Hello, EPICS mates. Thanks Torsten for replying. I will be away for the Chinese New Year and may not reply. >> However, everytime I move the motor(piezo stage), >> the CNEN of motor record will be switched to 0(Disable). >You may need to add an asynPrint in you driver to find out what is >going on. >What does your stage reply ? After a move command, the CNEN of motor record got switched to 0(Disable). However, everything else seems fine. I still can issue move commands. >> myStatus is 10. Very strange. It's outside the valid values of asynStatus. >> res value is 0. >It simply means asynParamUndefined. >More information may be found here: > https://github.com/epics-modules/asyn/pull/226>< https://github.com/epics-modules/asyn/commit/df33718b41> I got it. 10 means asynParamUndefined. In my old version of asyn, it's located in paramErrors.h. #define asynParamUndefined (asynStatus)(asynDisabled + 5) >All-in-all do many of the model3 drivers use a scaling factor, >which is either hard-coded or configurable in the driver. >And do not use motorRecResolution_ at all. >(I do think that this is documented, but can not find any links) >If you want to use motorRecResolution_, be prepared for handling this >error code in your driver. I see. I'll use "scaling factor".
Hej again,
some answers inline.
On 2026-02-11 03:47, LiangChih Chiang wrote:
> Hi, thank you Torsten for replying.
> >> But in the CNEN field of motor record is 0(Disable).
> >CNEN is updated from the status of the controller.
> >Does the code in the poll() function update the
> >"motorClosedLoop_" parameter ?
> You're right.
> I added the code to update "motorClosedLoop_" parameter in poll(),
> and I added the member function setClosedLoop(bool closedLoop).
> Basically, it works.
going on.
> >> I got value 0 from motorResolution_ parameter. why?
> >motorRecResolution_ is your friend.
> Getting resolution from motorRecResolution_ parameter works.
> >myStatus = c_p_->getDoubleParam(channel_, c_p_->motorResolution_, &res);
> >And see that myStatus is not asynSuccess,right ?
> res value is 0.
Nothing strange (tm)
<https://github.com/epics-modules/asyn/commit/df33718b41>
> >> There is no "home" concept in this piezo controller.
> >> So I have no way to implement the asynMotorAxis::home function, am I
> right?
> >Is it called reference ?
> >Then that can be mapped to "home()"
> No such things.
> The piezo system(controller and stage) uses SGS(Strain Gauge Sensor) to
> tell the position.
> In some sense, it's like an absolute encoder.
That's good.
Just set integer parameter "motorStatusHomed_" to 1.
(It's enough to do it once)
> On Tue, Feb 10, 2026 at 4:44 PM Torsten Bögershausen <tboegi at edom.se
> <mailto:tboegi at edom.se>> wrote:
> On 2026-02-10 08:51, LiangChih Chiang wrote:
> > Hello, EPICS mates, thanks for the help.
> > The Model 3 driver implementation of nanoFaktur EBD-060310 piezo
> > controller is kind of working now.
> > The attachment files include source code.and IOC startup files.
> > I still have some questions. Hope you can provide suggestions.
> > 1.
> > I thought motorClosedLoop_ is mapped to CNEN, isn't it?
> Yes, that is what most (all ?) model 3 driver do
> > I set motorClosedLoop_ to 1 in code, as following:
> > setIntegerParam(c_p_->motorClosedLoop_, 1);
> > 2.
> > Can I set UEIP field of motor record in driver code?
> > If UEIP is 0, the RRBV won't update even REP is updated continuously.
> > > I use the asyn_motor.db in motor-R6-11.
> That's pretty old.
> > The motor record in this .db doesn't have UEIP field.
> > So I set it in a .doAfterIocInit file.
> > 3.
> > The MRES field of motor record to 0.000001 in ioc startup file.
> > When I set VAL of motor record to 1.234,
> > I will get "position" value 1234000
> > in asynMotorAxis::move(double position, int relative, double
> > minVelocity, double maxVelocity, double acceleration);
> > Then I need the MRES value to do the conversion,
> > because I need to send the value "1.234" to the controller.
