1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  <20232024  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  <20232024
Subject: Re: Help getting modbus module started
From: Mark Rivers via Tech-talk <tech-talk at aps.anl.gov>
To: "tech-talk at aps.anl.gov" <tech-talk at aps.anl.gov>, Christian Pauly <pauly at physik.uni-wuppertal.de>
Date: Wed, 15 Feb 2023 13:24:06 +0000
Hi Christian,
> But how do i have to define the ai(?)-record in FUrecords.db now, to read a single word from the given address 0x2103 using the IN_int function as defined above ?
You are using absolute Modbus addressing because you set the modbusStartAddress argument to drvModbusAsynConfigure to -1.   That means that the "offset" parameter in the record INP link field is the absolute Modbus address, 0x2103 in your case.  That is explained here: https://epics-modules.github.io/modbus/#epics-device-support
The record definition depends on what you want to do with the value in that register.  Perhaps the simplest is just to read it into a longin record.
# longin record template for register inputs
record(longin,"$(P)$(R)") {
    field(DTYP,"asynUInt32Digital")
    field(INP,"@asynMask($(PORT) $(OFFSET) 0xFFFF)")
    field(SCAN,"$(SCAN)")
You could load this as follows, for example:
dbLoadRecords("$(MODBUS)/db/longin.template", "P=IOC:, R=longin1, PORT=IN_int, OFFSET=0x2103, SCAN=1 second")
Note that because you are using absolute addressing the driver will not periodically poll, and you therefore cannot use SCAN=I/O Intr, you need to use a periodic scan rate, or Passive and arrange to processes the record some other way.
If the register contains an integer value that you want to convert to a double in engineering units then you could use an ai record with LINEAR conversion like this example:
# ai record template for register inputs
record(ai, "$(P)$(R)") {
    field(DTYP,"asynInt32")
    field(INP,"@asynMask($(PORT) $(OFFSET) $(BITS))MODBUS_DATA")
    field(LINR,"LINEAR")
    field(EGUL,"$(EGUL)")
    field(EGUF,"$(EGUF)")
    field(HOPR,"$(EGUF)")
    field(LOPR,"$(EGUL)")
    field(PREC,"$(PREC)")
The meaning of the BITS argument in the INP field is explained here: https://epics-modules.github.io/modbus/#asynint32.  If your A/D was 12-bit unipolar you would set BITS=12.  The EGU* fields set the values of the engineering units for the minimum and maximum values of the A/D, e.g. 0 and 4095 for a 12-bit A/D.  PREC is the number of digits you want EPICS to display, and the other fields are as above.
From: Tech-talk <tech-talk-bounces at aps.anl.gov> on behalf of Christian Pauly via Tech-talk <tech-talk at aps.anl.gov>
Sent: Tuesday, February 14, 2023 6:56 PM
To: tech-talk at aps.anl.gov <tech-talk at aps.anl.gov>
Great, thanks for the quick help !
Now it works, the ioc starts and is running.
But now i am stuck with defining a record using the modbus interface.
As a simpe start, I would like to read a single word (int16) from a
given address 0x2103 of master device with id=1, using modbus read
function type 3.
the relevant part of my st.cmd at the moment looks like this:
drvAsynSerialPortConfigure("RS485", "/dev/ttyUSB0", 0, 0, 0)
asynSetOption("RS485",0,"baud","9600")
asynSetOption("RS485",0,"parity","none")
asynSetOption("RS485",0,"bits","7")
asynSetOption("RS485",0,"stop","2")
asynOctetSetOutputEos("RS485",0,"\r\n")
asynOctetSetInputEos("RS485",0,"\r\n")
modbusInterposeConfig("RS485",2,1000,5)
drvModbusAsynConfigure(IN_int,"RS485",1,3,-1,1,UINT16,1000,0)
asynSetTraceIOMask("RS485",0,4)
## Load record instances
dbLoadTemplate "FUrecords.db"
without using template- and substitution files like in all examples i
found so far ?? (for sure that is the more clever way, but before i try
to understand that part i would like to have a running example first)
Thanks again for any help !
Christian
On 2/14/23 20:23, Pierrick M Hanlet via Tech-talk wrote:
> I almost forgot, you'll also need to add modbus to your
> $TOP/configure/RELEASE file (assuming that you have the modbus module).
> This may not be precisely worded, but when adding a module, you need to
> define its path in $TOP/configure/RELEASE and then
> add the modules (lib / dbd) to the $TOP/xxxApp/src/Makefile.
> Cheers,
> Pierrick
> On 2/14/23 13:02, Pierrick M Hanlet via Tech-talk wrote:
>> Hi Christian,
>> You will also need to add some things to your xxxApp/src/Makefile:
>> - xxx_DBD+=modbusSupport.dbd
>> - xxx_DBD+=drvAsynSerialPort.dbd
>> - xxx_LIBS+=modbus
>> I think that this should do it for you.
>> Good luck,
>> Pierrick
>> On 2/14/23 11:38, Christian Pauly via Tech-talk wrote:
>>> Hi folks
>>> I am trying hard to set up a Raspberry running an EPICS IOC for a
>>> Delta VFD motor driver / frequency inverter. The device is controlled
>>> via modbus, using a large set of individual 16bit integer read/write
>>> registers for configuration, and few more registers for control.
>>> At the moment it is configured to talk Modbus ASCII via RS485, and
>>> with a simple Python program using minimalmodbus-lib i can talk to the
>>> controller.
>>> Now i started with a fresh EPICS 3.15.7 base, (in ~/EPICS/base) and
>>> installed ASYN-R4-43 (~/EPICS/modules/asyn-R4-43) and modbus
>>> (~/EPICS/modules/modbus_R3-2).
>>> I initiated a new application ~/EPICS/projects/FUcontrol,
>>> ran "makeBaseApp.pl -t example FUcontrol", "makeBaseApp.pl -i -t
>>> example FUcontrol" - and thats basically it.
>>> And now i am stuck how to include modbus (includes / libs / dbd files)
>>> into my exampleApp.
>>> I kind of managed to include ASYN already by adding
>>>     ASYN=... to the RELEASE file
>>> and to the Makefile:
>>>     FUcontrol_LIBS += asyn
>>> In my ioc startup st.cmd i can run the commands
>>> to configure the interface.
>>> But if i add
>>> modbusInterposeConfig("RS485",2,1000,0)
>>> i get an error on startup claiming that modnusinterposeconfig can not
>>> be found.
>>> So:
>>> Is there any simple step-by-step instructions how to add modbus to an
>>> existing ioc application ?
>>> I could not find anything "simple" in the documentation. I saw the
>>> examples which come with modbus, but all these already look quite
>>> complicated to me...
>>> Or any good advise on how to continue from here ?
>>> Thanks for any help !
>>> Christian
Help getting modbus module started Christian Pauly via Tech-talk
Re: Help getting modbus module started Pierrick M Hanlet via Tech-talk
Re: Help getting modbus module started Christian Pauly via Tech-talk
Prev: Re: Help getting modbus module started Christian Pauly via Tech-talk
Next: Cpp code not recognizing asyn parameter Marco A. Barra Montevechi Filho via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  <20232024
Next: RE: Help getting modbus module started Mark Rivers via Tech-talk
ANJ, 15 Feb 2023 Valid HTML 4.01! · Home · News · About · Base · Modules · Extensions · Distributions · Download ·