Hi Randall,
One example, which I would like to explain, may be useful to you.
You can add the reading unit to update the current EGU field. For
example, you have three PVs:
* I-RB (ai)
* EGU-RB (mbbi)
* FLNK-EGU (stringout)
record(ai, I-RB) { ... }
record(mbbi, EGU-RB) { ...
field(FLNK, "FLKN-EGU")
record(stringout, "FLNK-EGU") {
field(OUT, "I-RB.EGU NPP")
field(OMSL, "closed_loop")
field(DOL, "EGU-RB.VAL NPP")
With this logic, you always make sure your value has the correct unit
(EGU) in that PV.
You also have to consider when two records are processed. In my case,
the mbbi record is processed when my IOC starts with the assumption that the
device EGU value will not be changed and myIOC doesn't have the write
permission on the device.
HTH,
Han
P.S. You can contact me through my lab account if you want.
On Mon, Jan 25, 2021 at 12:40 PM Mark Rivers via Tech-talk
<[email protected]> wrote:
> There are a lot of useful records in that epics-modules/calc repository.
> Mark
> -----Original Message-----
> From: Randall Cayford <[email protected]>
> Sent: Monday, January 25, 2021 2:38 PM
> To: Mark Rivers <[email protected]>
> Subject: Re: changing unit string to scale factor
> That looks like the right way to go. It’s not in the base record types documentation so I hadn’t seen it. Thanks!
> > On Jan 25, 2021, at 12:27 PM, Mark Rivers <[email protected]> wrote:
> > Look at the scalcout record:
> > http://htmlpreview.github.io/?https://github.com/epics-modules/calc/blob/master/documentation/sCalcoutRecord.html
> > Mark
> > From: Tech-talk <[email protected]> On Behalf Of Randall Cayford via Tech-talk
> > Sent: Monday, January 25, 2021 2:16 PM
> > To: Engbretson, Mark S. via Tech-talk <[email protected]>
> > Subject: changing unit string to scale factor
> > I have a device which returns a value and a string indicating the units of the value. I’ll get inputs like 0.3nA or 3.4mA, etc. Since I want to report the value in a consistent unit, I want to convert the unit string to a scale factor (nA=1, uA=1000, mA=10000) and then use a calc record to scale the value. CALC records seem to only take numbers as input and I don’t see any other appropriate record type.
> > In programming I would use a case statement or if-elseif constructs. How do I do this with EPICS record processing?
> > Randall
> > LBNL
- changing unit string to scale factor Randall Cayford via Tech-talk
- RE: changing unit string to scale factor Mark Rivers via Tech-talk
Re: Altering timestamp of softIOC PV Johnson, Andrew N. via Tech-talk
EPICS Archiver routing issue Manoussakis, Adamandios via Tech-talk
<2021>
2025
2026
Re: changing unit string to scale factor Zimoch Dirk (PSI) via Tech-talk
<2021>
2025
2026