA_FMT_CHAR:
i += (1+1);
break;
case CMD_DATA_FMT_U16:
ps->vals[j].uData = pkg[i+1] | (pkg[i+2] << 8);
i += (1+2);
break;
case CMD_DATA_FMT_S16:
ps->vals[j].nData = pkg[i+1] | (pkg[i+2] << 8);
i += (1+2);
break;
case CMD_DATA_FMT_ARRAY: // can not handle; skip remaining params
i = pkg_size;
#ifdef DEBUG
printf("Warning: un-handled param data format: 0x%02x(CMD_DATA_FMT_ARRAY).\n", CMD_DATA_FMT_ARRAY);
#endif
break;
case CMD_DATA_FMT_LF:
i += 1;
break;
case CMD_DATA_FMT_INVALID: // can not handle; skip remaining params
i = pkg_size;
#ifdef DEBUG
printf("Warning: un-handled param data format: 0x%02x(CMD_DATA_FMT_INVALID).\n", CMD_DATA_FMT_INVALID);
#endif
break;
default: // can not handle; skip remaining params
i = pkg_size;
#ifdef DEBUG
printf("Warning: un-handled unknown param data format: 0x%02x(?).\n", pkg[i]);
#endif
break;
j++;
ps->paramsCount = j;
if(ps->paramsCount > 0){ // has params
const size_t params_and_checksum_size = pkg_size - HEADER_AND_CHECKSUM_SIZE;
const size_t params_size = params_and_checksum_size - 1;
ps->checksumParams = pkg[params_checksum_i];
const uint8_t checksumParamsCalc = checksum(&pkg[PARAMS_START_I], params_size);
if(ps->checksumParams != checksumParamsCalc){
#ifdef DEBUG
printf("Error: params checksum fail: in package 0x%02x, calculated 0x%02x.\n", ps->checksumParams, checksumParamsCalc);
#endif
err = PKG_ERR_PARAMS_CHECKSUM;
return err;
return err;
#define NF_IS_WRITE_CMD 1
#define NF_IS_READ_CMD 0
// make command package
// return package size
static size_t make_pkg(uint16_t cmdId, int isReadCmd, size_t params_count, const uint8_t *fmts, const ParamVal *params, uint8_t *pkg){
size_t i = PARAMS_START_I; // package index
size_t j; // params count index
for(j = 0; j < params_count; j++){ // params
switch(fmts[j]){
pkg[i] = CMD_DATA_FMT_U8;
pkg[i+1] = params[j].uData & 0xFF;
i += (1+1);
break;
pkg[i] = CMD_DATA_FMT_U32;
pkg[i+2] = (params[j].uData >> 8) & 0xFF;
pkg[i+3] = (params[j].uData >> 16) & 0xFF;
pkg[i+4] = (params[j].uData >> 24) & 0xFF;
i += (1+4);
break;
pkg[i] = CMD_DATA_FMT_FLOAT;
float_to_le_bytes(params[j].fData, &pkg[i+1]);
break;
pkg[i] = CMD_DATA_FMT_DOUBLE;
double_to_le_bytes(params[j].dData, &pkg[i+1]);
break;
pkg[i] = CMD_DATA_FMT_STRING;
strcpy((char *)&pkg[i+1], params[j].sData);
i += (1 + strlen((char *)&pkg[i+1]) + 1);
break;
pkg[i] = CMD_DATA_FMT_S32;
pkg[i+1] = params[j].nData & 0xFF;
pkg[i+2] = (params[j].nData >> 8) & 0xFF;
pkg[i+3] = (params[j].nData >> 16) & 0xFF;
pkg[i+4] = (params[j].nData >> 24) & 0xFF;
i += (1+4);
break;
pkg[i] = CMD_DATA_FMT_CHAR;
i += (1+1);
break;
pkg[i] = CMD_DATA_FMT_U16;
i += (1+2);
break;
pkg[i] = CMD_DATA_FMT_S16;
i += (1+2);
break;
j = params_count;
#ifdef DEBUG
#endif
break;
pkg[i] = CMD_DATA_FMT_LF;
i += (1);
break;
j = params_count;
#ifdef DEBUG
#endif
break;
j = params_count;
#ifdef DEBUG
printf("Warning: un-handled unknown param data format: 0x%02x(?).\n", fmts[j]);
#endif
break;
const uint16_t params_size = i - PARAMS_START_I; // if 0, means no params
