1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  <2026>  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  <2026>
Subject: Re: Support for piezo controller nanoFAKTUR EBD-060310
From: Torsten Bögershausen via Tech-talk <tech-talk at aps.anl.gov>
To: LiangChih Chiang <yehnan174 at gmail.com>
Cc: "tech-talk at aps.anl.gov" <tech-talk at aps.anl.gov>
Date: Fri, 6 Feb 2026 17:08:52 +0100
Hej again,
Why are the RMP and REP fields integer ?
The "real world encoders" typically count in integer,
and so far the int32 had been enough.
Even if we today have encoders with more bits,
these are typically attached to the motor controller
and handled there.
The RMP field counts steps.
It was designed for a stepper motor, and even here
32 bit where both enough
(and that is what we have before int64 became available)
The motorRecord itself uses the step in RMP to prevent
commanding a motion the will end up on the same step.
Moving from 0.050 to 0.051 is prevented, when MRES is 0.05
For a piezo (or other modern controllers) we don't need this
step-size, so that the motorRecord has  got the SPDB field,
Set Point Dead Band.
For the controllers which are in use here, most of them
communicate in EGU.
For that reason I made a patch, where the value
"motorPosition_" from the driver is copied into
the DRBV field without conversion through integers.
The driver needs this patch:
<https://urldefense.us/v3/__https://github.com/EuropeanSpallationSource/m-epics-ethercatmc/blob/master/ethercatmcApp/src/ethercatmcIndexerAxis.cpp*L81..*L83__;IyM!!G_uCfscf7eWS!Y7WX8-mvQ1jbmRMFbDnfNF_DTCQsfKdZL_8fQ1f2Et8_Y6fykZdcJ8MPKwhFh88rcl7GnP_akIT_j0qHjrs$ >
The motor package itself is here:
<https://urldefense.us/v3/__https://github.com/EuropeanSpallationSource/motor/releases/tag/v7.2.8.1-ESS__;!!G_uCfscf7eWS!Y7WX8-mvQ1jbmRMFbDnfNF_DTCQsfKdZL_8fQ1f2Et8_Y6fykZdcJ8MPKwhFh88rcl7GnP_akIT_Feyulpc$ >
BR
/Torsten
On 2026-02-06 14:20, LiangChih Chiang wrote:
Hi, Torsten, thanks for replying.
 >Using epicsPrintf (or even printf) should be forbidden in
 >these kind of driver code.
ok. I'll fix it.
 >>1.
 > pC_->motorPosition_ is an int, used as an index
 > motorPosition is a double
You're right. My mistake.
Another question follows:
"cainfo <motor_record>.REP and .RMP" will get DBF_LONG.
Why aren't they DBF_DOUBLE?
 >>3.
 >>The values of position and voltage from the controller are float values.
>>When setting, say 2.123456, to motorEncoderPosition, it will become 2 (which is an int).
 >This is depending on MRES in the motorRecord.
 >If you set it to 1.0 (or not at all, the the fallback is 1.0)
 >all values are rounded into integer.
 >The trick is to set MRES to 0.000001 or so and compensate
 >this in the driver (multipy with 1000000)
Yes. You're right.
I'll try.
 >For the open-loop-voltage:
 >You probably want an own asyn-parameter for this.
I'll consider it.
However, the chance of this piezo controller in open-loop mode is extremely slim.
How to support two modes(closed-loop and open-loop) in Model 3 driver?
In closed-loop mode, VAL and RBV mean position(unit um)?
In open-loop mode, VAL and RBV mean voltage?
On Fri, Feb 6, 2026 at 5:51 PM Torsten Bögershausen <tboegi at edom.se <mailto:tboegi at edom.se>> wrote:
    Hej LiangChih Chiang,
    thanks for asking.
    Before going into your questions, please allow one comment:
    Please consider to us asynPrint instead.
