1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  <2022>  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  <2022>  2023  2024  2025  2026
Subject: AW: Eurotherm2604 modbus support
From: "Sintschuk, Michael via Tech-talk" <[email protected]>
To: Mark Rivers <[email protected]>, tech-talk <[email protected]>
Date: Tue, 6 Dec 2022 15:39:55 +0000
Hi Mark,
thanks for the hint. I got it working now when I connected the Eurotherm to the Moxa NPort serial device server:
drvAsynIPPortConfigure("EMODBUS","nport1:4008",0,0,1)
After all, it was setting the link type to 1=RTU, second argument in this line:
modbusInterposeConfig(EMODBUS, 1, 2000, 0)
I thought that when I’m using “drvAsynIPPortConfigure” the link type has to be 0=TCP because the serial device server converts the serial port to a TCP/IP port...
Michael
Von: Mark Rivers <[email protected]>
Gesendet: Montag, 5. Dezember 2022 19:56
An: Sintschuk, Michael <[email protected]>; tech-talk <[email protected]>
Cc: [email protected]; [email protected]
Betreff: RE: Eurotherm2604 modbus support
SICHERHEITSHINWEIS: Diese E-Mail wurde von außerhalb an die BAM gesendet. Bitte klicken Sie nicht auf Links oder öffnen Anhänge, bevor Sie nicht den Absender verifiziert haben und sicher sind, dass der Inhalt vertrauenswürdig ist.
This message was sent from outside of BAM. Please do not click links or open attachments unless you recognize the sender and know the content is trustworthy.
Hi Michael,
I know very little about these controllers.  But looking at the catalog here https://eurothermonline.com/controllers/eurotherm-2408.html for one model, it seems that the communications option is specified when ordering, and there are lots of choices like RS-485 BiSync, RS-484-Modbus, RS232-Modbus, etc.  See attachment. Are you sure how yours is configured?
Sent: Monday, December 5, 2022 11:53 AM
To: Mark Rivers <[email protected]>; tech-talk <[email protected]>
Hi Mark,
yes, that is still a leftover when I was trying to connect via a Moxa NPort serial device server. This is actually the way I want to connect in the end but to be sure that it is not a faulty device server setting, I connect this way (because iTools connects to the COM1 port without problems).
However, when I change the link type to 2=ASCII, the error messages stay the same. When I change to 1=RTU, I get CRC errors:
C:\epics\IOC\EurothermIOC\iocBoot\iocEurotherm>C:\epics\IOC\EurothermIOC\bin\windows-x64-static\Eurotherm.exe st.cmd
#!../../bin/windows-x64-static/Eurotherm
< envPaths
epicsEnvSet("IOC","iocEurotherm")
epicsEnvSet("TOP","C:/epics/IOC/EurothermIOC")
epicsEnvSet("SUPPORT","C:/epics/inst-7.0.3.1")
epicsEnvSet("ASYN","C:/epics/inst-7.0.3.1/asyn-R4-39")
epicsEnvSet("EUROTHERM2K","C:/epics/inst-7.0.3.1/eurotherm2k")
epicsEnvSet("MODBUS","C:/epics/inst-7.0.3.1/modbus")
epicsEnvSet("EPICS_BASE","C:/epics/base-7.0.3.1")
cd "C:/epics/IOC/EurothermIOC"
dbLoadDatabase "dbd/Eurotherm.dbd"
Eurotherm_registerRecordDeviceDriver pdbbase
drvAsynSerialPortConfigure("EMODBUS","COM1",0,0,1)
asynSetOption("EMODBUS", -1, "baud",    "9600")
asynSetOption("EMODBUS", -1, "bits",    "8")
asynSetOption("EMODBUS", -1, "stop",    "1")
asynSetOption("EMODBUS", -1, "parity",  "none")
#asynSetOption("EMODBUS", -1, "crtscts", "Y")
#asynSetOption("EMODBUS", -1, "clocal",  "N")
#asynSetOption("EMODBUS", -1, "ixon", "Y")
#asynOctetSetInputEos( "EMODBUS", -1, "\r\n")
#asynOctetSetOutputEos("EMODBUS", -1, "\r")
