1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  <2026>  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  <2026>
Subject: Re: Support for piezo controller nanoFAKTUR EBD-060310
From: Torsten Bögershausen via Tech-talk <tech-talk at aps.anl.gov>
To: LiangChih Chiang <yehnan174 at gmail.com>, tboegi at edom.se
Cc: "tech-talk at aps.anl.gov" <tech-talk at aps.anl.gov>
Date: Tue, 10 Feb 2026 09:44:55 +0100
On 2026-02-10 08:51, LiangChih Chiang wrote:
Hello, EPICS mates, thanks for the help.
The Model 3 driver implementation of nanoFaktur EBD-060310 piezo controller is kind of working now.
The attachment files include source code.and IOC startup files.
I still have some questions. Hope you can provide suggestions.
1.
I thought motorClosedLoop_ is mapped to CNEN, isn't it?
Yes, that is what most (all ?) model 3 driver do
I set motorClosedLoop_ to 1 in code, as following:
setIntegerParam(c_p_->motorClosedLoop_, 1);
But in the CNEN field of motor record is 0(Disable).
CNEN is updated from the status of the controller.
Does the code in the poll() function update the
"motorClosedLoop_" parameter ?
2.
Can I set UEIP field of motor record in driver code?
If UEIP is 0, the RRBV won't update even REP is updated continuously.
> > I use the asyn_motor.db in motor-R6-11.
That's pretty old.
The motor record in this .db doesn't have UEIP field.
So I set it in a .doAfterIocInit file.
3.
The MRES field of motor record to 0.000001 in ioc startup file.
When I set VAL of motor record to 1.234,
I will get "position" value 1234000
in asynMotorAxis::move(double position, int relative, double minVelocity, double maxVelocity, double acceleration);
Then I need the MRES value to do the conversion,
because I need to send the value "1.234" to the controller.
Why the following code returns the value 0 instead the wanted 0.000001?
     double res = 0.000001;  // resolution
     c_p_->getDoubleParam(channel_, c_p_->motorResolution_, &res);
We can call that on ol' bug.
See even
<https://urldefense.us/v3/__https://github.com/epics-modules/motor/blob/master/motorApp/Db/asyn_motor.db__;!!G_uCfscf7eWS!a6-0o3PaphqYIbSZJV-AhLdQoFjzGJKqz6FYeIhy3LVrZaK_SCDeV78gSx6AiWjNjuvePxhR6OXlx-vx9_0$ >
.... follow the flow .... and
motorRecResolution_
is your friend. However, since that is processed through records,
be prepared to read 0.0 a couple of times.
myStatus = c_p_->getDoubleParam(channel_, c_p_->motorResolution_, &res);
And see that myStatus is not asynSuccess,right ?
4.
There is no "home" concept in this piezo controller.
So I have no way to implement the asynMotorAxis::home function, am I right?
Is it called reference ?
Then that can be mapped to "home()"
On Sat, Feb 7, 2026 at 12:08 AM Torsten Bögershausen <tboegi at edom.se <mailto:tboegi at edom.se>> wrote:
    Hej again,
    Why are the RMP and REP fields integer ?
    The "real world encoders" typically count in integer,
    and so far the int32 had been enough.
    Even if we today have encoders with more bits,
    these are typically attached to the motor controller
    and handled there.
    The RMP field counts steps.
    It was designed for a stepper motor, and even here
    32 bit where both enough
    (and that is what we have before int64 became available)
    The motorRecord itself uses the step in RMP to prevent
    commanding a motion the will end up on the same step.
    Moving from 0.050 to 0.051 is prevented, when MRES is 0.05
    For a piezo (or other modern controllers) we don't need this
    step-size, so that the motorRecord has  got the SPDB field,
    Set Point Dead Band.
    For the controllers which are in use here, most of them
    communicate in EGU.
    For that reason I made a patch, where the value
    "motorPosition_" from the driver is copied into
    the DRBV field without conversion through integers.