    Especially things like
    #ifdef DEBUG
                printf("Warning: un-handled param data format:
    #endif
    Could be better coded as
        asynPrint(this->pasynUserSelf, ASYN_TRACE_ERROR,
            "%s: Warning....\n",
            __FUNCTION__);
    (If you write Warning or Err: or something is more a matter of taste)
    But in any way you want to know if things go bad much later,
    after firmware updates, changes in the IOC, glitches here and the )
    Having said that, finishing my review, which may read unintentionally
    hard, lets digg into the questions.
       1.
      > In asynMotorController.h, the data type of motorPosition_
      > and motorEncoderPosition_ are ints.
    A call inside the axis class looks like this:
    asynMotorAxis::setDoubleParam(pC_->motorPosition_, motorPosition);
    saying which asynparameter we ar writing to.
    motorPosition is a double, saying where the motor should be,
    according to the controller.
    motorEncoderPosition_ is the value coming from the sensor inside the
    controller.
    Example:
    the MCS2 from Smaract reads motorPosition like this:
       // Read the target position
        snprintf(pC_->outString_,sizeof(pC_->outString_)-1,
          ":CHAN%d:POS:TARG?", axisNo_);
    And encoderPosition like this:
           // read the actual position as measured by the sensor
            ":CHAN%d:POS?", axisNo_);
    3.
      > The values of position and voltage from the controller are float
    values.
      > When setting, say 2.1234...
    /BR Torsten
    On 2026-02-06 08:48, LiangChih Chiang via Tech-talk wrote:
     > Hello, EPICS mates,
     > I started to implement the “Model 3” driver for nanoFaktur
    EBD-060310
     > piezo controller.
     > The attached files(.cpp and .h) are the work-in-progress source
    code.
     > Not finished yet.
     > I have some questions.
     > 1.
     > But in derived class of asynMotorcontroller(like
     > smarActMCSMotorDriver.cpp and ACRMotorDriver.cpp),
     > the function setDoubleParam is used to set the above parameters.
     > Why is that?
     > 2.
     > I can read the position(unit um, range 0 to 40) and voltage(unit
    volts,
     > range -30 to 130) from the controller.
     > But which one should I set to motorPosition_and
    motorEncoderPosition_?
     > I don't quite understand.
     > 3.
    values.
    become 2
     > (which is an int).
     > How to handle this situation?
     > Should I do some kind of transformation? For example, multiply by
    1000,000?
     > 4.
     > In the member function: asynStatus poll(bool* moving_p),
     > I need to set the moving/done status of the stage to moving_p
     > and motorStatusDone_.
     > But there is no such exact suitable command provided by thhe
    controller.
     > A possible candidate is "get on-target status" meaning in closed-
    loop
     > mode(servo ON),
     > whether the position(from sensor) approached the set target or not.
     > 5.
     > The controller has two modes:
     > closed-loop mode(servo ON), users set the desired potion(unit um).
     > open-loop mode(servo OFF), uses set the voltage(unit volts).
     > What should I set to motorPosition_?
     > I think it should be something like "motor pulse".
     > what should I set to motorEncoderPosition_.?
     > I think it should be something like "encoder value".
     > ps
     > The controller uses binary communication protocol.
     > The following example is to read the position(in um) of channel 0:
     > hexadecimal bytes in little-endian:
     > 10 00 01 20 02 00 20 00 00 ac 01 00 00 00 00 fe
     > 10 00: total length, 16 bytes
     > 01 20: command ID, 0x2001 means "get position"
     > 02 00: custom ID, used to distinguish different client programs.
     > 20: option, 0x20 means "read"
     > 00: sequence number, Used in very long responses. Not used in
    commands.
     > 00: interface id, RS-232 or USB or Ethernet. Not used in commands.
     > ac: header checksum
     > 01: data format, 01 means 32-bit unsigned int
     > 00 00 00 00: data, channel 0
     > fe: checksum
     > The  response:
     > 13 00 01 20 02 00 10 00 01 b8 00 00 02 70 74 6a 3e
     > 13 00: total length, 19 bytes
     > 10: option, 0x10 means "final, no more".
     > 01: interface id, 0x01 means RS-232.
