Subject: Re: Modbus alarms question
From: John Dobbins via Tech-talk <[email protected]>
Date: Thu, 16 Jul 2020 15:26:38 +0000
Mark,
The sequence is now  TIMEOUT INVALID followed shortly thereafter  by COMM INVALID.
John
Sent: Thursday, July 16, 2020 10:36 AM
To: John Dobbins <[email protected]>
Cc: [email protected] <[email protected]>
Subject: RE: Modbus alarms question
Ø  I would suggest now adding this to your startup script after creating the MISC port.
asynSetOption(“MISC”, 0, “disconnectOnReadTimeout”, “Y)
> That's better. Thanks.
initial state:
MSD_S1F_FLD_CR                 2020-07-16 09:36:52.285315  STATE MAJOR
I unplug the cable:
MSD_S1F_FLD_CR                 2020-07-16 09:37:25.876095  TIMEOUT INVALID
MSD_S1F_FLD_CR                 2020-07-16 09:37:26.376358  READ INVALID
OK, good.  There is still something I am not completely happy with.  Note that first you get a TIMEOUT alarm, which is correct.  But once the port disconnects you get a READ alarm which is not really correct.  The asynStatus should be asynDisconnected which maps to COMM alarm.  That would be more meaningful.  I think this patch will fix the problem.
(sphinx) corvette:asyn/asyn/asynDriver>git diff .
diff --git a/asyn/asynDriver/asynManager.c b/asyn/asynDriver/asynManager.c
index deefbe7..911e14e 100644
--- a/asyn/asynDriver/asynManager.c
+++ b/asyn/asynDriver/asynManager.c
@@ -1829,7 +1829,7 @@ static asynStatus queueLockPort(asynUser *pasynUser)
                 pasynUserCopy->errorMessage);
             epicsMutexUnlock(plockPortPvt->queueLockPortMutex);
             pasynManager->freeAsynUser(pasynUserCopy);
-            return asynError;
+            return status;
         /* Wait for event from the port thread in the queueLockPortCallback function */
         asynPrint(pasynUser,ASYN_TRACE_FLOW, "%s asynManager::queueLockPort waiting for event\n", pport->portName);
@@ -1840,7 +1840,7 @@ static asynStatus queueLockPort(asynUser *pasynUser)
                 "asynManager::queueLockPort queueRequest timed out");
-            return asynError;
+            return asynTimeout;
         asynPrint(pasynUser,ASYN_TRACE_FLOW, "%s asynManager::queueLockPort got event from callback\n", pport->portName);
You have already applied the second change in this patch.  Could you also try the first change and see if that changes the final alarm to COMM alarm?
Sent: Thursday, July 16, 2020 8:46 AM
Mark,
initial state:
I unplug the cable:
2+ minutes late I plug the cable back in and it recovers promptly
MSD_S1F_FLD_CR                 2020-07-16 09:40:02.911512  STATE MAJOR
John
Sent: Thursday, July 16, 2020 9:19 AM
I think you are seeing is due to Linux taking a really long time to realize that the device is disconnected and closing the socket.  I think that eventually it would reconnect, but it can take hours.  Windows is better with this.
I am very interested to know what you see when you do that.
Sent: Thursday, July 16, 2020 8:10 AM
To: Mark Rivers
Mark,
That fixed my problem. Thanks!
My test involves disconnecting the network cable from the PC hosting the simulated PLC.  When I unplug the cable I now get a single transition to "TIMEOUT INVALID".  When I plug the cable back in things return to normal.
In doing this testing I did notice something else I wanted to ask about. If the time the cable is unplugged is > ~ 2 minutes, the connection between the IOC and the simulated PLC is not restored when I plug the cable back in (though it is for shorter outages). The record remains in the "TIMEOUT INVALID" state.  Is this what you would expect?
John
Modbus alarms question John Dobbins via Tech-talk
Re: Modbus alarms question Mark Rivers via Tech-talk
Re: Modbus alarms question John Dobbins via Tech-talk
RE: Modbus alarms question Mark Rivers via Tech-talk
Prev: RE: Modbus alarms question Mark Rivers via Tech-talk
Next: Re: Stream device - general concept how to use Christian Pauly via Tech-talk
Next: Announcing aioca: Python asyncio Channel Access client using libca via ctypes Cobb, Tom (DLSLtd,RAL,LSCI) via Tech-talk