1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  <2026 Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  <2026
Subject: Re: EPICS support for Fastech motors
From: Rea Domitrović via Tech-talk <tech-talk at aps.anl.gov>
To: Torsten Bögershausen <tboegi at edom.se>, Mark Rivers <rivers at cars.uchicago.edu>, "tech-talk at aps.anl.gov" <tech-talk at aps.anl.gov>
Date: Mon, 29 Jun 2026 13:51:02 +0000
Hi Mark and Torsten,
thanks so much for your help debugging. In today's commit on the repo I've rewritten the driver to override the base class method writeReadController and code the number of bytes exchanged directly by the method instead of using strlen. I've also added a method writeReadFrame instead of building the boilerplate string every time. I suspect something is still wrong with the poller as so far only JOGF, JOGR and STOP work semi-reliably, and readback isn't syncing into the motor record, but I should have an easier time debugging from here; I'll come back with more questions if I have them.
As far as Mark's comment on the frame header, the manual in fact contradicts itself - on page 4, section 1-1-4, it says the null byte should go in (zero-indexed) position 2 (after length, before Sync No) and in position 3 (after Sync No, before Frame Type), with the sync counter going in the other one, while in section 1-1-5 both the inline visualisation and the bullet-point list request the null byte in position 3. Testing via StreamDevice has shown that the reserved null byte is in fact in position 3.
Cheers,
Rea
Sent: Monday, June 29, 2026 6:38:04 AM
To: Mark Rivers; Rea Domitrović; tech-talk at aps.anl.gov
Thanks Mark for digging.
While reading your comments and the code,
there is one more thing:
   //write the outstring to controller
   memcpy(&pC_->outString_, buffer, 2+buffer[1]);
   status = pC_->writeReadController();
The method pC_->writeReadController(), without any parameters,
will use a strlen() under the hood to find out how many
bytes are realy send to the controller.
Please have a look at:
writeReadController(const char *output, char *input,
                     size_t maxChars, size_t *nread, double timeout)
For binary data, as in your case,
pasynOctetSyncIO->writeRead() must be used, I think.
Where 2+buffer[1] is the number of bytes to be send.
Probably you can write a wrapper in your code ?
Mark, Rea, any more comments ?
/Torsten
On 2026-06-26 21:18, Mark Rivers via Tech-talk wrote:
> Hi Rea,
> Thanks for sharing that repository, that is very helpful.
> I think I found the correct manual for your controller here:
> https://fastech.co.kr/new/board/bbs/download_product_en.php?
> bo_table=sub010208_en&wr_id=0 <https://urldefense.us/v3/__https://
> bo_table=sub010208_en&wr_id=0__;!!G_uCfscf7eWS!ZG7XUWxxrpQ37e-
> akIDsZDGp4KKtM1ycFzKnNiO_tLUFBMGylb-98MZgDcyWWEOAYj6cH0fKuJACQotBhkNvUPEoY6M$>
> I looked at EzS2PEAxis::move.  I see that it is building a binary
> structure and sending that to the controller with pC_-
>  >writeReadController().
> However, I think I see an error in your code. Everywhere you define
> boiler[] similar to this:
>      unsigned char boiler[] = {HEADER, 8, pC_->syncCounter, 0x00,
> SET_PARAMETER, param};
> https://github.com/redomitro/motorFastech/
> blob/94b93b150501490cf9cf7ef77d4d4e3a6b0ad62f/fastechApp/src/
> EzS2PE_Driver.cpp#L146 <https://urldefense.us/v3/__https://github.com/
> redomitro/motorFastech/blob/94b93b150501490cf9cf7ef77d4d4e3a6b0ad62f/
> fastechApp/src/EzS2PE_Driver.cpp*L146__;Iw!!G_uCfscf7eWS!ZG7XUWxxrpQ37e-
> akIDsZDGp4KKtM1ycFzKnNiO_tLUFBMGylb-98MZgDcyWWEOAYj6cH0fKuJACQotBhkNvT9F0Ouk$>
> However, the manual says the frame header is this:
> ① Header : 0xAA, Displays that the beginning of Frame
> ② Length : Length of Data after Length
>     (Sync No. + Reserved + Frame type + Data)
> ③ Reserved : 1 byte Input as “ 0x00
> ④ Sync No. : The Sync number of the packet is used to c heck whether the
> command is executed
>     in the drive module. The value should change every time when you
> send a new command.