     > b8: header checksum
     > 00: data format, 00 means 8-bit unsigned int
     > 00: data, channel 0
     > 02: data format, 02 means float
     > 70 74 6a 3e: data, 0.228960 (position in um)
     > 3e: checksum
     > Any suggestions and responses are appreciated.
     > Thank you.
     > On Thu, Apr 24, 2025 at 5:31 AM Mark Rivers
    <rivers at cars.uchicago.edu <mailto:rivers at cars.uchicago.edu>
    <mailto:rivers at cars.uchicago.edu>>> wrote:
     >       * I think I would need to write the EPICS motor driver
    module for
     >         it.____
     >     __ __
     >     That is correct.  You should write a “Model 3” driver,
    meaning it is
     >     a C++ driver derived from the base classes
    asynMotorController and
     >     asynMotorAxis.____
     >     __ __
>     I just looked at the manual for the nanoFAKTUR EBD-060310. It uses
     >     a non-standard binary communications protocol, not ASCII
    strings.
     >     That is unusual, most controllers use ASCII communication.____
     >     __ __
>     The driver you suggested as a model, https://urldefense.us/v3/__https://github.com/__;!!G_uCfscf7eWS!Y7WX8-mvQ1jbmRMFbDnfNF_DTCQsfKdZL_8fQ1f2Et8_Y6fykZdcJ8MPKwhFh88rcl7GnP_akIT_PQlaFes$ epics-motor/ <https://urldefense.us/v3/__https://github.com/epics-motor/__;!!G_uCfscf7eWS!Y7WX8-mvQ1jbmRMFbDnfNF_DTCQsfKdZL_8fQ1f2Et8_Y6fykZdcJ8MPKwhFh88rcl7GnP_akIT_j8jA-bI$ >
     >     motorPIGCS2 <https://urldefense.us/v3/__https:/github.com/
    epics- <https://urldefense.us/v3/__https:/github.com/epics->
     >     motor/motorPIGCS2__;!!G_uCfscf7eWS!
>  YgABnMrr4ouWf_GcXAuVe7LU-96lfvWFNG96utdBA3mgcrk9dBsWVY7JQtxclFMQQYwD2Zz0RmrbQGad8OJXFPc$>  is fairly complex because of the class hierarchy, so you might want to start with something simpler as your example. ____
     >     __ __
> https://urldefense.us/v3/__https://github.com/epics-motor/motorSmarAct/blob/master/__;!!G_uCfscf7eWS!Y7WX8-mvQ1jbmRMFbDnfNF_DTCQsfKdZL_8fQ1f2Et8_Y6fykZdcJ8MPKwhFh88rcl7GnP_akIT_zq3ZIW8$ smarActApp/ <https://urldefense.us/v3/__https://github.com/epics-motor/motorSmarAct/blob/__;!!G_uCfscf7eWS!Y7WX8-mvQ1jbmRMFbDnfNF_DTCQsfKdZL_8fQ1f2Et8_Y6fykZdcJ8MPKwhFh88rcl7GnP_akIT_1LYwiQ8$ master/smarActApp/>
     >     src/smarActMCSMotorDriver.cpp <https://urldefense.us/v3/
    __https:// <https://urldefense.us/v3/__https://>
     > github.com/epics-motor/motorSmarAct/blob/master/smarActApp/src/
    <https://urldefense.us/v3/__http://github.com/epics-motor/motorSmarAct/blob/master/smarActApp/src/__;!!G_uCfscf7eWS!Y7WX8-mvQ1jbmRMFbDnfNF_DTCQsfKdZL_8fQ1f2Et8_Y6fykZdcJ8MPKwhFh88rcl7GnP_akIT_TyhCqIo$ >
     >     smarActMCSMotorDriver.cpp__;!!G_uCfscf7eWS!YLctRUSDiyz4K-
>  t8_BzT33ew7q6EOnMR2oSaoEqf7fY5hpd5mII4cyq4pP6Gt3vwMPp1s38VSS7kXyY4shD2qrU$>____
     >     __ __
     >     That uses ASCII communication, but it should not be too hard
    to take
