Hi Andy,
I feel like there is a better way than me trying to use a calcout record and check if any record has its STAT field set to COMM. Like, is it possible to monitor for connection status without needing to process a record whose device type is StreamDevice and
check its STAT field?
Yes,
there is a better way.
First,
you probably want to use this line in your startup script:
asynSetOption("$(PORT)",0,
"disconnectOnReadTimeout", "Y")
That
will cause the port to disconnect if there is a timeout. If you don't do that then the asyn won't know that the port is disconnected for a very long time on Linux, it will just keep giving "temporarily unavailable" messages.
In your startup script load an asyn record that is connected to that asyn port. Here is an example:
dbLoadRecords("$(ASYN)/db/asynRecord.db", "P=IOC:, R=asyn1, PORT=ARIES1, ADDR=0, OMAX=256, IMAX=256")
You
can monitor the IOC:asyn1.CNCT field, which will either be "Connect" or "Disconnect".
From: Tech-talk <tech-talk-bounces at aps.anl.gov> on behalf of Wang, Andrew via Tech-talk <tech-talk at aps.anl.gov>
Sent: Thursday, December 8, 2022 8:21 PM
To: EPICS tech-talk <tech-talk at aps.anl.gov>
Subject: Ways to know if instrument connected via TCP/IP through StreamDevice has lost connection
Hi all,
Basically, I was wondering if there is a better way to know if communication to an instrument has
been lost. I understand that this can be done either by simplying looking at the IOC shell for disconnection errors or checking if the STAT field is set to COMM.
I was wondering if there is another method of determining if the instrument is still connected or not besides the two methods described above. Additionally, I would like to have a record called "is_instrument_connected", that holds a value like 1 to indicate
the instrument is connected and a 0 if it is not. I feel like there is a better way than me trying to use a calcout record and check if any record has its STAT field set to COMM. Like, is it possible to monitor for connection status without needing to process
a record whose device type is StreamDevice and check its STAT field?
Thank you,
Andy