> ⑤ Frame type : Specify the command type of the Frame. The types are
> listed below.
>     Refer to  Frametypeand Data configuration 」
> ⑥ Data : The data structure and length of this clause are determined by
> the Frame type.
>     The detailed structure refers to [Frametypeand Data configuration]
> section below.
> Note that the Reserved 0x00 byte is defined in the manual to come
> between the Length and the Sync Number byte.  But your code has the 0x00
> after the Sync Number.  This seems wrong.
> The communication is UDP based.  Once you fix the error above I suspect
> that write operations will succeed.
> However, I think that read operations will fail because you have created
> the L0 UDP port with the default value of noProcessEos=0.  This means
> that the UDP driver is doing EOS processing.  Although you have not
> defined input or output terminators, another thing that the EOS
> processing does is wait for the requested number of bytes to be
> received.  Since you have no way of knowing how many bytes will be
> received you need to request more than you will receive, and the read
> will time out.
> The solution is to change your startup script to this:
> drvAsynIPPortConfigure("L0", "192.168.0.204:3001 UDP", 0, 0, 1)
> That sets noProcessEos to 1.  That means that the driver will not wait
> for the requested number of characters but will return as soon as any
> characters are received, or after a timeout.
> Cheers,
> Mark
> *From:* Rea Domitrović <rea.domitrovic at irb.hr>
> *Sent:* Friday, June 26, 2026 8:44 AM
> *To:* Mark Rivers <rivers at cars.uchicago.edu>; tech-talk at aps.anl.gov
> *Subject:* Re: EPICS support for Fastech motors
> Hi Mark,
> the source code is here: https://github.com/redomitro/motorFastech
> <https://urldefense.us/v3/__https://github.com/redomitro/
> motorFastech__;!!G_uCfscf7eWS!ZG7XUWxxrpQ37e-
> akIDsZDGp4KKtM1ycFzKnNiO_tLUFBMGylb-98MZgDcyWWEOAYj6cH0fKuJACQotBhkNvZcjRvUo$> - the repository should be public. Thank you again for the help; it's the end of the week here so I'll dig into the debugging more come Monday. Best,
> Rea
> *From:* Mark Rivers <rivers at cars.uchicago.edu>
> *Sent:* Friday, June 26, 2026 3:15:45 PM
> *To:* Rea Domitrović; tech-talk at aps.anl.gov
> Hi Rea,
>     Is it even possible to use the Model 3 framework to communicate with
>     something that uses such a specific and non-standard byte stream, or
>     will I have to find a different way? Kind regards,
> Yes, definitely.  You can use the Model 3 framework to communicate with
> any type of motor controller API: ASCII strings, vendor library calls,
> Modbus, etc.
> The issue is the motorAxis->move() function that you have implemented in
> your derived class.  It is returning the error status -1.  You need to
> figure out why.  Is your code on a repository where we can see it?  If
> not can you share the code, or at least the code for the axis->move()
> function?
> Here are 2 suggestions for debugging this:
>     Enable asynTraceIODriver and ASYN_TRACEIO_ESCAPE for the underlying
>     asyn communication port.  That will let you see the complete
>     communication with the device.  Put these lines in your startup
>     script right after you create the asyn communication port, which I
>     have called $(PORT) here:
> asynSetTraceMask($(PORT), 0, ERROR|DRIVER)
> asynSetTraceIOMask($(PORT), 0, ESCAPE)
>     Put debugging printf or asynPrint statements in your driver to see
>     what is happening.
