Hi Mark,
I see,thank you very much.
Best regards.
Gao Zhenhua
> -----原始邮件-----
> 发件人: "Mark Rivers" <[email protected]>
> 发送时间: 2021-05-25 20:12:19 (星期二)
> 收件人: "高振华" <[email protected]>
> 抄送: "[email protected]" <[email protected]>
> 主题: Re: Re: How to set bo PV to zero when starting Modbus IOC
> Hi Zhenhua,
> > 1. Is the Dbpf command placed after iocInit written to the PLC after the IOC is started and before the scanner mechanism starts scanning processing?
> No, dbpf happens after iocInit is complete and scanning has started.
> However, if you use autosave and PINI=YES then it does happen as part of iocInit, before scanning starts.
> > 2. Is it performed as the first write to the PLC with the start of the IOC?
> The dbpf will be the first write to that PLC register if you set PINI=NO on the record that writes to that register. If other records have PINI=YES then it will not be the first write to the PLC, just the first write to that register.
> Mark
> ________________________________
> From: 高振华 <[email protected]>
> Sent: Tuesday, May 25, 2021 2:26 AM
> To: Mark Rivers
> Cc: [email protected]
> Subject: Re: Re: How to set bo PV to zero when starting Modbus IOC
> Hi Mark,
> Thanks,two questions remain:
> Best regards.
> Gao Zhenhua
> > -----原始邮件-----
> > 发送时间: 2021-05-25 09:00:06 (星期二)
> > 主题: Re: How to set bo PV to zero when starting Modbus IOC
> > Hi Zhenhua,
> > The value in the database file will be replaced by the value read from the device.
> > There are 2 ways to force the value to zero when the IOC start up:
> > - Add the PV to autosave and set the value to 0 before the IOC reboots. The value in autosave will be written to the device if PINI=1.
> > - Put a dbpf command after iocInit which writes zero to the PV.
> > Mark
> > Sent from my iPhone
> > > On May 24, 2021, at 7:39 PM, 高振华 <[email protected]> wrote:
> > > Hi Mark,
> > > I tried to set BO PV to zero when starting Modbus R2-11 IOC, but failed. PINI worked, but VAL didn't work.When IOC is started, what is written to PLC is the value that has just been read.
> > > Can't the Modbus R2-11 driver set BO PV to zero when IOC starts?
> > > Best regards.
> > > Gao Zhenhua
> > > BSRF(Beijing Synchrotron Radiation Facility)
> > > Email:[email protected]
> 祝好!
> 高振华
> 电话:010-88235426
祝好!
高振华
电话:010-88235426
- How to set bo PV to zero when starting Modbus IOC 高振华 via Tech-talk
- Re: How to set bo PV to zero when starting Modbus IOC Mark Rivers via Tech-talk
- Re: Re: How to set bo PV to zero when starting Modbus IOC 高振华 via Tech-talk
- Re: Re: How to set bo PV to zero when starting Modbus IOC Mark Rivers via Tech-talk
Re: using autosave, iocInit hangs Heinz Junkes via Tech-talk
Re: SNMP in EPICS Miroslaw Dach via Tech-talk
<2021>
2025
2026
Issue with FPGA based encoder box when running with EPICS 7.0.5 Wlodek, Jakub via Tech-talk
<2021>
2025
2026