> > Why the following code returns the value 0 instead the wanted
> 0.000001?
> > double res = 0.000001; // resolution
> We can call that on ol' bug.
> See even
> <https://github.com/epics-modules/motor/blob/master/motorApp/Db/
> asyn_motor.db <https://github.com/epics-modules/motor/blob/master/
> motorApp/Db/asyn_motor.db>>
> .... follow the flow .... and
> motorRecResolution_
> is your friend. However, since that is processed through records,
> be prepared to read 0.0 a couple of times.
> > 4.
> am I right?
> > On Sat, Feb 7, 2026 at 12:08 AM Torsten Bögershausen
> <tboegi at edom.se <mailto:tboegi at edom.se>
> > <mailto:tboegi at edom.se <mailto:tboegi at edom.se>>> wrote:
> > Hej again,
> > Why are the RMP and REP fields integer ?
> > The "real world encoders" typically count in integer,
> > and so far the int32 had been enough.
> > Even if we today have encoders with more bits,
> > these are typically attached to the motor controller
> > and handled there.
> > The RMP field counts steps.
> > It was designed for a stepper motor, and even here
> > 32 bit where both enough
> > (and that is what we have before int64 became available)
> > The motorRecord itself uses the step in RMP to prevent
> > commanding a motion the will end up on the same step.
> > Moving from 0.050 to 0.051 is prevented, when MRES is 0.05
> > For a piezo (or other modern controllers) we don't need this
> > step-size, so that the motorRecord has got the SPDB field,
> > Set Point Dead Band.
> > For the controllers which are in use here, most of them
> > communicate in EGU.
> > For that reason I made a patch, where the value
> > "motorPosition_" from the driver is copied into
> > the DRBV field without conversion through integers.
> > The driver needs this patch:
> > <https://github.com/EuropeanSpallationSource/m-epics-
> ethercatmc/ <https://github.com/EuropeanSpallationSource/m-epics-
> ethercatmc/>
> > blob/master/ethercatmcApp/src/ethercatmcIndexerAxis.cpp#L81..#L83
> ethercatmc/>
> %23L83>>
> > The motor package itself is here:
> > <https://github.com/EuropeanSpallationSource/motor/releases/
> tag/ <https://github.com/EuropeanSpallationSource/motor/releases/tag/>
> > v7.2.8.1-ESS <https://github.com/EuropeanSpallationSource/
> motor/ <https://github.com/EuropeanSpallationSource/motor/>
> > releases/tag/v7.2.8.1-ESS>>
> > BR
> > /Torsten
> > On 2026-02-06 14:20, LiangChih Chiang wrote:
> > > Hi, Torsten, thanks for replying.
> > > >Using epicsPrintf (or even printf) should be forbidden in
> > > >these kind of driver code.
> > > ok. I'll fix it.
> > > >>1.
> > > > pC_->motorPosition_ is an int, used as an index
> > > > motorPosition is a double
> > > You're right. My mistake.
> > > Another question follows:
> > > "cainfo <motor_record>.REP and .RMP" will get DBF_LONG.
> > > Why aren't they DBF_DOUBLE?
> > > >>3.
> > > >>The values of position and voltage from the controller are
> > float values.
> > > >>When setting, say 2.123456, to motorEncoderPosition, it
> will
> > become 2
> > > (which is an int).
> > > >This is depending on MRES in the motorRecord.
> > > >If you set it to 1.0 (or not at all, the the fallback is
> 1.0)
> > > >all values are rounded into integer.
> > > >The trick is to set MRES to 0.000001 or so and compensate
> > > >this in the driver (multipy with 1000000)
> > > Yes. You're right.
> > > I'll try.
> > > >For the open-loop-voltage:
> > > >You probably want an own asyn-parameter for this.
> > > I'll consider it.
> > > However, the chance of this piezo controller in open-loop
> mode is
> > > extremely slim.
> > > How to support two modes(closed-loop and open-loop) in Model 3
> > driver?