    The driver needs this patch:
<https://urldefense.us/v3/__https://github.com/EuropeanSpallationSource/m-epics-ethercatmc/__;!!G_uCfscf7eWS!a6-0o3PaphqYIbSZJV-AhLdQoFjzGJKqz6FYeIhy3LVrZaK_SCDeV78gSx6AiWjNjuvePxhR6OXlFzUYEyE$ blob/master/ethercatmcApp/src/ethercatmcIndexerAxis.cpp#L81..#L83 <https://urldefense.us/v3/__https://github.com/EuropeanSpallationSource/m-epics-ethercatmc/__;!!G_uCfscf7eWS!a6-0o3PaphqYIbSZJV-AhLdQoFjzGJKqz6FYeIhy3LVrZaK_SCDeV78gSx6AiWjNjuvePxhR6OXlFzUYEyE$ blob/master/ethercatmcApp/src/ethercatmcIndexerAxis.cpp#L81..%23L83>>
    The motor package itself is here:
<https://urldefense.us/v3/__https://github.com/EuropeanSpallationSource/motor/releases/tag/__;!!G_uCfscf7eWS!a6-0o3PaphqYIbSZJV-AhLdQoFjzGJKqz6FYeIhy3LVrZaK_SCDeV78gSx6AiWjNjuvePxhR6OXl_rIq3VA$ v7.2.8.1-ESS <https://urldefense.us/v3/__https://github.com/EuropeanSpallationSource/motor/__;!!G_uCfscf7eWS!a6-0o3PaphqYIbSZJV-AhLdQoFjzGJKqz6FYeIhy3LVrZaK_SCDeV78gSx6AiWjNjuvePxhR6OXl49zxdGA$ releases/tag/v7.2.8.1-ESS>>
    BR
    /Torsten
    On 2026-02-06 14:20, LiangChih Chiang wrote:
     > Hi, Torsten, thanks for replying.
     >  >Using epicsPrintf (or even printf) should be forbidden in
     >  >these kind of driver code.
     > ok. I'll fix it.
     >  >>1.
     >  > pC_->motorPosition_ is an int, used as an index
     >  > motorPosition is a double
     > You're right. My mistake.
     > Another question follows:
     > "cainfo <motor_record>.REP and .RMP" will get DBF_LONG.
     > Why aren't they DBF_DOUBLE?
     >  >>3.
     >  >>The values of position and voltage from the controller are
    float values.
     >  >>When setting, say 2.123456, to motorEncoderPosition, it will
    become 2
     > (which is an int).
     >  >This is depending on MRES in the motorRecord.
     >  >If you set it to 1.0 (or not at all, the the fallback is 1.0)
     >  >all values are rounded into integer.
     >  >The trick is to set MRES to 0.000001 or so and compensate
     >  >this in the driver (multipy with 1000000)
     > Yes. You're right.
     > I'll try.
     >  >For the open-loop-voltage:
     >  >You probably want an own asyn-parameter for this.
     > I'll consider it.
     > However, the chance of this piezo controller in open-loop mode is
     > extremely slim.
     > How to support two modes(closed-loop and open-loop) in Model 3
    driver?
     > In closed-loop mode, VAL and RBV mean position(unit um)?
     > In open-loop mode, VAL and RBV mean voltage?
     > On Fri, Feb 6, 2026 at 5:51 PM Torsten Bögershausen
     > <mailto:tboegi at edom.se <mailto:tboegi at edom.se>>> wrote:
     >     Hej LiangChih Chiang,
     >     thanks for asking.
     >     Before going into your questions, please allow one comment:
     >     Please consider to us asynPrint instead.
     >     Especially things like
     >     #ifdef DEBUG
     >                 printf("Warning: un-handled param data format:
     >     #endif
     >     Could be better coded as
     >         asynPrint(this->pasynUserSelf, ASYN_TRACE_ERROR,
     >             "%s: Warning....\n",
     >             __FUNCTION__);
     >     (If you write Warning or Err: or something is more a matter
    of taste)
     >     But in any way you want to know if things go bad much later,
     >     after firmware updates, changes in the IOC, glitches here and
    the )
     >     Having said that, finishing my review, which may read
    unintentionally
     >     hard, lets digg into the questions.
