On Mon, 2021-01-25 at 12:16 -0800, Randall Cayford via Tech-talk wrote:
> I have a device which returns a value and a string indicating the units of the value. I’ll get inputs like 0.3nA or
> 3.4mA, etc. Since I want to report the value in a consistent unit, I want to convert the unit string to a scale
> factor (nA=1, uA=1000, mA=10000) and then use a calc record to scale the value. CALC records seem to only take
> numbers as input and I don’t see any other appropriate record type.
> In programming I would use a case statement or if-elseif constructs. How do I do this with EPICS record processing?
> Randall
> LBNL
When using StreamDevice, you can use regular expression preprocessing to modify the unit prefixes.
Assuming the possible units are nA, uA, and mA (not A) and you want everything in nA, you can convert the unit prefix
letters to exponential scaling factors like this:
in "%#/u/e3n/%#/m/e6n/%fnA";
Then "uA" becomes "3enA" and "mA" becomes "e6nA". Your example "3.4mA" becomes "3.4e6nA" before "%fnA" reads it.
Dirk
- changing unit string to scale factor Randall Cayford via Tech-talk