Hi, dear Mark, thanks for replying.
>The Modbus ports are being created with a
length of 3+2 (5) and 3+1 (4) registers respectively. >The records are
reading single registers at offsets of 0,
1, and 2. >That should not generate the error you see.
I see. There should be somewhere records access beyond the max length of registers.
And I found the following record access address 4.
record(ai, "$(P)$(Q):WSP:RBV") { field(DESC, "Working SP Readback") field(DTYP, "asynInt32") field(INP, "@asyn(Eurotherm_$(PORT)_$(ADDR)_$(LOOP=1)_Rd_PV,4,1000)MODBUS_DATA") field(EGU, "$(EGUT=C)") field(SCAN, "I/O Intr") field(ASLO, "0.1") field(PREC, "1") }
Thank you again. It's probably I or my colleague modified the code and forgot.
I don’t understand why you are getting that error. The Modbus ports are being created with a length of 3+2 (5) and 3+1 (4) registers respectively. The records are reading single registers at offsets of 0,
1, and 2. That should not generate the error you see.
Please send the output of:
asynReport 2
That will show information about all the asyn port drivers and may provide a clue.
On Behalf Of LiangChih Chiang via Tech-talk
Sent: Wednesday, November 6, 2024 7:57 PM
To: [email protected]
Subject: Error "drvModbusAsyn::readPoller ... invalud memory request 3, max=3" of module Eurotherm2k
to access controller Eurothermm 3508.
It's ok mostly, but I can't set the P/I/D values.
And there are two errors showed repeatedly:
2024/11/07 09:07:35.155 drvModbusAsyn::readPoller port Eurotherm_E3K01_1_1_Rd_PID invalid memory request 3, max=3
2024/11/07 09:07:35.852 drvModbusAsyn::readPoller port Eurotherm_E3K01_1_1_Rd_PV invalid memory request 4, max=3
"E3K01" is the port name,
the following "1" is the Modbus address,
then "1" is the loop number.
I found that in the file eurothermModbus.c of the module, it calls drvMosbusAsynConfigure:
/* Create modbus channels for the PV, target setpoint and manual output */
mkname(str, strmaxlen, asynPortName, modbusAddress, loopNumber, 0, "PV");
asynRet = drvModbusAsynConfigure(str, asynPortName, modbusAddress,
MODBUS_READW, loopStart+PV_OFFSET, 3+2,
0, EUROTHERM_POLL_MS, "");
if (asynRet != asynSuccess) {
LOG_ERROR("drvModbusAsynConfigure failed with error %d", asynRet);
free(str);
return -EIO;
/* Create modbus channels for the PID parameters */
mkname(str, strmaxlen, asynPortName, modbusAddress, loopNumber, 0, "PID");
MODBUS_READW, loopStart+PID_OFFSET, 3+1,
free(str);
return -EIO;
And in the file eurothermModbusLoop.template, the records uses the ports created above:
# PV: address 1
# % gdatag,pv,ro,$(gda_name=),PVRBV
# % archiver 1 Monitor
record(ai, "$(P)$(Q):PV:RBV") {
field(DESC, "Temperature Readback")
field(INP, "@asyn(Eurotherm_$(PORT)_$(ADDR)_$(LOOP=1)_Rd_PV,0,1000)MODBUS_DATA")
# % gdatag,pv,ro,$(gda_name=),SPRBV
# % archiver 10 Monitor
record(ai, "$(P)$(Q):SP:RBV") {
field(DESC, "Setpoint Readback")
field(INP, "@asyn(Eurotherm_$(PORT)_$(ADDR)_$(LOOP=1)_Rd_PV,1,1000)MODBUS_DATA")
field(ASLO, "0.1")
# % gdatag,pv,ro,$(gda_name=),ORBV
record(ai, "$(P)$(Q):O:RBV") {
field(DESC, "Output Readback")
field(INP, "@asyn(Eurotherm_$(PORT)_$(ADDR)_$(LOOP=1)_Rd_PV,2,1000)MODBUS_DATA")
field(EGU, "%")
field(ASLO, "0.1")
field(PREC, "1")
Would you please provide some suggestions?
- Error "drvModbusAsyn::readPoller ... invalud memory request 3, max=3" of module Eurotherm2k LiangChih Chiang via Tech-talk
- RE: Error "drvModbusAsyn::readPoller ... invalud memory request 3, max=3" of module Eurotherm2k Mark Rivers via Tech-talk
Re: IOClog Dale Cox via Tech-talk
Re: IOClog Saisrikiran Mudigonda via Tech-talk
<2024>
2025
2026
Multiple asyn ports inside asynPortDriver class Abdalla Ahmad via Tech-talk
<2024>
2025
2026