> > > In closed-loop mode, VAL and RBV mean position(unit um)?
> > > In open-loop mode, VAL and RBV mean voltage?
> > > On Fri, Feb 6, 2026 at 5:51 PM Torsten Bögershausen
> <mailto:tboegi at edom.se <mailto:tboegi at edom.se>>>> wrote:
> > > Hej LiangChih Chiang,
> > > thanks for asking.
> > > Before going into your questions, please allow one
> comment:
> > > Please consider to us asynPrint instead.
> > > Especially things like
> > > #ifdef DEBUG
> > > printf("Warning: un-handled param data format:
> > > #endif
> > > Could be better coded as
> > > asynPrint(this->pasynUserSelf, ASYN_TRACE_ERROR,
> > > "%s: Warning....\n",
> > > __FUNCTION__);
> > > (If you write Warning or Err: or something is more a
> matter
> > of taste)
> > > But in any way you want to know if things go bad much
> later,
> > > after firmware updates, changes in the IOC, glitches
> here and
> > the )
> > > Having said that, finishing my review, which may read
> > unintentionally
> > > hard, lets digg into the questions.
> > > 1.
> > > > In asynMotorController.h, the data type of
> motorPosition_
> > > > and motorEncoderPosition_ are ints.
> > > A call inside the axis class looks like this:
> > > asynMotorAxis::setDoubleParam(pC_->motorPosition_,
> > motorPosition);
> > > saying which asynparameter we ar writing to.
> > > motorPosition is a double, saying where the motor
> should be,
> > > according to the controller.
> > > motorEncoderPosition_ is the value coming from the sensor
> > inside the
> > > controller.
> > > Example:
> > > the MCS2 from Smaract reads motorPosition like this:
> > > // Read the target position
> > > snprintf(pC_->outString_,sizeof(pC_->outString_)-1,
> > > ":CHAN%d:POS:TARG?", axisNo_);
> > > And encoderPosition like this:
> > > // read the actual position as measured by the
> sensor
> >outString_)-1,
> > > ":CHAN%d:POS?", axisNo_);
> > > 3.
> > are float
> > > values.
> > > > When setting, say 2.1234...
> is 1.0)
> > > /BR Torsten
> > > On 2026-02-06 08:48, LiangChih Chiang via Tech-talk wrote:
> > > > Hello, EPICS mates,
> > > > I started to implement the “Model 3” driver for
> nanoFaktur
> > > EBD-060310
> > > > piezo controller.
> > > > The attached files(.cpp and .h) are the work-in-
> progress
> > source
> > > code.
> > > > Not finished yet.
> > > > I have some questions.
> > > > 1.
> motorPosition_
> > > > But in derived class of asynMotorcontroller(like
> > > > smarActMCSMotorDriver.cpp and ACRMotorDriver.cpp),
> > > > the function setDoubleParam is used to set the above
> > parameters.
> > > > Why is that?
> > > > 2.
> > > > I can read the position(unit um, range 0 to 40) and
> > voltage(unit
> > > volts,
> > > > range -30 to 130) from the controller.
> > > > But which one should I set to motorPosition_and
> > > motorEncoderPosition_?
> > > > I don't quite understand.
> > > > 3.
> controller are
> > float
> > > values.
> motorEncoderPosition, it will
> > > become 2
> > > > (which is an int).
> > > > How to handle this situation?
> > > > Should I do some kind of transformation? For example,
> > multiply by
> > > 1000,000?
> > > > 4.
> > > > In the member function: asynStatus poll(bool*
> moving_p),
> > > > I need to set the moving/done status of the stage
> to moving_p
> > > > and motorStatusDone_.
> > > > But there is no such exact suitable command
> provided by thhe
> > > controller.
> > > > A possible candidate is "get on-target status"
> meaning in
> > closed-
> > > loop
> > > > mode(servo ON),
> > > > whether the position(from sensor) approached the set
> > target or not.
> > > > 5.
