1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  <20222023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  <20222023  2024  2025  2026
Subject: RE: Bus errors accessing VME with base 7.0.6.1 and latest synApps modules
To: Torsten Bögershausen <[email protected]>, Michael Davidsaver <[email protected]>
Date: Tue, 31 May 2022 20:58:23 +0000
I did a test with the latest 3.15 base, 3.15.9.  It works fine.
Torsten suggested:
Ø  So R7.0.5 is good, and f9ea6a5bff695c5f88bb95dce38a3fd349738907 is bad ?
Ø  There are some "real" commits, and merges:
Ø  git log R7.0.5..f9ea6a5bff695c5f88bb95dce38a3fd349738907
Ø  Then it could make sense, to bisect between those 2?
That was a good idea.  I did:
git bisect start f9ea6a5bff695c5f88bb95dce38a3fd349738907 R7.0.5
The results were [bad, good, bad, good, bad, bad].  This is the final output:
corvette:local/epics-devel/base-7.0.6>git bisect bad
56f05d722dee4b8ca2968b8bface2737a3a9b185 is the first bad commit
commit 56f05d722dee4b8ca2968b8bface2737a3a9b185
Author: Ben Franksen <[email protected]>
Date:   Thu Jan 14 17:38:58 2021 +0100
    fix in dbGet: decide use of db_field_log based on whether it has copy or not
:040000 040000 c097595692ed4936a3c90b5583fe78d635635e07 62d947b9bb7f1bc2c21375dfaf13917f4500d59f M      modules
Since every single failure, whether in CAS-event or in CAC-event is failing in db_delete_field_log this commit does seem very suspicious.  I will run long tests on the commit before this one, and on this commit.
Torsten asked:
Ø  Could it be that a stack has become too short under vxWorks ?
I checked that with checkStack after it failed running 7.0.6.  None of the tasks have run out of stack space.
iocexample> checkStack
  NAME        ENTRY        TID       SIZE   CUR  HIGH  MARGIN
tJobTask     0x1c6b00     0x23b8fa0   8000   224   608   7392
(Exception Stack)                     4000     0    96   3904
tExcTask     0x1c61f8     0x33a5d0    8192   256  1248   6944
tLogTask     logTask      0x23bc340   5008   368  1232   3776
tShell0      shellTask    0x351a600  65536   864  7328  58208
(Exception Stack)                     3696     0    96   3600
tWdbTask     0x261f48     0x26e0a30   8192   272   320   7872
ipcom_tickd  0x285b88     0x26c6ea0   6144   256   576   5568
tVxdbgTask   0x13185c     0x26da910   8192   208   256   7936
tNet0        ipcomNetTask 0x23c1060  10000   240  1904   8096
(Exception Stack)                     4000     0   192   3808
ipcom_syslog 0x16bf48     0x268d220   6144   480   800   5344
tNetConf     0x1b74b8     0x26b9a50   6144   640  1488   4656
ipcom_telnet ipcom_telnet 0x26cdcc0   6144   512  1152   4992
ipsntps      0x1ba330     0x26d1450   6144   416  1056   5088
tPortmapd    portmapd     0x26d5570  10000   640  1072   8928
cbHigh       epicsThreadE 0x3464310  22000   288   576  21424
timerQueue   epicsThreadE 0x3449ff0  12000   448   704  11296
scanOnce     epicsThreadE 0x3479e60  22000   320   864  21136
(Exception Stack)                     3696     0   352   3344
scan-0.1     epicsThreadE 0x34a8cb0  22000   432   688  21312
(Exception Stack)                     3696     0   192   3504
scan-0.2     epicsThreadE 0x34a2180  22000   432   688  21312
cbMedium     epicsThreadE 0x345b7b0  22000   288   576  21424
scan-0.5     epicsThreadE 0x349b650  22000   432   688  21312
scan-1       epicsThreadE 0x3494b20  22000   432   688  21312
scan-2       epicsThreadE 0x348dff0  22000   432   688  21312
scan-5       epicsThreadE 0x34874c0  22000   432   688  21312
scan-10      epicsThreadE 0x3480990  22000   432   688  21312
cbLow        epicsThreadE 0x3452b00  22000   288   576  21424
CAC-event    epicsThreadE 0x34d4ae0  12000   240  2944   9056
(Exception Stack)                     3696   656  1344   2352
dbCaLink     epicsThreadE 0x346b0c0  22000   336  2976  19024
poolPoll     epicsThreadE 0x34b9e30   8000   272   560   7440
CAS-client   epicsThreadE 0x3560ef0  22000   784  1056  20944
CAS-client   epicsThreadE 0x357c910  22000   992  1232  20768
CAS-client   epicsThreadE 0x3586b10  22000   784  1056  20944
CAS-event    epicsThreadE 0x230c4b0  12000   320  2784   9216
(Exception Stack)                     3696     0   176   3520
CAS-event    epicsThreadE 0x3577040  12000   320   608  11392
CAS-event    epicsThreadE 0x357ff60  12000   320  2784   9216
CAS-TCP      epicsThreadE 0x34b2670  12000   768  1632  10368
(Exception Stack)                     3696     0   144   3552
CAS-beacon   epicsThreadE 0x34ce050   8000   464   928   7072
CAS-UDP      epicsThreadE 0x34b69e0  12000   864  1648  10352
errlog       epicsThreadE 0x343b740   8000   320   592   7408
taskwd       epicsThreadE 0x3445470   8000   416   560   7440
INTERRUPT                             5008     0   928   4080
value = 63 = 0x3f = '?'