     >        1.
     >       > In asynMotorController.h, the data type of motorPosition_
     >       > and motorEncoderPosition_ are ints.
     >     A call inside the axis class looks like this:
     >     asynMotorAxis::setDoubleParam(pC_->motorPosition_,
    motorPosition);
     >     saying which asynparameter we ar writing to.
     >     motorPosition is a double, saying where the motor should be,
     >     according to the controller.
     >     motorEncoderPosition_ is the value coming from the sensor
    inside the
     >     controller.
     >     Example:
     >     the MCS2 from Smaract reads motorPosition like this:
     >        // Read the target position
     >         snprintf(pC_->outString_,sizeof(pC_->outString_)-1,
     >           ":CHAN%d:POS:TARG?", axisNo_);
     >     And encoderPosition like this:
     >            // read the actual position as measured by the sensor
     >             ":CHAN%d:POS?", axisNo_);
     >     3.
     >       > The values of position and voltage from the controller
    are float
     >     values.
     >       > When setting, say 2.1234...
     >     /BR Torsten
     >     On 2026-02-06 08:48, LiangChih Chiang via Tech-talk wrote:
     >      > Hello, EPICS mates,
     >      > I started to implement the “Model 3” driver for nanoFaktur
     >     EBD-060310
     >      > piezo controller.
     >      > The attached files(.cpp and .h) are the work-in-progress
    source
     >     code.
     >      > Not finished yet.
     >      > I have some questions.
     >      > 1.
     >      > But in derived class of asynMotorcontroller(like
     >      > smarActMCSMotorDriver.cpp and ACRMotorDriver.cpp),
     >      > the function setDoubleParam is used to set the above
    parameters.
     >      > Why is that?
     >      > 2.
     >      > I can read the position(unit um, range 0 to 40) and
    voltage(unit
     >     volts,
     >      > range -30 to 130) from the controller.
     >      > But which one should I set to motorPosition_and
     >     motorEncoderPosition_?
     >      > I don't quite understand.
     >      > 3.
     >      > The values of position and voltage from the controller are
    float
     >     values.
     >      > When setting, say 2.123456, to motorEncoderPosition, it will
     >     become 2
     >      > (which is an int).
     >      > How to handle this situation?
     >      > Should I do some kind of transformation? For example,
    multiply by
     >     1000,000?
     >      > 4.
     >      > In the member function: asynStatus poll(bool* moving_p),
     >      > I need to set the moving/done status of the stage to moving_p
     >      > and motorStatusDone_.
     >      > But there is no such exact suitable command provided by thhe
     >     controller.
     >      > A possible candidate is "get on-target status" meaning in
    closed-
     >     loop
     >      > mode(servo ON),
     >      > whether the position(from sensor) approached the set
    target or not.
     >      > 5.
     >      > The controller has two modes:
     >      > closed-loop mode(servo ON), users set the desired
    potion(unit um).
     >      > open-loop mode(servo OFF), uses set the voltage(unit volts).
     >      > What should I set to motorPosition_?
     >      > I think it should be something like "motor pulse".
     >      > what should I set to motorEncoderPosition_.?
     >      > I think it should be something like "encoder value".
     >      > ps
     >      > The controller uses binary communication protocol.
     >      > The following example is to read the position(in um) of
    channel 0:
     >      > hexadecimal bytes in little-endian:
     >      > 10 00 01 20 02 00 20 00 00 ac 01 00 00 00 00 fe
     >      > 10 00: total length, 16 bytes
     >      > 01 20: command ID, 0x2001 means "get position"
     >      > 02 00: custom ID, used to distinguish different client
    programs.