const uint16_t params_checksum_size = params_size > 0 ? params_size + 1 : 0;
const uint16_t pkg_size = HEADER_AND_CHECKSUM_SIZE + params_checksum_size;
pkg[0] = pkg_size & 0xFF; // len(size)
pkg[1] = (pkg_size >> 8) & 0xFF;
pkg[2] = cmdId & 0xFF; // cmdId
pkg[3] = (cmdId >> 8) & 0xFF;
pkg[4] = CUSTOM_ID_EPICS & 0xFF; // customId
pkg[5] = (CUSTOM_ID_EPICS >> 8) & 0xFF;
pkg[6] = isReadCmd == NF_IS_READ_CMD ? OPT_CMD_READ : OPT_CMD_WRITE; // opt
pkg[7] = 0; // seq
pkg[8] = 0; // intfId
pkg[HEADER_CHECKSUM_I] = checksum(pkg, HEADER_SIZE); // header checksum
if(params_size > 0){
const uint16_t params_checksum_i = pkg_size - 1;
pkg[params_checksum_i] = checksum(&pkg[PARAMS_START_I], params_size); // params checksum
return pkg_size;
/* nanaFaktur EBD; end */
/* NanoFakturEBDException; start */
NanoFakturEBDException::NanoFakturEBDException(NanoFakturEBDExceptionType t, const char *fmt, ...)
: t_(t)
va_list ap;
if ( fmt ) {
va_start(ap, fmt);
epicsVsnprintf(str_, sizeof(str_), fmt, ap);
va_end(ap);
} else {
str_[0] = 0;
NanoFakturEBDException::NanoFakturEBDException(NanoFakturEBDExceptionType t, const char *fmt, va_list ap)
: t_(t)
/* NanoFakturEBDException; end */
/* NanoFakturEBDController; start */
NanoFakturEBDController::NanoFakturEBDController(const char *portName, const char *IOPortName, int numAxes, double movingPollPeriod, double idlePollPeriod)
: asynMotorController(portName, // portName
numAxes, // numAxes
0, // numParams
0, // interfaceMask
0, // interruptMask
ASYN_CANBLOCK | ASYN_MULTIDEVICE, // asynFlags
1, // autoconnect
0, // priority
0) // stack size
, asynUserMot_p_(0)
asynStatus status;
char junk[100];
size_t got_junk;
int eomReason;
pAxes_ = (NanoFakturEBDAxis **)(asynMotorController::pAxes_);
asynPrint(this->pasynUserSelf, ASYN_TRACEIO_DRIVER, "NanoFakturEBDController pasynOctetSyncIO->connect to port %s\n", portName);
/* asynStatus (*connect)(const char *port, int addr, asynUser **ppasynUser, const char *drvInfo); */
status = pasynOctetSyncIO->connect(IOPortName, 0, &asynUserMot_p_, NULL);
if(status){
asynPrint(this->pasynUserSelf, ASYN_TRACE_ERROR,
"NanoFakturEBDController pasynOctetSyncIO->connect: cannot connect to port %s\n",
portName);
THROW_(NanoFakturEBDException(EBDConnectionError, "NanoFakturEBDController: unable to connect to controller"));
// slurp away any initial telnet negotiation; there is no guarantee that
// the other end will not send some telnet chars in the future. The terminal
// server should really be configured to 'raw' mode!
status = pasynOctetSyncIO->read(asynUserMot_p_, junk, sizeof(junk), 0.5, &got_junk, &eomReason);
if(got_junk){
asynPrint(this->pasynUserSelf, ASYN_TRACE_WARNING, "NanoFakturEBDController port %s: Warning: detected unexpected bytes on link (%s) initially.\n", portName, IOPortName);
/* set command level of the controller to 1; default is 0, not high enough */
status = setUint(CMD_CMD_LEVEL, 1);
if(status){
"NanoFakturEBDController port %s: Error: set command level failed. \n", portName);
// nanaFaktur EBD controllers use binary protocol, not ASCII protocol.