eurothermModbusCtrlConfigure(EMODBUS, 1)
2022/12/05 18:27:09.067 modbusInterpose::readIt, CRC error
2022/12/05 18:27:09.070 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_0_Wr_
ATUNE error calling writeRead, error=, nwrite=6/6, nread=0
eurothermModbusLoopConfigure(EMODBUS, 1, 1)
2022/12/05 18:27:09.105 modbusInterpose::readIt, CRC error
2022/12/05 18:27:09.106 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Wr_
PV error calling writeRead, error=, nwrite=6/6, nread=0
2022/12/05 18:27:09.133 modbusInterpose::readIt, CRC error
2022/12/05 18:27:09.134 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Wr_
RR error calling writeRead, error=, nwrite=6/6, nread=0
2022/12/05 18:27:09.161 modbusInterpose::readIt, CRC error
2022/12/05 18:27:09.162 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Wr_
MAN error calling writeRead, error=, nwrite=6/6, nread=0
2022/12/05 18:27:09.196 modbusInterpose::readIt, CRC error
2022/12/05 18:27:09.197 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Wr_
PID error calling writeRead, error=, nwrite=6/6, nread=0
## Load record instances
dbLoadRecords("db/example_modbus_expanded.db","user=bl")
cd "C:/epics/IOC/EurothermIOC/iocBoot/iocEurotherm"
iocInit
Starting iocInit
## EPICS R7.0.3.1
## EPICS Base built Mar  9 2020
## Start any sequence programs
#seq sncxxx,"user=bl"
2022/12/05 18:27:09.750 modbusInterpose::readIt, CRC error
2022/12/05 18:27:09.751 EUROTHERM2K:SP devAsynInt32::processCallbackOutput proce
ss write error
2022/12/05 18:27:09.776 modbusInterpose::readIt, CRC error
2022/12/05 18:27:09.777 EUROTHERM2K:RR devAsynInt32::processCallbackOutput proce
ss write error
2022/12/05 18:27:09.801 modbusInterpose::readIt, CRC error
2022/12/05 18:27:09.803 EUROTHERM2K:P devAsynInt32::processCallbackOutput proces
s write error
epics> 2022/12/05 18:27:10.066 modbusInterpose::readIt, CRC error
2022/12/05 18:27:10.067 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_0_Rd_
2022/12/05 18:27:10.103 modbusInterpose::readIt, CRC error
2022/12/05 18:27:10.105 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Rd_
2022/12/05 18:27:10.131 modbusInterpose::readIt, CRC error
2022/12/05 18:27:10.133 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Rd_
2022/12/05 18:27:10.159 modbusInterpose::readIt, CRC error
2022/12/05 18:27:10.161 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Rd_
2022/12/05 18:27:10.196 modbusInterpose::readIt, CRC error
2022/12/05 18:27:10.197 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Rd_
2022/12/05 18:27:11.094 modbusInterpose::readIt, CRC error
2022/12/05 18:27:11.133 modbusInterpose::readIt, CRC error
2022/12/05 18:27:11.157 modbusInterpose::readIt, CRC error
2022/12/05 18:27:11.191 modbusInterpose::readIt, CRC error
2022/12/05 18:27:11.225 modbusInterpose::readIt, CRC error
2022/12/05 18:27:13.121 modbusInterpose::readIt, CRC error
When I change the crtscts Option to Yes
the error messages are again like with the 0=TCP link type.
Michael
Gesendet: Montag, 5. Dezember 2022 17:48
Hi Michael,
  • drvAsynSerialPortConfigure("EMODBUS","COM1",0,0,1)
  • modbusInterposeConfig(EMODBUS, 0, 2000, 0)
The above 2 lines do not look internally consistent to me.  The first line says you are using a serial port for communication.  The second line says that the link type (second argument) is 0, which is Modbus TCP.  Normally when you communicate over a serial link type needs to be 1=RTU or 2=ASCII.