     >      > 20: option, 0x20 means "read"
     >      > 00: sequence number, Used in very long responses. Not used in
     >     commands.
     >      > 00: interface id, RS-232 or USB or Ethernet. Not used in
    commands.
     >      > ac: header checksum
     >      > 01: data format, 01 means 32-bit unsigned int
     >      > 00 00 00 00: data, channel 0
     >      > fe: checksum
     >      > The  response:
     >      > 13 00 01 20 02 00 10 00 01 b8 00 00 02 70 74 6a 3e
     >      > 13 00: total length, 19 bytes
    programs.
     >      > 10: option, 0x10 means "final, no more".
     >      > 01: interface id, 0x01 means RS-232.
     >      > b8: header checksum
     >      > 00: data format, 00 means 8-bit unsigned int
     >      > 00: data, channel 0
     >      > 02: data format, 02 means float
     >      > 70 74 6a 3e: data, 0.228960 (position in um)
     >      > 3e: checksum
     >      > Any suggestions and responses are appreciated.
     >      > Thank you.
     >      > On Thu, Apr 24, 2025 at 5:31 AM Mark Rivers
     >     <rivers at cars.uchicago.edu <mailto:rivers at cars.uchicago.edu>
    <mailto:rivers at cars.uchicago.edu <mailto:rivers at cars.uchicago.edu>>
     >      > <mailto:rivers at cars.uchicago.edu
    <mailto:rivers at cars.uchicago.edu>>>> wrote:
     >      >       * I think I would need to write the EPICS motor driver
     >     module for
     >      >         it.____
     >      >     __ __
     >      >     That is correct.  You should write a “Model 3” driver,
     >     meaning it is
     >      >     a C++ driver derived from the base classes
     >     asynMotorController and
     >      >     asynMotorAxis.____
     >      >     __ __
     >      >     I just looked at the manual for the nanoFAKTUR
    EBD-060310.
     >     It uses
     >      >     a non-standard binary communications protocol, not ASCII
     >     strings.
     >      >     That is unusual, most controllers use ASCII
    communication.____
     >      >     __ __
     >      >     The driver you suggested as a model, https://
    github.com/ <https://urldefense.us/v3/__https://github.com/__;!!G_uCfscf7eWS!a6-0o3PaphqYIbSZJV-AhLdQoFjzGJKqz6FYeIhy3LVrZaK_SCDeV78gSx6AiWjNjuvePxhR6OXle25glHI$ >
     >     epics-motor/ <https://urldefense.us/v3/__https://github.com/epics-motor/__;!!G_uCfscf7eWS!a6-0o3PaphqYIbSZJV-AhLdQoFjzGJKqz6FYeIhy3LVrZaK_SCDeV78gSx6AiWjNjuvePxhR6OXlw2mOxdY$  <https://
    github.com/epics-motor/>>
     >      >     motorPIGCS2 <https://urldefense.us/v3/__https:/
    github.com/ <https://urldefense.us/v3/__https:/github.com/>
     >     epics- <https://urldefense.us/v3/__https:/github.com/epics-
    <https://urldefense.us/v3/__https:/github.com/epics->>
     >      >     motor/motorPIGCS2__;!!G_uCfscf7eWS!