// pasynOctetSyncIO->setInputEos(asynUserMot_p_, "\n", 1);
// pasynOctetSyncIO->setOutputEos(asynUserMot_p_, "\n", 1);
// Create axes; move to iocsh function nanoFakturEBDCreateAxis()
/* for(ax = 0; ax < numAxes; ax++){
pAxes_[ax] = new NanoFakturEBDAxis(this, ax);
startPoller(movingPollPeriod, idlePollPeriod, 2);
// read command, channel
// response, ok, channel value u8 u32 float
// response, error code s32 < 0
// write command, channel value(uint or float)
// response, ok, s32 0 Acknowledge
// readInt, readFloat, return ok_or_error
// if something wrong, print
// write fmt value int, float
// read write
// 0x2001 u32 index - get position
// u8 index, float v
// 0x2002 u32 index u32 index, float v close-loop target
// u8 index, float v s32 0 ack
// 0x2003 - u32 index, float v set close-loop target relative
// s32 0 ack
// 0x2010 u32 index - get on-target status
// u8 index, u8 v(0,1)
// 0x2011 u32 index - get overflow status
// 0x2040 u32 index u32 index, u32 v(0,1) servo controlling set/get
// u8 index, u8 v(0,1) s32 0 ack
// 0x2043 - u32 index, (no value) Stop motion
// s32 0 ack
// 0xFFF0 - u32 level command level
// send a command and get response
asynStatus NanoFakturEBDController::cmdRsp(uint16_t cmdId, int32_t isReadCmd, size_t params_count, const uint8_t *fmts, const ParamVal *vals, size_t *params_count_out, uint8_t *fmts_out, ParamVal *vals_out)
asynStatus status;
uint8_t pkg[MAX_PACKAGE_LEN];
size_t pkg_size;
size_t nwrite;
int eomReason;
uint8_t pkg_rsp[MAX_PACKAGE_LEN];
size_t pkg_rsp_size;
nfPackageStruct ps_rsp;
nfPkgErrCode pkg_rsp_err_code;
size_t j;
pkg_size = make_pkg(cmdId, isReadCmd, params_count, fmts, vals, pkg);
asynStatus (*writeRead)(asynUser *pasynUser,
const char *write_buffer, size_t write_buffer_len,
char *read_buffer, size_t read_buffer_len,
double timeout,
size_t *nbytesOut, size_t *nbytesIn,
int *eomReason);
status = pasynOctetSyncIO->writeRead(asynUserMot_p_, (const char *)pkg, pkg_size,
(char *)pkg_rsp, MAX_PACKAGE_LEN,
DEFAULT_TIMEOUT, &nwrite, &pkg_rsp_size, &eomReason);
if(asynSuccess != status){
"Error: NanoFakturEBDController::cmdRsp pasynOctetSyncIO->writeRead, cmdId %04x, asynStatus %d\n",
cmdId, status);
return status;
pkg_rsp_err_code = parse_pkg(pkg_rsp, pkg_rsp_size, &ps_rsp);
if(PKG_ERR_OK != pkg_rsp_err_code){
"Error: NanoFakturEBDController::cmdRsp response package parse error, cmdId %04x, pkg_rsp_err_code %d, %s\n",
cmdId, pkg_rsp_err_code, pkg_err_to_str(pkg_rsp_err_code));
status = asynError;
return status;
// check if error
if(ps_rsp.paramsCount == 1 && ps_rsp.fmts[0] == CMD_DATA_FMT_S32 && ps_rsp.vals[0].nData != 0){
"Error: cmdRsp response error, cmdId 0x%04x, rsp_err_code %d %s\n",
cmdId, ps_rsp.vals[0].nData, rsp_err_to_str(ps_rsp.vals[0].nData));
status = asynError;
return status;
*params_count_out = ps_rsp.paramsCount;
for(j = 0; j < ps_rsp.paramsCount; j++){
fmts_out[j] = ps_rsp.fmts[j];
vals_out[j] = ps_rsp.vals[j];
return status;
// read command to get a value.
