1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  <2007>  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  <2007>  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Subject: Re: device support for output connected to volatile device
To: Andrew Johnson <[email protected]>, EPICS Tech-Talk <[email protected]>
Date: Wed, 05 Dec 2007 10:39:51 -0500
First thanks to the responders. In addition to Andrew, Emmanuel Mayssat, Mark Rivers, Erik Johansson.
I agree this is not an ideal situation, having multiple paths to control hardware with one of those paths being outside EPICS. However I find when I purchase network capable hardware it generally comes with a vendor supplied interface which turns out to be useful at one point or another. Given this situation I want to be sure that the operator screens reflect the current state of the hardware.
I considered the solution of having a readback record for each output. In my case there are many outputs and this would have led to even more cluttered displays. My device support is in fact scanning, the state of all registers is readback periodically, so it was fairly straight forward to modify it in the style of the Ether_IP device support (thanks Kay for the example).
John Dobbins
Andrew Johnson wrote:
John Dobbins wrote:
I am working on device support for a device which is volatile in the sense that it can change in ways other than through the EPICS IOC. For inputs this is not a problem, periodically scanned input records will get the current value. For output records it is not obvious how to deal with this. I would like the output values displayed on the operator screen to be correct even when they are changed via means external to EPICS.
The EPICS record types weren't really written with this in mind. The usual approach to solving this is for every output record to have a separate input record that reflects the actual setting read back from the device; the user can see that their last request value is different to the current setting and infer that the output was changed via the other control method.
Ether_IP, the device support for Allen-Bradley hardware, is an example of a device support that does this. The device driver periodically reads from hardware the values corresponding to EPICS output records and executes a callback to update the output record. In this way the EPICS output record has the correct value even if someone changes a PLC tag via the vendor software RSLogix.
Is there another example of a device support which does this?
Something in my subconscious is telling me that this can lead to incorrect values being displayed if changes are made from both sources simultaneously. If I set the record at the same moment that it's being changed by some other controller, my change results in a message getting queued from the record to the device, but if it queues up a message to me at the same time saying that the value was changed from outside, its message will override my value in the record but my message will still change the actual output value. When that happens, my display of the record value shows that my put failed when actually it succeeded.
I guess this problem only occurs if the protocol is message-based and not scanned; for a protocol like EtherIP where the driver is continually scanning the PLC, the next scan would clear up the problem and show the actual state of the output. Thus if you're using a message-based protocol the above two-record approach is safest, but if you're going to be continually scanning the device Kay's method should be safe.
HTH,
- Andrew
device support for output connected to volatile device John Dobbins
Re: device support for output connected to volatile device Andrew Johnson
Prev: Re: Java CA context cleanup issues on Linux? Kay-Uwe Kasemir
Next: RE: string monitoring in medm Jeff Hill
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  <2007>  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Prev: Re: device support for output connected to volatile device Andrew Johnson
Next: I want to unsubscribe from tech-talk Aravamuthan Govindan