> Mark
> *Sent:* Friday, June 26, 2026 2:50 AM
> Hi Mark,
> thanks for taking the time. I followed the debug instructions you
> gave here: https://epics.anl.gov/tech-talk/2017/msg00282.php <https://
> epics.anl.gov/tech-talk/2017/msg00282.php> - thanks for clarifying what
> is actually needed.
> I suspect this message is what's wrong, i.e. the writes are not actually
> getting through to the motor:
> 2026/06/26 09:39:45.144 asynMotorController:writeFloat64 error, status=1
> axis=0, function=1, value=-150000.000000
> 2026/06/26 09:39:45.148 devMotorAsyn::asynCallback: EXIT:zpos
> pasyn{Float64,Int32}->write returned
> To me, it smells like the problem is in the fact the motor doesn't use
> ASCII-compatible strings to communicate - every message has to start
> with a five-byte header of the following structure: 0xAA, length,
> idempotence counter, 0x00, frame type. That null byte is presumably
> making communication difficult; that is why everywhere in the source
> code I used memcpy instead of sprintf to build the outString. A test IOC
> made with StreamDevice instead of Motor confirms the motor is responsive
> to that kind of communication; I was able to turn the servo on and poll
> it for position using StreamDevice, but not actually move it.
> Rea
> *Sent:* Thursday, June 25, 2026 4:35:51 PM
> *To:* tech-talk at aps.anl.gov; Rea Domitrović
> H Rea,
> You have set the asynTraceMask to enable lots of debugging.  That is OK,
> but it makes it hard to see the real errors from warning and
> informational messages.  For example these messages are printed with
> ASYN_TRACE_FLOW, they are not really errors.
> 2026/06/25 15:29:48.311 asynPortDriver:getDoubleParam: port=motorExit
> error getting parameter 9 MOTOR_ENCODER_POSITION, in list 0, value undefined
> error getting parameter 5 MOTOR_VELOCITY, in list 0, value undefined
> This message
> 2026/06/25 15:07:46.444 asynMotorController:writeFloat64: Set driver
> motorExit, axis 0 move absolute to 0.000000, base velocity=500.000000,
> velocity=25000.000000, acceleration=245000.000000
> is being printed here.  It is just an informational message.
> https://github.com/epics-modules/motor/blob/
> f3d089bae20d04f8b9ed18fcfdc55274075d6a42/motorApp/MotorSrc/
> asynMotorController.cpp#L328 <https://urldefense.us/v3/__https://
> asynMotorController.cpp*L328__;Iw!!G_uCfscf7eWS!ZG7XUWxxrpQ37e-
> akIDsZDGp4KKtM1ycFzKnNiO_tLUFBMGylb-98MZgDcyWWEOAYj6cH0fKuJACQotBhkNv9k8nZJQ$>
> However, this message:
> 2026/06/25 15:07:46.445 asynMotorController:writeFloat64 error, status=1
> axis=0, function=1, value=0.000000
> is being printed here:
> asynMotorController.cpp#L428 <https://urldefense.us/v3/__https://
> asynMotorController.cpp*L428__;Iw!!G_uCfscf7eWS!ZG7XUWxxrpQ37e-
> akIDsZDGp4KKtM1ycFzKnNiO_tLUFBMGylb-98MZgDcyWWEOAYj6cH0fKuJACQotBhkNvdoyZWuk$>
> Function=1 is a move absolute command, so it is consistent with the
> first message.  status=1 means that your driver's pAxis->move() function
> returned -1.  It was called from here:
> asynMotorController.cpp#L324-L325 <https://urldefense.us/v3/__https://
> asynMotorController.cpp*L324-L325__;Iw!!G_uCfscf7eWS!ZG7XUWxxrpQ37e-
> akIDsZDGp4KKtM1ycFzKnNiO_tLUFBMGylb-98MZgDcyWWEOAYj6cH0fKuJACQotBhkNvASUhELQ$>
> If you set your asynTrace flags to ERROR|WARNING you will only see the
> more important messages.