-----Original Message-----
Sent: Tuesday, May 31, 2022 9:01 AM
To: Mark Rivers <[email protected]>; Michael Davidsaver <[email protected]>
Cc: [email protected]
Subject: Re: Bus errors accessing VME with base 7.0.6.1 and latest synApps modules
Hej Mark,
Another question:
Coluld it make sense to run the SW (even more stripped may be) under Linux instead with valgrind ?
A 3rd one:
From: Tech-talk <[email protected]> on behalf of Mark Rivers via Tech-talk <[email protected]>
Reply-To: Mark Rivers <[email protected]>
Date: Tuesday, 31 May 2022 at 15:35
To: Michael Davidsaver <[email protected]>
I have rebuilt the example application with soft records with base 7.0.5 with the DAC128V enabled.  It has currently run for 2500 seconds without failing, while base 7.0.6 always failed within 138 seconds.  I will let it run overnight.
Base 7.0.5 ran fine overnight, no failures in over 15 hours.
I previously reported that when I removed the AMSG and PAMSG fields from dbCommon in base 7.0.6 it did not fail when I was testing with IPAC hardware.  However, removing those fields did NOT fix the problem when running with records with soft device support.
I thus decided to run “git bisect” again, testing with the soft device support records.  I bisected from R7.0.6 to R7.0.5.  The results were [good, bad, bad, bad].  The bisect completed successfully with this output:
corvette:local/epics-devel/base-7.0.6>git bisect bad The merge base f9ea6a5bff695c5f88bb95dce38a3fd349738907 is bad.
This means the bug has been fixed between f9ea6a5bff695c5f88bb95dce38a3fd349738907 and [1c6b02b9be2a1c778f6395dd677ef425b04410be 7f142e03f5cef74b5516e76494f29c3a0f143f4f].
This looks like a merge commit, so I am not sure how to proceed.
Sent: Monday, May 30, 2022 3:02 PM
Hi Michael,
I have now reproduced the problem with no VME bus activity, i.e. no VME bus drivers initialized and no records using the VME bus.  This is the configuration:
- Base 7.0.6, only change is to configure/CONFIG_SITE to build for vxWorks-ppc32
- asyn, ipac, ip330, and dac128V modules built from new clones, master branch
- IOC application newly created using makeBaseApp.pl from base 7.0.6
These are the changes to the example application created with makeBaseApp.
configure/RELEASE has these changes:
# Variables and paths to dependent modules:
MODULES = /corvette/home/epics/devel_test #MYMODULE = $(MODULES)/my-module
# If using the sequencer, point SNCSEQ at its top directory:
#SNCSEQ = $(MODULES)/seq-ver
ASYN = $(MODULES)/asyn-4-42
IPAC = $(MODULES)/ipac-2-16
IP330 = $(MODULES)/ip330-2-10
DAC128V = $(MODULES)/dac128V-2-10-1
exampleApp/src/Makefile was changed to this.  Modules can be added and removed from the application by editing configure/RELEASE.  I removed the example records, etc. that is normally built in this file.