// fmt0/val0 is ususally channel number; can be CMD_DATA_FMT_INVALID if no params
asynStatus NanoFakturEBDController::getVal(uint16_t cmdId, uint8_t fmt0, const void *val0, void *val_out)
asynStatus status;
size_t params_count = 0;
uint8_t fmts[1];
ParamVal vals[1];
size_t params_count_out;
uint8_t fmts_out[3]; // channel, val_out,
ParamVal vals_out[3]; // params returned from controller may contains an LF
switch(fmt0){
fmts[0] = fmt0;
vals[0].uData = *(const uint32_t *)val0;
params_count++;
break;
fmts[0] = fmt0;
vals[0].nData = *(const int32_t *)val0;
params_count++;
break;
fmts[0] = fmt0;
vals[0].fData = *(const float *)val0;
params_count++;
break;
default: // other formats are not handled
break;
status = cmdRsp(cmdId, NF_IS_READ_CMD, params_count, fmts, vals, ¶ms_count_out, fmts_out, vals_out);
"Error: NanoFakturEBDController getVal cmdId %04x, asynStatus %d\n", cmdId, status);
return status;
// assume [0] is channel number
switch(fmts_out[1]){ // magic number 1 is for val_out
*(uint32_t *)val_out = vals_out[1].uData;
break;
*(int32_t *)val_out = vals_out[1].nData;
break;
*(float *)val_out = vals_out[1].fData;
break;
return status;
// read command; no params(no channel)
// example:
asynStatus NanoFakturEBDController::getUint(uint16_t cmdId, uint32_t *val_out)
return getVal(cmdId, CMD_DATA_FMT_INVALID, NULL, val_out);
asynStatus NanoFakturEBDController::getInt(uint16_t cmdId, int32_t *val_out)
asynStatus NanoFakturEBDController::getFloat(uint16_t cmdId, float *val_out)
// write command
// fmt0/val0 is ususally channel number or the value to set
// fmt1/val1 is usually the vale to set; can be CMD_DATA_FMT_INVALID if no params
// example: set closed-loop target of a channel
// example: set command level
asynStatus NanoFakturEBDController::setVal(uint16_t cmdId, uint8_t fmt0, const void *val0, uint8_t fmt1, const void *val1)
asynStatus status;
uint8_t fmts[2] = {fmt0, fmt1}; // magic number 2
const void *p_vals[2] = {val0, val1};
ParamVal vals[2];
size_t j;
uint8_t fmts_out[2]; // index 0 for response error code, s32 0 is ok.