     >     the concepts and use binary communication.____
     >     __ __
     >     Mark____
     >     __ __
     >     __ __
     >     __ __
     >     __ __
     >     __ __
     >     *From:*Tech-talk <tech-talk-bounces at aps.anl.gov <mailto:tech-
    talk-bounces at aps.anl.gov> <mailto:tech-talk- <mailto:tech-talk->
     > bounces at aps.anl.gov <mailto:bounces at aps.anl.gov>>> *On Behalf Of
    *LiangChih Chiang via Tech-talk
     >     *Sent:* Wednesday, April 23, 2025 1:41 AM
     >     *To:* tech-talk at aps.anl.gov <mailto:tech-talk at aps.anl.gov>
    <mailto:tech-talk at aps.anl.gov <mailto:tech-talk at aps.anl.gov>>
     >     *Subject:* Support for piezo controller nanoFAKTUR EBD-060310____
     >     __ __
     >     Hello, EPICS mates,____
     >     __ __
     >     I need to control a piezo sage with the controller nanoFAKTUR
     >     EBD-060310.____
     >     This is my first time using this controller.____
     >     I searched and couldn't find the EPICS support module for it.____
     >     __ __
     >     I think I would need to write the EPICS motor driver module
    for it.____
     >     __ __
     >     What module code would you recommend me to use as a starter
     >     reference?____
     >     For example, something like ____
     >     EPICS motor drivers for Physik Instrumente GCS2 (General Command
     >     Set) compatible controllers____
> https://urldefense.us/v3/__https://github.com/epics-motor/motorPIGCS2__;!!G_uCfscf7eWS!Y7WX8-mvQ1jbmRMFbDnfNF_DTCQsfKdZL_8fQ1f2Et8_Y6fykZdcJ8MPKwhFh88rcl7GnP_akIT_K2tNr-s$ <https://urldefense.us/v3/__https://github.com/__;!!G_uCfscf7eWS!Y7WX8-mvQ1jbmRMFbDnfNF_DTCQsfKdZL_8fQ1f2Et8_Y6fykZdcJ8MPKwhFh88rcl7GnP_akIT_PQlaFes$ epics-motor/motorPIGCS2> <https://urldefense.us/ <https://
    urldefense.us/>
>     v3/__https://urldefense.us/v3/__https://github.com/epics-motor/motorPIGCS2__;!!__;!!G_uCfscf7eWS!Y7WX8-mvQ1jbmRMFbDnfNF_DTCQsfKdZL_8fQ1f2Et8_Y6fykZdcJ8MPKwhFh88rcl7GnP_akIT_5upGZ5U$ G_uCfscf7eWS <https://urldefense.us/v3/__http://github.com/epics-motor/motorPIGCS2__;!!__;!!G_uCfscf7eWS!Y7WX8-mvQ1jbmRMFbDnfNF_DTCQsfKdZL_8fQ1f2Et8_Y6fykZdcJ8MPKwhFh88rcl7GnP_akIT_S8bsz0w$ G_uCfscf7eWS>! >  YgABnMrr4ouWf_GcXAuVe7LU-96lfvWFNG96utdBA3mgcrk9dBsWVY7JQtxclFMQQYwD2Zz0RmrbQGad8OJXFPc$> ____
     >     __ __
     >     __ __
Re: Support for piezo controller nanoFAKTUR EBD-060310 LiangChih Chiang via Tech-talk
Re: Support for piezo controller nanoFAKTUR EBD-060310 Torsten Bögershausen via Tech-talk
Prev: control room operations accounts Paul Sichta via Tech-talk
Next: Re: Record TIME field taken from another record's VAL Torsten Bögershausen via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  <2026>
Prev: Re: Support for piezo controller nanoFAKTUR EBD-060310 LiangChih Chiang via Tech-talk
Next: Re: Support for piezo controller nanoFAKTUR EBD-060310 LiangChih Chiang via Tech-talk