TOP=../..
include $(TOP)/configure/CONFIG
#  ADD MACRO DEFINITIONS BELOW HERE
# Build the IOC application
PROD_IOC = example
# example.dbd will be created and installed DBD += example.dbd
# example.dbd will include these files:
example_DBD += base.dbd
# example_registerRecordDeviceDriver.cpp derives from example.dbd example_SRCS += example_registerRecordDeviceDriver.cpp
# Build the main IOC entry point where needed example_SRCS_DEFAULT += exampleMain.cpp example_SRCS_vxWorks += -nil-
ifdef IPAC
    example_LIBS += Ipac
    example_DBD += drvIpac.dbd
endif
ifdef IP330
    example_LIBS += ip330
    example_DBD += ip330Support.dbd
endif
ifdef DAC128V
    example_LIBS += dac128V
    example_DBD += dac128VSupport.dbd
endif
ifdef ASYN
    example_LIBS += asyn
    example_DBD += asyn.dbd
endif
# Finally link IOC to the EPICS Base libraries example_LIBS += $(EPICS_BASE_IOC_LIBS)
include $(TOP)/configure/RULES
#  ADD EXTRA GNUMAKE RULES BELOW HERE
In the iocBoot/iocexample directory I added 2 new database files containing records with soft device support only.
aoTest.template contains 10 ao records:
corvette:example/iocBoot/iocexample>more aoTest.template
record(ao,"testAo_0") {}
record(ao,"testAo_1") {}
record(ao,"testAo_2") {}
record(ao,"testAo_3") {}
record(ao,"testAo_4") {}
record(ao,"testAo_5") {}
record(ao,"testAo_6") {}
record(ao,"testAo_7") {}
record(ao,"testAo_8") {}
record(ao,"testAo_9") {}
aiTest.template contains 10 ai records with an INP link to the corresponding ao record, using CP
corvette:example/iocBoot/iocexample>more aiTest.template
record(ai,"testAi_0") {field(INP, "testAo_0 CP") }
record(ai,"testAi_1") {field(INP, "testAo_1 CP") }
record(ai,"testAi_2") {field(INP, "testAo_2 CP") }
record(ai,"testAi_3") {field(INP, "testAo_3 CP") }
record(ai,"testAi_4") {field(INP, "testAo_4 CP") }
record(ai,"testAi_5") {field(INP, "testAo_5 CP") }
record(ai,"testAi_6") {field(INP, "testAo_6 CP") }
record(ai,"testAi_7") {field(INP, "testAo_7 CP") }
record(ai,"testAi_8") {field(INP, "testAo_8 CP") }
record(ai,"testAi_9") {field(INP, "testAo_9 CP") }
The st.cmd file just loads these 2 databases, it does not initialize any VME or IPAC drivers.
corvette:example/iocBoot/iocexample>more st.cmd
#- Example vxWorks startup file
#- The following is needed if your board support package doesn't at boot time
#- automatically cd to the directory containing its startup script #cd "/home/epics/devel_test/example/iocBoot/iocexample"
< cdCommands
# Mount drives with NFS
nfsAuthUnixSet("corvette", 849601092, 849600513, 0, 0)
nfsMount("corvette","/home","/corvette/home")
nfsMount("corvette","/home","/home")
cd topbin
load("example.munch")
cd startup
dbLoadDatabase "$(TOP)/dbd/example.dbd"
example_registerRecordDeviceDriver pdbbase
## Load record instances
dbLoadRecords "./aoTest.template"
dbLoadRecords "./aiTest.template"
iocInit
When the IOC boots this is the output of dbior and asynReport.  This indicates that these drivers are present, but there are no IPAC carrier cards or asyn port drivers initialized.
iocexample> dbior
Driver: drvIpac
Driver: drvAsyn
value = 0 = 0x0
iocexample> asynReport
value = 0 = 0x0
Once the IOC is running I run the following scripts.
This script runs camonitor on all 10 ai records and all 10 ao records.
corvette:example/iocBoot/iocexample>more test_monitor camonitor -tcr \
testAi_0 \
testAi_1 \
testAi_2 \
testAi_3 \
testAi_4 \
testAi_5 \
testAi_6 \
testAi_7 \
testAi_8 \
testAi_9 \
testAo_0 \
testAo_1 \
testAo_2 \
testAo_3 \
testAo_4 \
testAo_5 \
testAo_6 \
testAo_7 \
testAo_8 \
testAo_9 \
I run 2 instances of that script on a Linux machine to cause lots of CA monitor events.
I run this IDL script that writes new values to all 10 ao records in a loop at 100 Hz.  That causes the ai records to process since they have CP links.  There will be 20 records * 100 Hz = 2000 new record values per second.  Since there are 2 camonitor clients that is 4000 monitor events/s.
corvette:example/iocBoot/iocexample>more test_ao.pro out = -10.
while 1 do begin
  t = caput('testAo_0', out)
  t = caput('testAo_1', out)
  t = caput('testAo_2', out)
  t = caput('testAo_3', out)
  t = caput('testAo_4', out)
  t = caput('testAo_5', out)
  t = caput('testAo_6', out)
  t = caput('testAo_7', out)
  t = caput('testAo_8', out)
  t = caput('testAo_9', out)
  wait, .01
  out = out + 0.1
  if (out gt 10.0) then out = -10.0
endwhile
end
If the example application is built with configure/RELEASE as shown above, defining ASYN, IPAC, IP330, and DAC128V, then it fails.  In 4 tests it failed after running for [42, 132, 32, 138] seconds respectively.