> Mark
> *From:* Tech-talk <tech-talk-bounces at aps.anl.gov> on behalf of Rea
> *Sent:* Thursday, June 25, 2026 8:53 AM
> *To:* tech-talk at aps.anl.gov <tech-talk at aps.anl.gov>
> Hi all,
> thanks so much for pointing me in the right direction so far. I've got
> to the point where I've got the structure of a driver based on the MCB4B
> driver and with inspiration from the SmarAct driver; however, at
> runtime, I'm getting errors that I'm struggling to diagnose. If someone
> could help me understand, I would be most grateful. Relevant info is
> below. Best,
> Rea Domitrović
> Institut Ruđer Bošković
> Zagreb, Croatia
> Source code is here: https://github.com/redomitro/motorFastech <https://
> urldefense.us/v3/__https://github.com/redomitro/motorFastech__;!!
> G_uCfscf7eWS!
> ckejUTszXgikK0HKxA_InFEgeEyYG2lD41P9WU4hEdAGledQERL0dK2U_KIYaLsarWXmtRkeqsmdlOkbbDFNsrR52DGXQg$>
> IOCinit output:
> 2026/06/25 15:29:48.311 asynPortDriver:drvUserCreate:
> drvInfo=MOTOR_MOVE_REL, index=0
> drvInfo=MOTOR_MOVE_ABS, index=1
> drvInfo=MOTOR_MOVE_VEL, index=2
> drvInfo=MOTOR_HOME, index=3
> drvInfo=MOTOR_STOP_AXIS, index=4
> drvInfo=MOTOR_VELOCITY, index=5
> drvInfo=MOTOR_VEL_BASE, index=6
> drvInfo=MOTOR_ACCEL, index=7
> drvInfo=MOTOR_POSITION, index=8
> drvInfo=MOTOR_RESOLUTION, index=12
> drvInfo=MOTOR_ENCODER_RATIO, index=13
> drvInfo=MOTOR_PGAIN, index=14
> drvInfo=MOTOR_IGAIN, index=15
> drvInfo=MOTOR_DGAIN, index=16
> drvInfo=MOTOR_HIGH_LIMIT, index=17
> drvInfo=MOTOR_LOW_LIMIT, index=18
> drvInfo=MOTOR_CLOSED_LOOP, index=19
> drvInfo=MOTOR_STATUS, index=25
> drvInfo=MOTOR_UPDATE_STATUS, index=26
> 2026/06/25 15:29:48.311 motorExit 0 registerInterruptUser
> 2026/06/25 15:29:48.311 asynMotorController:readGenericPointer:
> MotorStatus = status34, position=425203751.000000, encoder
> position=0.000000, velocity=0.000000
> 2026/06/25 15:29:48.311 motorExit asynManager::queueLockPort locking port
> 2026/06/25 15:29:48.311 motorExit asynManager::queueLockPort created
> queueLockPortPvt=0x561069c8f7a0
> queueLockPortPvt=0x561069c8f7a0, event=0x561069c979e0, mutex=0x561069c97990
> 2026/06/25 15:29:48.311 motorExit asynManager::queueLockPort taking
> mutex 0x561069c97990
> 2026/06/25 15:29:48.311 motorExit asynManager::queueLockPort queueing
> request
> 2026/06/25 15:29:48.311 motorExit addr 0 queueRequest priority 0 not
> lockHolder
> 2026/06/25 15:29:48.311 motorExit schedule queueRequest timeout in
> 2.000000 seconds
> 2026/06/25 15:29:48.311 motorExit asynManager::queueLockPort waiting for
> event
> 2026/06/25 15:29:48.312 motorExit 0 autoConnect
> 2026/06/25 15:29:48.312 asynPortDriver:connect:, pasynUser=0x561069c83188
> 2026/06/25 15:29:48.312 asynManager::portThread port=motorExit callback
> 2026/06/25 15:29:48.312 motorExit asynManager::queueLockPortCallback
> signaling begin event
> waiting for mutex from queueUnlockPort
> 2026/06/25 15:29:48.312 motorExit asynManager::queueLockPort got event
> from callback
> 2026/06/25 15:29:48.312 EXIT:zpos devMotorAsyn::statusCallback new
> value=[p:425203751.000000,e:0.000000,s:22]
> 2026/06/25 15:29:48.312 asynMotorController:writeFloat64: Set driver
> motorExit, axis 0 encoder ratio=1.000000
> 2026/06/25 15:29:48.312 asynMotorController:writeFloat64:: axis=0,
> function=13, value=1.000000
> 2026/06/25 15:29:48.312 asynFloat64SyncIO wrote: 1.000000e+00
> 2026/06/25 15:29:48.312 motorExit queueUnlockPort
> 2026/06/25 15:29:48.312 motorExit asynManager::queueUnlockPort waiting
> for event
> 2026/06/25 15:29:48.313 motorExit queueUnlockPort unlock mutex
> 0x561069c97990 complete.