ParamVal vals_out[2]; // index 1 is for extra safety
for(j = 0; j < 2; j++){
switch(fmts[params_count]){
vals[params_count].uData = *(const uint32_t *)p_vals[params_count];
params_count++;
break;
vals[params_count].nData = *(const int32_t *)p_vals[params_count];
params_count++;
break;
vals[params_count].fData = *(const float *)p_vals[params_count];
params_count++;
break;
status = cmdRsp(cmdId, NF_IS_WRITE_CMD, params_count, fmts, vals, ¶ms_count_out, fmts_out, vals_out);
"Error: NanoFakturEBDController setVal cmdId 0x%04x, asynStatus %d\n", cmdId, status);
return status;
return status;
// write command; one param(value) to set
asynStatus NanoFakturEBDController::setUint(uint16_t cmdId, uint32_t val)
return setVal(cmdId, CMD_DATA_FMT_U32, &val, CMD_DATA_FMT_INVALID, NULL);
asynStatus NanoFakturEBDController::setInt(uint16_t cmdId, int32_t val)
return setVal(cmdId, CMD_DATA_FMT_S32, &val, CMD_DATA_FMT_INVALID, NULL);
asynStatus NanoFakturEBDController::setFloat(uint16_t cmdId, float val)
return setVal(cmdId, CMD_DATA_FMT_FLOAT, &val, CMD_DATA_FMT_INVALID, NULL);
/* NanoFakturEBDController; end */
/* NanoFakturEBDAxis; start */
NanoFakturEBDAxis::NanoFakturEBDAxis(class NanoFakturEBDController *cnt_p, int axisNumber, int channel)
: asynMotorAxis(cnt_p, axisNumber), c_p_(cnt_p)
channel_ = channel;
asynPrint(c_p_->pasynUserSelf, ASYN_TRACEIO_DRIVER, "NanoFakturEBDAxis -- creating axis %d, channel %d\n", axisNumber, channel);
setIntegerParam(c_p_->motorStatusHasEncoder_, 1);
setIntegerParam(c_p_->motorStatusGainSupport_, 1);
// setIntegerParam(c_p_->motorPowerAutoOnOff_, 0);
// setDoubleParam(c_p_->motorPowerOnDelay_, 0);
// setDoubleParam(c_p_->motorPowerOffDelay_, 0);
// setDoubleParam(c_p_->motorPostMoveDelay_, 0);
// turn on servo; closed-loop
if( (comStatus_ = setUint(CMD_SERVO_ON, 1)) ){
setIntegerParam(c_p_->motorClosedLoop_, 0);
goto bail;
setIntegerParam(c_p_->motorClosedLoop_, 1);
bail:
setIntegerParam(c_p_->motorStatusProblem_, comStatus_ ? 1 : 0);
setIntegerParam(c_p_->motorStatusCommsError_, comStatus_ ? 1 : 0);
callParamCallbacks(); /* Do callbacks so higher layers see any changes */
if(comStatus_){
THROW_(NanoFakturEBDException(EBDCommunicationError, "NanoFakturEBDAxis::NanoFakturEBDAxis -- channel %u, ASYN error %i", axisNumber, comStatus_));
/* Obtain value of the 'motorClosedLoop_' parameter (which maps to the record's CNEN field) */
bool NanoFakturEBDAxis::getClosedLoop()
int val;
c_p_->getIntegerParam(channel_, c_p_->motorClosedLoop_, &val);
return val;
/* return 1 if encoder exists; return 0 otherwise */
bool NanoFakturEBDAxis::hasEncoder()
int val;
c_p_->getIntegerParam(channel_, c_p_->motorStatusHasEncoder_, &val);
return val;
// get(read) a value for this channel from controller (nothing to do with asyn's parameter library).
// read command, parameter 0 is channel number
// cmdId: controller command id
// val_out: where to store the value returned by the controller
// return: asynError if an error occurred, asynSuccess otherwise.