>  YgABnMrr4ouWf_GcXAuVe7LU-96lfvWFNG96utdBA3mgcrk9dBsWVY7JQtxclFMQQYwD2Zz0RmrbQGad8OJXFPc$>  is fairly complex because of the class hierarchy, so you might want to start with something simpler as your example. ____
     >      >     __ __
>      > https://urldefense.us/v3/__https://github.com/epics-motor/motorSmarAct/blob/master/__;!!G_uCfscf7eWS!a6-0o3PaphqYIbSZJV-AhLdQoFjzGJKqz6FYeIhy3LVrZaK_SCDeV78gSx6AiWjNjuvePxhR6OXlyR82pl4$ <https://urldefense.us/v3/__https://github.com/epics-motor/motorSmarAct/blob/master/__;!!G_uCfscf7eWS!a6-0o3PaphqYIbSZJV-AhLdQoFjzGJKqz6FYeIhy3LVrZaK_SCDeV78gSx6AiWjNjuvePxhR6OXlyR82pl4$ > >     smarActApp/ <https://urldefense.us/v3/__https://github.com/epics-motor/motorSmarAct/__;!!G_uCfscf7eWS!a6-0o3PaphqYIbSZJV-AhLdQoFjzGJKqz6FYeIhy3LVrZaK_SCDeV78gSx6AiWjNjuvePxhR6OXlMoTTQTM$ blob/ <https://urldefense.us/v3/__https://github.com/epics-motor/motorSmarAct/blob/__;!!G_uCfscf7eWS!a6-0o3PaphqYIbSZJV-AhLdQoFjzGJKqz6FYeIhy3LVrZaK_SCDeV78gSx6AiWjNjuvePxhR6OXlCzDAfYk$ >
     >     master/smarActApp/>
>      >     src/smarActMCSMotorDriver.cpp <https://urldefense.us/ v3/ <https://urldefense.us/v3/>
     >     __https:// <https://urldefense.us/v3/__https:// <https://
    urldefense.us/v3/__https://>>
     >      > github.com/epics-motor/motorSmarAct/blob/master/
smarActApp/src/ <https://urldefense.us/v3/__http://github.com/epics-motor/motorSmarAct/blob/__;!!G_uCfscf7eWS!a6-0o3PaphqYIbSZJV-AhLdQoFjzGJKqz6FYeIhy3LVrZaK_SCDeV78gSx6AiWjNjuvePxhR6OXliKBOMl8$ master/smarActApp/src/> >     <https://urldefense.us/v3/__http://github.com/epics-motor/motorSmarAct/blob/master/__;!!G_uCfscf7eWS!a6-0o3PaphqYIbSZJV-AhLdQoFjzGJKqz6FYeIhy3LVrZaK_SCDeV78gSx6AiWjNjuvePxhR6OXlald25MY$ smarActApp/src/ <https://urldefense.us/v3/__http://github.com/epics-motor/motorSmarAct/blob/__;!!G_uCfscf7eWS!a6-0o3PaphqYIbSZJV-AhLdQoFjzGJKqz6FYeIhy3LVrZaK_SCDeV78gSx6AiWjNjuvePxhR6OXliKBOMl8$ master/smarActApp/src/>>
     >      >     smarActMCSMotorDriver.cpp__;!!G_uCfscf7eWS!YLctRUSDiyz4K-
>  t8_BzT33ew7q6EOnMR2oSaoEqf7fY5hpd5mII4cyq4pP6Gt3vwMPp1s38VSS7kXyY4shD2qrU$>____
     >      >     __ __
     >      >     That uses ASCII communication, but it should not be
    too hard
     >     to take
     >      >     the concepts and use binary communication.____
     >      >     __ __
     >      >     Mark____
     >      >     __ __
     >      >     __ __
     >      >     __ __
     >      >     __ __
     >      >     __ __
     >      >     *From:*Tech-talk <tech-talk-bounces at aps.anl.gov
    <mailto:tech-talk-bounces at aps.anl.gov> <mailto:tech- <mailto:tech->
     > talk-bounces at aps.anl.gov <mailto:talk-bounces at aps.anl.gov>>
    <mailto:tech-talk- <mailto:tech-talk-> <mailto:tech-talk-
    <mailto:tech-talk->>
     >      > bounces at aps.anl.gov <mailto:bounces at aps.anl.gov>
    <mailto:bounces at aps.anl.gov <mailto:bounces at aps.anl.gov>>>> *On
    Behalf Of
     >     *LiangChih Chiang via Tech-talk
     >      >     *Sent:* Wednesday, April 23, 2025 1:41 AM