> 2026/06/25 15:29:48.313 devMotorAsyn::init_controller, EXIT:zpos set
> encoder ratio to 1.000000
> 2026/06/25 15:29:48.313 devMotorAsyn::init_controller, EXIT:zpos setting
> of position not required, position=425203751.000000, mres=0.000200,
> dval=0.000000, rdbd=0.0002002026/06/25 15:29:48.313 EXIT:zpos
> devMotorAsyn::update_values, needUpdate=1
> 2026/06/25 15:29:48.313 devMotorAsyn::build_trans: EXIT:zpos
> motor_cmnd=19, pact=0, value=375000.000000
> 2026/06/25 15:29:48.313 devAsynMotor::build_trans: calling queueRequest,
> pmsg=0x561069c97c40, sizeof(*pmsg)=24pmsg->command=14, pmsg-
>  >interface=1, pmsg->dvalue=375000.000000
> 2026/06/25 15:29:48.313 motorExit addr 0 queueRequest priority 0 not
> lockHolder
> motor_cmnd=20, pact=0, value=-375000.000000
> pmsg=0x561069c97c90, sizeof(*pmsg)=24pmsg->command=15, pmsg-
>  >interface=1, pmsg->dvalue=-375000.000000
> lockHolder
> 2026/06/25 15:29:48.313 asynManager::portThread port=motorExit callback
> 2026/06/25 15:29:48.313 devMotorAsyn::asynCallback: EXIT:zpos
> pmsg=0x561069c97c40, sizeof(*pmsg)=24, pmsg->command=14,pmsg-
>  >interface=1, pmsg->ivalue=0, pmsg->dvalue=375000.000000, pasynUser-
>  >reason=17
> 2026/06/25 15:29:48.313 asynMotorController:writeFloat64: Set driver
> motorExit, axis 0 high limit=375000.000000
> 2026/06/25 15:29:48.313 asynMotorController:writeFloat64:: axis=0,
> function=17, value=375000.000000
> pmsg=0x561069c97c90, sizeof(*pmsg)=24, pmsg->command=15,pmsg-
>  >interface=1, pmsg->ivalue=0, pmsg->dvalue=-375000.000000, pasynUser-
>  >reason=18
> motorExit, axis 0 low limit=-375000.000000
> function=18, value=-375000.000000
> Output when attempting to caput absolute position:
> 2026/06/25 15:07:44.438 192.168.0.204:3001 UDP write 3
> \xaa\v\a
>                        se velocity=500.000000, velocity=25000.000000,
> 2026/06/25 15:07:46.445 devMotorAsyn::asynCallback: EXIT:zpos
> 2026/06/25 15:07:46.445 EXIT:zpos devMotorAsyn::update_values, needUpdate=1
> *Sent:* Wednesday, June 17, 2026 21:07
> *To:* Torsten Bögershausen; tech-talk at aps.anl.gov; Rea Domitrović
> Hi Rea,
>       I see that driver developers prefer to use octet-based
>     communication rather than use the manufacturer-provided libraries.
>     Is there a reason why that is the case, or is it simply that octet-
>     based communicaton is more universal?