asynStatus NanoFakturEBDAxis::getUint(uint16_t cmdId, uint32_t *val_out)
return c_p_->getVal(cmdId, CMD_DATA_FMT_U32, &channel_, val_out);
asynStatus NanoFakturEBDAxis::getInt(uint16_t cmdId, int32_t *val_out)
asynStatus NanoFakturEBDAxis::getFloat(uint16_t cmdId, float *val_out)
// set(write) a value for this channel to controller
// write command, parameter 0 is channel number, parameter 1 is the value to set
asynStatus NanoFakturEBDAxis::setUint(uint16_t cmdId, uint32_t val)
return c_p_->setVal(cmdId, CMD_DATA_FMT_U32, &channel_, CMD_DATA_FMT_U32, &val);
asynStatus NanoFakturEBDAxis::setInt(uint16_t cmdId, int32_t val)
return c_p_->setVal(cmdId, CMD_DATA_FMT_U32, &channel_, CMD_DATA_FMT_S32, &val);
asynStatus NanoFakturEBDAxis::setFloat(uint16_t cmdId, float val)
return c_p_->setVal(cmdId, CMD_DATA_FMT_U32, &channel_, CMD_DATA_FMT_FLOAT, &val);
// write command, parameter 0 is channel number, no parameter 1
// example: stop motion
asynStatus NanoFakturEBDAxis::setNone(uint16_t cmdId)
return c_p_->setVal(cmdId, CMD_DATA_FMT_U32, &channel_, CMD_DATA_FMT_INVALID, NULL);
asynStatus NanoFakturEBDAxis::poll(bool* moving_p)
float val_pos;
float val_target; // voltage or position
uint32_t val_ontarget;
uint32_t val_overflow;
uint32_t cmdId = getClosedLoop() ? CMD_GET_POS : CMD_CURRENT_CTRL_TARGET;
if( (comStatus_ = getFloat(CMD_GET_POS, &val_pos)) ){
goto bail;
setDoubleParam(c_p_->motorEncoderPosition_, val_pos);
if( (comStatus_ = getFloat(cmdId, &val_target)) ){
goto bail;
setDoubleParam(c_p_->motorPosition_, val_target);
#ifdef DEBUG
printf("NanoFakturEBDAxis poll, channel %d, position %f, target %f", channel_, val_pos, val_target);
#endif
// is this correct? there is no direct command for the moving/stopped status of axis
if((comStatus_ = getUint(CMD_ON_TARGET_STATUS, &val_ontarget))){
goto bail;
*moving_p = !(getClosedLoop() && (bool)val_ontarget);
setIntegerParam(c_p_->motorStatusDone_, *moving_p ? 0 : 1);
#ifdef DEBUG
printf(", on-target status %u", val_ontarget);
#endif
if((comStatus_ = getUint(CMD_OVERFLOW_STATUS, &val_overflow))){
goto bail;
setIntegerParam(c_p_->motorStatusProblem_, val_overflow ? 1 : 0);
#ifdef DEBUG
printf(", overflow status %u", val_overflow);
#endif
bail:
#ifdef DEBUG
printf(".\n");
#endif
return comStatus_;
// unit of position, pulse
// unit of minVelocity and maxVelocity, pulse/second
// unit of acceleration, pulse/second^2, = (maxV - minV) / ACCL
asynStatus NanoFakturEBDAxis::move(double position, int relative, double min_vel, double max_vel, double accel)
uint32_t cmdId;
if(getClosedLoop()){
cmdId = relative ? CMD_CLOSE_LOOP_TARGET_REL : CMD_CLOSE_LOOP_TARGET;
else{
cmdId = relative ? CMD_OPEN_LOOP_TARGET_REL : CMD_OPEN_LOOP_TARGET;
#ifdef DEBUG
printf("NanoFakturEBDAxis move channel %u, %s, %s to %f (speed %f - %f); accel %f\n",
channel_, getClosedLoop() ? "ClosedLoop" : "OpenLoop", relative ? "relative" : "absolute", position, min_vel, max_vel, accel);
#endif
if( (comStatus_ = setFloat(cmdId, position)) ){
goto bail;
bail:
if(comStatus_){
setIntegerParam(c_p_->motorStatusProblem_, 1);
setIntegerParam(c_p_->motorStatusCommsError_, 1);
return comStatus_;
// jog
// No command we an use directly.
// Just move to a very far target.