VME Bus Error accessing A32: 0xbff66664
machine check
Exception next instruction address: 0x0332133c Machine Status Register: 0x0008b032 Condition Register: 0x48000844
Task: 0x34d4950 "CAC-event"
0x34d4950 (CAC-event): task 0x34d4950 has had a failure and has been stopped.
0x34d4950 (CAC-event): The task has been terminated because it triggered an exception that raised the signal 10.
Note that the task in error is CAC-event.  In the tests I did previously when using the VME hardware it was failing in CAS-event.
This is the task trace:
iocexample> tt  0x34d4950
0x0012489c vxTaskEntry  +0x48 : epicsThreadEntry () 0x0333fe9c epicsThreadEntry+0x80 : 0x0329b884 () 0x0329bb5c db_start_events+0x458: db_delete_field_log () 0x0329b06c db_delete_field_log+0x54 : freeListFree () value = 0 = 0x0
I have found that if I build the application with DAC128V commented out in configure/RELEASE then the application does not crash within the time I tested for.  I ran it twice and it ran for [630, 1400] seconds before I killed it.
I cannot explain why building without DAC128V allows the application to run, since the DAC128V driver is never being initialized.  It could just be a memory layout artifact if there are uninitialized pointers or something.
When I was doing previous tests with the dac128V and ip330 hardware enabled and running I made some changes to base 7.0.6 and observed the following:
- If I comment out all lines referencing dbCommon.amsg and dbCommon.namsg in dbAccess.c, dbDbLink.c, dbEvent.c, and recGbl.c then it did fail, but in 2 tests it took [4317, 22400] seconds to fail.
- If I also comment out the AMSG and NAMSG fields in dbCommon.dbd.pod then it did not fail in 18000 seconds.
However, with the soft record example described here the application failed in [3, 171] seconds in CAC-event even with all of those changes to base.
Sent: Friday, May 27, 2022 3:17 PM
To: Michael Davidsaver <mailto:[email protected]>
Cc: mailto:[email protected]
My recent tests have been done with the following:
- A very "thin" startup script that only loads the ip330 and dac128V drivers and records.
- A "thick" application that is built with most of the synApps modules.
I just stripped it down so the application is only built with base, asyn, ipac, ip330, dac128v.  I made fresh git clones of asyn, ipac, ip330, dac128v.
The application Makefile is very simple:
corvette:CARS/CARSApp/testSrc>more Makefile TOP=../..
#  ADD MACRO DEFINITIONS AFTER THIS LINE
PROD_NAME = CARSTest
PROD_IOC_vxWorks = $(PROD_NAME)
DBD_NAME = $(PROD_NAME)VX
DBD  += $(DBD_NAME).dbd
$(DBD_NAME)_DBD += base.dbd
$(DBD_NAME)_DBD += asyn.dbd
$(PROD_NAME)_LIBS := asyn $($(PROD_NAME)_LIBS)
$(DBD_NAME)_DBD += dac128VSupport.dbd
$(PROD_NAME)_LIBS := dac128V $($(PROD_NAME)_LIBS)
$(DBD_NAME)_DBD += ip330Support.dbd
$(PROD_NAME)_LIBS := ip330 $($(PROD_NAME)_LIBS)
$(DBD_NAME)_DBD += drvIpac.dbd
$(PROD_NAME)_LIBS := Ipac $($(PROD_NAME)_LIBS)
$(PROD_NAME)_LIBS += $(EPICS_BASE_IOC_LIBS)
$(PROD_NAME)_SRCS  += $(DBD_NAME)_registerRecordDeviceDriver.cpp
$(PROD_NAME)_OBJS_vxWorks += $(EPICS_BASE_BIN)/vxComLibrary
#  ADD RULES AFTER THIS LINE
These are the commands that build the dbd file and link the application.
