1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  <2022>  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  <2022>  2023  2024  2025  2026
Subject: Re: PINI field not working with modbus
To: "Marco A. Barra Montevechi Filho" <[email protected]>, "[email protected]" <[email protected]>
Date: Wed, 27 Jul 2022 12:02:34 +0000
Hi Marco,
I'm glad that adding the epicsThreadSleep(1.0) fixes the problem.
>  I was not aware that this is how the modbus driver worked.
The behavior for read functions is documented here:
From: Marco A. Barra Montevechi Filho <[email protected]>
Sent: Wednesday, July 27, 2022 6:57 AM
To: Mark Rivers <[email protected]>; [email protected] <[email protected]>
Oh! this makes sense and also explains the wireshark capture. I was not aware that this is how the modbus driver worked.
I tested just now and it works. Thanks!
Sent: 27 July 2022 08:52
To: Marco A. Barra Montevechi Filho <[email protected]>; [email protected] <[email protected]>
Hi Marco,
I think I understand why you are not seeing the correct value when you use PINI=YES and SCAN=Passive.  The problem is a race condition.
As I said in a previous message, it appears that you have set the MBUS_POLL macro to 1000, which means the poller for that Modbus driver is running every 1000 ms (1 second).  The poller waits for this delay at the beginning of the poll loop.  The poller thread is started when your startup script calls drvModbusAsynConfigure().  When the record processes during iocInit() because PINI=YES it just gets the most recent value from the poller.
However, in your case because you have a slow polling rate of 1 second it is likely that the poller has not yet done the first poll when the record is processed during iocInit, so there is no value to use.
I believe you can fix the problem by adding this line to your startup script just before iocInit()
PINI field not working with modbus Marco A. Barra Montevechi Filho via Tech-talk
Re: PINI field not working with modbus Mark Rivers via Tech-talk
Re: PINI field not working with modbus Marco A. Barra Montevechi Filho via Tech-talk
RE: PINI field not working with modbus Mark Rivers via Tech-talk
Prev: Re: PINI field not working with modbus Mark Rivers via Tech-talk
Next: Re: PINI field not working with modbus bob dalesio via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  <2022>  2023  2024  2025  2026
Prev: Re: PINI field not working with modbus Marco A. Barra Montevechi Filho via Tech-talk