Thank you very much for this patch Andrew. We have been testing in the lab here at DLS and it is looking good; our plan is to roll it out more generally quite soon.
In our case it turns out that the trigger was (accidentially) changing a particular status pv from mbbi to stringin.
> -----Original Message-----
> From: Andrew Johnson [mailto:[email protected]]
> Sent: 29 June 2018 17:34
> To: Abbott, Michael (DLSLtd,RAL,TEC); EPICS tech-talk
> Subject: Re: 'assert (pca->pgetNative)' failed in ../dbCa.c
> Hi Michael,
> On 06/29/2018 01:43 AM, [email protected] wrote:
> > From: [email protected]
> >> So by this point you're probably hoping that the attached patch
> >> fixes the issue; well congratulations for reading this far, I tried
> >> out my suspicion above and the attached patch does seem to work for
> >> me on the 3.14 branch version, which should be close enough to
> >> yours to be able to apply one way or the other. Please test and let
> >> me know so I can apply it to the Base-3.14 branch and merge up.
> > I've just noticed that the patch doesn't address the data type
> > mismatch directly, only through the separate connection callback. Is
> > this going to be enough to avoid hitting those asserts even in the
> > presence of an IOC server breaking the rules?
> Without the patch I can trigger this assertion using the attached pair
> of databases. Start by booting both in separate IOCs, then switch the
> anj:val alias to point to a different record type and reboot that IOC.
> This causes the other IOC to die with:
> > epics> DB CA Link Exception: "Virtual circuit disconnect", context
> "tux.aps.anl.gov:44710"
> > A call to 'assert(pca->pgetNative)'
> > by thread 'CAC-TCP-recv' failed in ../dbCa.c line 686.
> > EPICS Release EPICS R3.14.12.7-DEV.
> > Local time is 2018-06-27 14:45:03.260025965 CDT
> > Please E-mail this message to the author or to [email protected]
> > Calling epicsThreadSuspendSelf()
> After applying that patch I can see all the INP links reconnecting and
> getting new values from the alias without any problems. It takes a
> couple of scan periods for everything to reconnect and sync up in this
> example, but there were no more crashes in my testing.
> > After all, an assert is a confident statement that the invariant in
> > question is never going to be broken, because all of the elements of
> > the invariant are under *our* control; but in this case aren't we
> > still in the situation where the ca_field_type() is not as expected?
> > Or are you saying (implicitly) that here connectionCallback() is
> > *guaranteed* to be called before any change of ca_field_type()?
> Au contraire, ca_field_type() should have been updated before the call
> to connectionCallback(). However the assertion that fails is in
> eventCallback() which isn't called until after connectionCallback(). By
> clearing the original monitor subscription inside connectionCallback()
> we are stopping the calls to eventCallback() with the old native data
> type.
> > I have a feeling that in our case when we saw the failure, it wasn't
> > so much that the restarting server changed its record type, but that
> > there was something rather more bumpy about its restart (my colleague
> > working on it was trying to migrate between different EPICS and Linux
> > versions with some unexpected failures). However the only concrete
> > evidence we have is the error message and a large coincidence.
> If you can find another way to trigger this assertion failure with the
> patch applied please try to replicate it so someone else can trigger it.
- 'assert (pca->pgetNative)' failed in ../dbCa.c [email protected]
- Re: 'assert (pca->pgetNative)' failed in ../dbCa.c Andrew Johnson
- RE: 'assert (pca->pgetNative)' failed in ../dbCa.c [email protected]
Failed caput not notified when using ca_array_put_callback [email protected]
areaDetector R3-3-2 released Mark Rivers
<2018>
2025
2026
CCD vs. CMOS in accelerator environement John Dobbins
<2018>
2025
2026