Subject: RE: Modbus alarms question
To: 'John Dobbins' <[email protected]>
Date: Thu, 16 Jul 2020 14:36:08 +0000
Ø  I would suggest now adding this to your startup script after creating the MISC port.
asynSetOption(“MISC”, 0, “disconnectOnReadTimeout”, “Y)
> That's better. Thanks.
initial state:
MSD_S1F_FLD_CR                 2020-07-16 09:36:52.285315  STATE MAJOR
I unplug the cable:
MSD_S1F_FLD_CR                 2020-07-16 09:37:25.876095  TIMEOUT INVALID
MSD_S1F_FLD_CR                 2020-07-16 09:37:26.376358  READ INVALID
OK, good.  There is still something I am not completely happy with.  Note that first you get a TIMEOUT alarm, which is correct.  But once the port disconnects you get a READ alarm which is not really correct.  The asynStatus should be asynDisconnected which maps to COMM alarm.  That would be more meaningful.  I think this patch will fix the problem.
(sphinx) corvette:asyn/asyn/asynDriver>git diff .
diff --git a/asyn/asynDriver/asynManager.c b/asyn/asynDriver/asynManager.c
index deefbe7..911e14e 100644
--- a/asyn/asynDriver/asynManager.c
+++ b/asyn/asynDriver/asynManager.c
@@ -1829,7 +1829,7 @@ static asynStatus queueLockPort(asynUser *pasynUser)
                 pasynUserCopy->errorMessage);
             epicsMutexUnlock(plockPortPvt->queueLockPortMutex);
             pasynManager->freeAsynUser(pasynUserCopy);
-            return asynError;
+            return status;
         /* Wait for event from the port thread in the queueLockPortCallback function */
         asynPrint(pasynUser,ASYN_TRACE_FLOW, "%s asynManager::queueLockPort waiting for event\n", pport->portName);
@@ -1840,7 +1840,7 @@ static asynStatus queueLockPort(asynUser *pasynUser)
                 "asynManager::queueLockPort queueRequest timed out");
-            return asynError;
+            return asynTimeout;
         asynPrint(pasynUser,ASYN_TRACE_FLOW, "%s asynManager::queueLockPort got event from callback\n", pport->portName);
You have already applied the second change in this patch.  Could you also try the first change and see if that changes the final alarm to COMM alarm?
Sent: Thursday, July 16, 2020 8:46 AM
Subject: Re: Modbus alarms question
Mark,
initial state:
I unplug the cable:
2+ minutes late I plug the cable back in and it recovers promptly
MSD_S1F_FLD_CR                 2020-07-16 09:40:02.911512  STATE MAJOR
John
Sent: Thursday, July 16, 2020 9:19 AM
To: John Dobbins <[email protected]>
I think you are seeing is due to Linux taking a really long time to realize that the device is disconnected and closing the socket.  I think that eventually it would reconnect, but it can take hours.  Windows is better with this.
I am very interested to know what you see when you do that.
Sent: Thursday, July 16, 2020 8:10 AM
To: Mark Rivers
Mark,
That fixed my problem. Thanks!
My test involves disconnecting the network cable from the PC hosting the simulated PLC.  When I unplug the cable I now get a single transition to "TIMEOUT INVALID".  When I plug the cable back in things return to normal.
In doing this testing I did notice something else I wanted to ask about. If the time the cable is unplugged is > ~ 2 minutes, the connection between the IOC and the simulated PLC is not restored when I plug the cable back in (though it is for shorter outages). The record remains in the "TIMEOUT INVALID" state.  Is this what you would expect?
John
Re: Modbus alarms question John Dobbins via Tech-talk
Re: Modbus alarms question Mark Rivers via Tech-talk
RE: Modbus alarms question Mark Rivers via Tech-talk
Prev: Re: Stream device - general concept how to use Ralph Lange via Tech-talk
Next: Re: Modbus alarms question John Dobbins via Tech-talk
Prev: RE: Modbus alarms question Mark Rivers via Tech-talk