Creating dbd file CARSTestVX.dbd
perl -CSD /corvette/usr/local/epics-devel/base-7.0.6/bin/linux-x86_64/dbdExpand.pl   -I. -I.. -I../O.Common -I../../../dbd -I/corvette/home/epics/devel/asyn-4-42/dbd -I/corvette/home/epics/devel/CARS/dbd -I/corvette/home/epics/devel/dac128V-2-10-1/dbd -I/corvette/home/epics/devel/ipac-2-16/dbd -I/corvette/home/epics/devel/ip330-2-10/dbd -I/corvette/usr/local/epics-devel/base-7.0.6/dbd -o CARSTestVX.dbd base.dbd asyn.dbd dac128VSupport.dbd ip330Support.dbd drvIpac.dbd Installing created dbd file ../../../dbd/CARSTestVX.dbd
/usr/local/vw/vxWorks-6.9/gnu/4.3.3-vxworks-6.9/x86-linux2/bin/ldppc -r -o CARSTest  -L/corvette/home/epics/devel/asyn-4-42/lib/vxWorks-ppc32/ -L/corvette/home/epics/devel/dac128V-2-10-1/lib/vxWorks-ppc32/ -L/corvette/home/epics/devel/ip330-2-10/lib/vxWorks-ppc32/ -L/corvette/home/epics/devel/ipac-2-16/lib/vxWorks-ppc32/ -L/corvette/usr/local/epics-devel/base-7.0.6/lib/vxWorks-ppc32/                   /corvette/usr/local/epics-devel/base-7.0.6/bin/vxWorks-ppc32/vxComLibrary.o CARSTestVX_registerRecordDeviceDriver.o    -lIpac -lip330 -ldac128V -lasyn -ldbRecStd -ldbCore –lca
I have a script that is writing new values to DAC channel 0 at 100 Hz.  That causes all 16 ADC records to post monitors at about 10 Hz.
I closed the medm screen and stopped camonitor on the ADC channels.  I started the IOC and it ran fine for 5 minutes with the script writing to the DAC.
I then opened the medm screen and started the camonitor on the ADC channels.  It failed in a few seconds with the A32 address error:
ioc13lab2>
VME Bus Error accessing A32: 0xbff99994
machine check
Exception next instruction address: 0x0329b0e0 Machine Status Register: 0x0008b032 Condition Register: 0x48000884
Task: 0x3560930 "CAS-event"
0x3560930 (CAS-event): task 0x3560930 has had a failure and has been stopped.
0x3560930 (CAS-event): The task has been terminated because it triggered an exception that raised the signal 10.
From: Michael Davidsaver <mailto:[email protected]>
Sent: Friday, May 27, 2022 1:49 PM
To: Mark Rivers <mailto:[email protected]>
> On 5/27/22 06:17, Mark Rivers wrote:
>> Hi Michael,
>> I commented out all lines in recGbl.c that reference the new amsg and namsg fields.  That did not fix the problem.
I take this to mean both db_post_events() and epicsVsnprintf() calls, which means that both AMSG and NAMSG should always be an empty string.
(aka. char[40] all nils)
https://github.com/epics-base/epics-base/commit/892a361de7002bf2b3f375f24bc5bf61858de2e5
> On 5/27/22 10:33, Mark Rivers wrote:
>> I am now using the unmodified 7.0.6 release.
> Before I build in that directory I run
I don't know how difficult it is with vxWorks @APS, but it might be a good idea to go further and start from fresh git-clone of all modules (base and synapps and application).  This should rule out build leftovers entirely.
> What could possibly cause this?
This is a very good question...
As I think about it, adding/removing AMSG+NAMSG would have exposed some partial rebuild problems with Base and parts of synapps.  The generated record type headers include a check that the number of fields at load time is the same as the number at build time.
If not a build/ABI issue, I don't see an easy way forward in troubleshooting.
We've passed the point where I would be trying to setup a (remote) debugger to inspect the stack of a faulting thread.  This should identify one of the records involved, and a dump of that record struct may show evidence of corruption.
For that matter, "dbpr <name> 5" could show evidence, if you can find one of the records.
RE: Bus errors accessing VME with base 7.0.6.1 and latest synApps modules Mark Rivers via Tech-talk
Re: Bus errors accessing VME with base 7.0.6.1 and latest synApps modules Michael Davidsaver via Tech-talk
Re: Bus errors accessing VME with base 7.0.6.1 and latest synApps modules Torsten Bögershausen via Tech-talk
Prev: Issue or misunderstanding with long string support Mark Rivers via Tech-talk
Next: RE: Bus errors accessing VME with base 7.0.6.1 and latest synApps modules Mark Rivers via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  <20222023  2024  2025  2026
Prev: Re: Bus errors accessing VME with base 7.0.6.1 and latest synApps modules Torsten Bögershausen via Tech-talk