> Manufacturer libraries will be provided for specific operating system
> and specific versions of those OS. That can restrict where they can be
> deployed.  They may restrict redistribution, which prevents including
> them in the motor Github repository.  They almost certainly won't be
> supported on real-time OS like RTEMS or vxWorks.
>     Further, the Fastech controller allows both octet-based
>     communication and library-based communication, but octet-based
>     communication requires the master to send a one-byte "sync number"
>     which serves as an idempotence token. I assume it would be necessary
>     to implement that myself; could I be using some sort of global
>     variable, and how do I make sure that I never land on the same
>     number twice in a row?
> Many protocols have something like that.  You just have a member
> variable in your driver class that increments by 1 on each message it
> sends, and wraps back to 0 after 255.
> Mark
> *Sent:* Wednesday, June 17, 2026 8:34 AM
> *To:* Torsten Bögershausen <tboegi at edom.se>; tech-talk at aps.anl.gov
> Hi Torsten,
> thanks for pointing me in the right direction. I'm looking at the manual
> and the source for other submodules now (motorSmarAct and motorAcs); I
> see that driver developers prefer to use octet-based communication
> rather than use the manufacturer-provided libraries. Is there a reason
> why that is the case, or is it simply that octet-based communicaton is
> more universal?
> Further, the Fastech controller allows both octet-based communication
> and library-based communication, but octet-based communication requires
> the master to send a one-byte "sync number" which serves as an
> idempotence token. I assume it would be necessary to implement that
> myself; could I be using some sort of global variable, and how do I make
> sure that I never land on the same number twice in a row? Kind regards,
> Rea
> *From:* Torsten Bögershausen <tboegi at edom.se>
> *Sent:* Wednesday, June 10, 2026 1:49:41 PM
> Hej Rea,
> I haven't worked with them, no.
> If you have Ethernet (not to be confused with EtherCAT),
> I read the manual as if they use UDP for communication,
> and knowing that you can write a simple model 3 driver, I think.
> (Other suggestions are welcome of course)
> /Torsten
> On 2026-06-10 12:52, Rea Domitrović via Tech-talk wrote:
>  > Hi all,
>  > I'm working with some Fastech Ezi-Servo II Plus-E motors, and I was
>  > wondering if someone had already worked with them and/or made an EPICS
>  > driver or Motor submodule? This particular line of motors and
>  > drives uses an Ethernet interface. Kind regards,
>  > Rea Domitrović
>  > Institut Ruđer Bošković
>  > Zagreb, Croatia
> Oprez: Ova poruka stigla je od vanjskog pošiljatelja. Prije otvaranja
> poveznica ili privitaka provjerite pošiljatelja. Caution:This email
> originated from an external sender. Please verify the sender before
> opening links or attachments.
> *Oprez:* Ova poruka stigla je od vanjskog pošiljatelja. Prije otvaranja
> poveznica ili privitaka provjerite pošiljatelja. *Caution:*This email
Oprez: Ova poruka stigla je od vanjskog pošiljatelja. Prije otvaranja poveznica ili privitaka provjerite pošiljatelja. Caution:This email originated from an external sender. Please verify the sender before opening links or attachments.
EPICS support for Fastech motors Rea Domitrović via Tech-talk
Re: EPICS support for Fastech motors Torsten Bögershausen via Tech-talk
Re: EPICS support for Fastech motors Rea Domitrović via Tech-talk
Re: EPICS support for Fastech motors Mark Rivers via Tech-talk
Prev: Bridge PV to REST and WebSocket in Python Wang, Lin via Tech-talk
Next: Re: 2026 white paper on EPICS vs commercial SCADA software Javier Cruz Miranda via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  <2026
Prev: Re: EPICS support for Fastech motors Torsten Bögershausen via Tech-talk
Next: Problem building on windows-x64 Mark Rivers via Tech-talk
ANJ, 30 Jun 2026 · Home · News · About · Talk · Base · Modules · Extensions ·