     >      >     *To:* tech-talk at aps.anl.gov <mailto:tech-
    talk at aps.anl.gov> <mailto:tech-talk at aps.anl.gov <mailto:tech-
    talk at aps.anl.gov>>
     >     <mailto:tech-talk at aps.anl.gov <mailto:tech-talk at aps.anl.gov>
    <mailto:tech-talk at aps.anl.gov <mailto:tech-talk at aps.anl.gov>>>
     >      >     *Subject:* Support for piezo controller nanoFAKTUR
    EBD-060310____
     >      >     __ __
     >      >     Hello, EPICS mates,____
     >      >     __ __
     >      >     I need to control a piezo sage with the controller
    nanoFAKTUR
     >      >     EBD-060310.____
     >      >     This is my first time using this controller.____
     >      >     I searched and couldn't find the EPICS support module
    for it.____
     >      >     __ __
     >      >     I think I would need to write the EPICS motor driver
    module
     >     for it.____
     >      >     __ __
     >      >     What module code would you recommend me to use as a
    starter
     >      >     reference?____
     >      >     For example, something like ____
     >      >     EPICS motor drivers for Physik Instrumente GCS2
    (General Command
     >      >     Set) compatible controllers____
     >      > https://urldefense.us/v3/__https://github.com/epics-motor/motorPIGCS2__;!!G_uCfscf7eWS!a6-0o3PaphqYIbSZJV-AhLdQoFjzGJKqz6FYeIhy3LVrZaK_SCDeV78gSx6AiWjNjuvePxhR6OXlRg-LFx8$  <https://
    github.com/epics-motor/motorPIGCS2> <https://urldefense.us/v3/__https://github.com/__;!!G_uCfscf7eWS!a6-0o3PaphqYIbSZJV-AhLdQoFjzGJKqz6FYeIhy3LVrZaK_SCDeV78gSx6AiWjNjuvePxhR6OXle25glHI$  <https://
    github.com/>
     >     epics-motor/motorPIGCS2> <https://urldefense.us/  <https://
    urldefense.us/> <https://
     > urldefense.us/ <http://urldefense.us/ >>
     >      >     v3/__https://urldefense.us/v3/__https://github.com/epics-motor/motorPIGCS2____;!!G_uCfscf7eWS!a6-0o3PaphqYIbSZJV-AhLdQoFjzGJKqz6FYeIhy3LVrZaK_SCDeV78gSx6AiWjNjuvePxhR6OXlutJ53r4$ ;
    <https://urldefense.us/v3/__http://github.com/epics-motor/motorPIGCS2____;!!G_uCfscf7eWS!a6-0o3PaphqYIbSZJV-AhLdQoFjzGJKqz6FYeIhy3LVrZaK_SCDeV78gSx6AiWjNjuvePxhR6OXlFWg9ZMY$ ;>!!
     >     G_uCfscf7eWS <https://urldefense.us/v3/__http://github.com/epics-motor/motorPIGCS2____;!!G_uCfscf7eWS!a6-0o3PaphqYIbSZJV-AhLdQoFjzGJKqz6FYeIhy3LVrZaK_SCDeV78gSx6AiWjNjuvePxhR6OXlFWg9ZMY$ ;
     >     G_uCfscf7eWS>!
>  YgABnMrr4ouWf_GcXAuVe7LU-96lfvWFNG96utdBA3mgcrk9dBsWVY7JQtxclFMQQYwD2Zz0RmrbQGad8OJXFPc$> ____
     >      >     __ __
     >      >     __ __
Re: Support for piezo controller nanoFAKTUR EBD-060310 LiangChih Chiang via Tech-talk
Re: Support for piezo controller nanoFAKTUR EBD-060310 Torsten Bögershausen via Tech-talk
Prev: Re: Support for piezo controller nanoFAKTUR EBD-060310 LiangChih Chiang via Tech-talk
Next: Yes, Base 7.0.10 was released! Johnson, Andrew N. via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  <2026>
Next: Re: Support for piezo controller nanoFAKTUR EBD-060310 LiangChih Chiang via Tech-talk