Sent: Monday, December 5, 2022 10:30 AM
To: tech-talk <
[email protected]>
Cc:
[email protected]; [email protected]; Mark Rivers <[email protected]>
Subject: Eurotherm2604 modbus support
Hello EPICS-community,
I have trouble connecting a Eurotherm2604 temperature controller via modbus with this EPICS-module:
https://github.com/jwlodek/eurotherm2k
A couple of months ago this package was refurbished as you can see from this tech-talk:
https://epics.anl.gov/tech-talk/2022/msg01319.php
I can compile the module and can build the IOC, which works fine via the EI-bisynch protocol. But I can’t establish any connection when it comes to modbus (I need the modbus protocol to read some additional info that is not implemented in EI-bisynch). FYI: the modbus communication on the very same COM-port (same cable) just works fine with the vendor software iTools. This is how my IOC-modbus startup looks like (I’m using the latest modbus-master R3-2):
< envPaths
2022/12/05 16:51:56.791 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_0_Rd_
ATUNE error calling writeRead, error=asynManager::queueLockPort queueRequest tim
ed out, nwrite=0/6, nread=0
2022/12/05 16:51:57.797 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_0_Wr_
2022/12/05 16:52:00.802 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Rd_
PV error calling writeRead, error=asynManager::queueLockPort queueRequest timed
2022/12/05 16:52:01.808 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Wr_
2022/12/05 16:52:03.814 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Wr_
2022/12/05 16:52:05.816 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Wr_
MAN error calling writeRead, error=asynManager::queueLockPort queueRequest timed
2022/12/05 16:52:06.809 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Rd_
2022/12/05 16:52:07.813 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Rd_
2022/12/05 16:52:07.814 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Wr_
PID error calling writeRead, error=asynManager::queueLockPort queueRequest timed
iocInit
Starting iocInit
## EPICS R7.0.3.1
2022/12/05 16:52:09.814 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Rd_
epics> 2022/12/05 16:52:12.321 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_
1_1_Wr_PV error calling writeRead, error=asynManager::queueLockPort queueRequest
timed out, nwrite=0/6, nread=0
2022/12/05 16:52:12.323 EUROTHERM2K:SP devAsynInt32::processCallbackOutput proce
ss write error
2022/12/05 16:52:12.325 EUROTHERM2K:P devAsynInt32::processCallbackOutput proces
s write error
2022/12/05 16:52:12.330 EUROTHERM2K:RR devAsynInt32::processCallbackOutput proce
ss write error
2022/12/05 16:52:13.414 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Rd_
RR error calling writeRead, error=asynManager::queueLockPort queueRequest timed
2022/12/05 16:52:13.416 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Rd_
2022/12/05 16:52:14.332 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_0_Rd_
ed out, nwrite=6/6, nread=0
2022/12/05 16:52:16.415 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Rd_
2022/12/05 16:52:22.410 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_0_Rd_
2022/12/05 16:52:22.419 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Rd_
2022/12/05 16:52:24.413 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Rd_
2022/12/05 16:52:24.420 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Rd_
2022/12/05 16:52:25.423 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Rd_
2022/12/05 16:52:26.419 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Rd_
2022/12/05 16:52:27.419 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Rd_
2022/12/05 16:52:28.418 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Rd_
Can someone help?
Michael
Michael Sintschuk
Bundesanstalt für Materialforschung und –prüfung (BAM)
8.5 Mikro-ZfP
Unter den Eichen 87
12205 Berlin
GERMANY
P: +49 30 8062-15063 (BESSY, Adlershof)
P: +49 30 8104-4065 (BAM, Steglitz)
[email protected]
[email protected]
Eurotherm2604 modbus support Sintschuk, Michael via Tech-talk
RE: Eurotherm2604 modbus support Mark Rivers via Tech-talk
AW: Eurotherm2604 modbus support Sintschuk, Michael via Tech-talk
Prev: Re: Compiling base on Rocky Linux 9 Ernesto Paiser via Tech-talk
Next: Re: A simple EPICS driver example for PCI devices using asynPortDriver on Linux Michael Davidsaver via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  <2022>  2023  2024  2025  2026
Prev: RE: Eurotherm2604 modbus support Mark Rivers via Tech-talk
Next: Compiling base on Rocky Linux 9 Ernesto Paiser via Tech-talk