asynStatus NanoFakturEBDAxis::moveVelocity(double min_vel, double max_vel, double accel)
double position = 40*1000000; // magic number
uint32_t cmdId = getClosedLoop() ? CMD_CLOSE_LOOP_TARGET : CMD_OPEN_LOOP_TARGET;
if(max_vel < 0){
position = -position;
#ifdef DEBUG
printf("NanoFakturEBDAxis moveVelocity channel %u, (%f - %f), accel %f\n",
channel_, min_vel, max_vel, accel);
#endif
goto bail;
bail:
if(comStatus_){
return comStatus_;
asynStatus NanoFakturEBDAxis::stop(double acceleration)
#ifdef DEBUG
printf("NanoFakturEBDAxis stop channel %d\n", channel_);
#endif
comStatus_ = setNone(CMD_STOP_MOTION);
if ( comStatus_ ) {
return comStatus_;
/* NanoFakturEBDAxis; end */
/* iocsh wrapping and registration business (stolen from ACRMotorDriver.cpp) */
/* nanoFakturEBDCreateController called to create one nanoFaktur EBD controller */
static const iocshArg cc_a0 = {"Port name [string]", iocshArgString};
static const iocshArg cc_a1 = {"I/O port name [string]", iocshArgString};
static const iocshArg cc_a2 = {"Number of axes [int]", iocshArgInt};
static const iocshArg cc_a3 = {"Moving poll period (ms) [double]", iocshArgDouble};
static const iocshArg cc_a4 = {"Idle poll period (ms) [double]", iocshArgDouble};
static const iocshArg * const cc_as[] = {&cc_a0, &cc_a1, &cc_a2, &cc_a3, &cc_a4};
static const iocshFuncDef cc_def = {"nanoFakturEBDCreateController", sizeof(cc_as)/sizeof(cc_as[0]), cc_as};
extern "C" void *
nanoFakturEBDCreateController(
const char *motorPortName, // port name used in motor record
const char *ioPortName, // asyn port name
int numAxes,
void *rval = 0;
// the asyn stuff doesn't seem to be prepared for exceptions. I get segfaults
// if constructing a controller (or axis) incurs an exception even if its
// caught (IMHO asyn should behave as if the controller/axis never existed...)
#ifdef ASYN_CANDO_EXCEPTIONS
try {
#endif
rval = new NanoFakturEBDController(motorPortName, ioPortName, numAxes, movingPollPeriod/1000, idlePollPeriod/1000); // create controller
} catch (NanoFakturEBDException &e) {
epicsPrintf("nanoFakturEBDCreateController failed (exception caught):\n%s\n", e.what());
rval = 0;
#endif
return rval;
static void cc_fn(const iocshArgBuf *args)
args[0].sval,
args[1].sval,
args[2].ival,
args[3].dval,
args[4].dval);
/* nanoFakturEBDCreateAxis called to create each axis of a nanoFaktur EBD controller */
static const iocshArg ca_a0 = {"Controller Port name [string]", iocshArgString};
static const iocshArg ca_a1 = {"Axis number [int]", iocshArgInt};
static const iocshArg ca_a2 = {"Channel [int]", iocshArgInt};
static const iocshArg * const ca_as[] = {&ca_a0, &ca_a1, &ca_a2};
static const iocshFuncDef ca_def = {"nanoFakturEBDCreateAxis", sizeof(ca_as)/sizeof(ca_as[0]), ca_as};
extern "C" void *
const char *controllerPortName,
int axisNumber, // from 0 to (numAxes-1); as index into asynMotorAxis **pAxes_ in asynMotorController
int channel) // used in commands sent to the controller hardware
void *rval = 0;
NanoFakturEBDController *pC;
NanoFakturEBDAxis *pAxis;
asynMotorAxis *pAsynAxis;
try {
#endif
pC = (NanoFakturEBDController *) findAsynPortDriver(controllerPortName);
if (!pC) {
printf("nanoFakturEBDCreateAxis: Error port %s not found\n", controllerPortName);
rval = 0;
return rval;
pAsynAxis = pC->getAxis(axisNumber);
if (pAsynAxis != NULL) { // check if axis number already exists
epicsPrintf("nanoFakturEBDCreateAxis failed: axis %u already exists\n", axisNumber);
THROW_(NanoFakturEBDException(EBDCommunicationError, "axis %u already exists", axisNumber));
#endif
rval = 0;
return rval;
pC->lock();
pAxis = new NanoFakturEBDAxis(pC, axisNumber, channel); // create axis
pAxis = NULL;
pC->unlock();
epicsPrintf("NanoFakturEBDAxis failed (exception caught):\n%s\n", e.what());
rval = 0;
#endif
return rval;
static void ca_fn(const iocshArgBuf *args)
args[0].sval,
args[1].ival,
args[2].ival);
static void nanoFakturEBDRegister(void)
iocshRegister(&cc_def, cc_fn); // CreateController
iocshRegister(&ca_def, ca_fn); // CreateAxis
extern "C" {
epicsExportRegistrar(nanoFakturEBDRegister);
#ifndef NANOFAKTUR_EBD_DRIVER_H
#define NANOFAKTUR_EBD_DRIVER_H
#ifdef __cplusplus
#include <stdarg.h>
#include <stdint.h>
#include <exception>
#include <asynMotorController.h>
#include <asynMotorAxis.h>
union ParamVal;
typedef union ParamVal ParamVal;
#define EXCEPTION_STR_LEN_MAX 100
enum NanoFakturEBDExceptionType {
EBDUnknownError,
EBDConnectionError,
class NanoFakturEBDException : public std::exception {
public:
NanoFakturEBDException(NanoFakturEBDExceptionType t, const char *fmt, ...);
NanoFakturEBDException(NanoFakturEBDExceptionType t)
: t_(t)
{ str_[0] = 0; }
NanoFakturEBDException()
: t_(EBDUnknownError)
{ str_[0] = 0; }
NanoFakturEBDException(NanoFakturEBDExceptionType t, const char *fmt, va_list ap);
NanoFakturEBDExceptionType getType()
const { return t_; }
virtual const char *what()
const throw() {return str_ ;}
protected:
char str_[EXCEPTION_STR_LEN_MAX];
NanoFakturEBDExceptionType t_;
class NanoFakturEBDAxis : public asynMotorAxis
public:
NanoFakturEBDAxis(class NanoFakturEBDController *cnt_p, int axis, int channel);
asynStatus poll(bool *moving_p);
asynStatus move(double position, int relative, double min_vel, double max_vel, double accel);
asynStatus moveVelocity(double min_vel, double max_vel, double accel);
asynStatus stop(double acceleration);
bool getClosedLoop();
bool hasEncoder();
asynStatus getUint(uint16_t cmdId, uint32_t *val_out);
asynStatus getInt(uint16_t cmdId, int32_t *val_out);
asynStatus getFloat(uint16_t cmdId, float *val_out);
asynStatus setUint(uint16_t cmdId, uint32_t val);
asynStatus setInt(uint16_t cmdId, int32_t val);
asynStatus setFloat(uint16_t cmdId, float val);
asynStatus setNone(uint16_t cmdId);
private:
NanoFakturEBDController *c_p_; // pointer to asynMotorController to which this axis belong
int channel_; // channel number used in commandsto controller; 0, 1, 2...
asynStatus comStatus_; // the last status of asyn communications
friend class NanoFakturEBDController;
class NanoFakturEBDController : public asynMotorController
public:
NanoFakturEBDController(const char *portName, const char *IOPortName, int numAxes, double movingPollPeriod, double idlePollPeriod);
asynStatus cmdRsp(uint16_t cmdId, int32_t isReadCmd, size_t params_count, const uint8_t *fmts, const ParamVal *vals, size_t *params_count_out, uint8_t *fmts_out, ParamVal *vals_out);
asynStatus getVal(uint16_t cmdId, uint8_t fmt0, const void *val0, void *val_out);
asynStatus setVal(uint16_t cmdId, uint8_t fmt0, const void *val0, uint8_t fmt1, const void *val1);
protected:
NanoFakturEBDAxis **pAxes_; // pointer to array of axis pointer
private:
asynUser *asynUserMot_p_; // for asyn communications
friend class NanoFakturEBDAxis;
#endif // __cplusplus
#endif // NANOFAKTUR_EBD_DRIVER_H
| ANJ, 19 Mar 2026 |
Home
News
About
Talk
Base
Modules
Extensions