> > > > The controller has two modes:
> > > > closed-loop mode(servo ON), users set the desired
> > potion(unit um).
> > > > open-loop mode(servo OFF), uses set the
> voltage(unit volts).
> > > > What should I set to motorPosition_?
> > > > I think it should be something like "motor pulse".
> > > > what should I set to motorEncoderPosition_.?
> > > > I think it should be something like "encoder value".
> > > > ps
> > > > The controller uses binary communication protocol.
> > > > The following example is to read the position(in um) of
> > channel 0:
> > > > hexadecimal bytes in little-endian:
> > > > 10 00 01 20 02 00 20 00 00 ac 01 00 00 00 00 fe
> > > > 10 00: total length, 16 bytes
> > > > 01 20: command ID, 0x2001 means "get position"
> > > > 02 00: custom ID, used to distinguish different client
> > programs.
> > > > 20: option, 0x20 means "read"
> > > > 00: sequence number, Used in very long responses.
> Not used in
> > > commands.
> > > > 00: interface id, RS-232 or USB or Ethernet. Not
> used in
> > commands.
> > > > ac: header checksum
> > > > 01: data format, 01 means 32-bit unsigned int
> > > > 00 00 00 00: data, channel 0
> > > > fe: checksum
> > > > The response:
> > > > 13 00 01 20 02 00 10 00 01 b8 00 00 02 70 74 6a 3e
> > > > 13 00: total length, 19 bytes
> > programs.
> > > > 10: option, 0x10 means "final, no more".
> > > > 01: interface id, 0x01 means RS-232.
> > > > b8: header checksum
> > > > 00: data format, 00 means 8-bit unsigned int
> > > > 00: data, channel 0
> > > > 02: data format, 02 means float
> > > > 70 74 6a 3e: data, 0.228960 (position in um)
> > > > 3e: checksum
> > > > Any suggestions and responses are appreciated.
> > > > Thank you.
> > > > On Thu, Apr 24, 2025 at 5:31 AM Mark Rivers
> > > <rivers at cars.uchicago.edu
> <mailto:rivers at cars.uchicago.edu> <mailto:rivers at cars.uchicago.edu
> <mailto:rivers at cars.uchicago.edu>>
> <mailto:rivers at cars.uchicago.edu>>>
> <mailto:rivers at cars.uchicago.edu>>>>> wrote:
> > > > * I think I would need to write the EPICS
> motor driver
> > > module for
> > > > it.____
> > > > __ __
> > > > That is correct. You should write a “Model 3”
> driver,
> > > meaning it is
> > > > a C++ driver derived from the base classes
> > > asynMotorController and
> > > > asynMotorAxis.____
> > > > __ __
> > > > I just looked at the manual for the nanoFAKTUR
> > EBD-060310.
> > > It uses
> > > > a non-standard binary communications protocol,
> not ASCII
> > > strings.
> > > > That is unusual, most controllers use ASCII
> > communication.____
> > > > __ __
> > > > The driver you suggested as a model, https://
> > github.com/ <http://github.com/> <https://github.com/ <https://
> github.com/>>
> > > epics-motor/ <https://github.com/epics-motor/
> <https://github.com/epics-motor/> <https://
> > github.com/epics-motor/ <http://github.com/epics-motor/>>>
> > > > motorPIGCS2 <https://urldefense.us/v3/__https:/
> <https://urldefense.us/v3/__https:/>
> > github.com/ <http://github.com/> <https://urldefense.us/v3/
> __https:/github.com/ <https://urldefense.us/v3/__https:/github.com/>>
> > > epics- <https://urldefense.us/v3/__https:/github.com/
> epics- <https://urldefense.us/v3/__https:/github.com/epics->
> <https://urldefense.us/v3/__https:/github.com/epics->>>
> > > > motor/motorPIGCS2__;!!G_uCfscf7eWS!
> YgABnMrr4ouWf_GcXAuVe7LU-96lfvWFNG96utdBA3mgcrk9dBsWVY7JQtxclFMQQYwD2Zz0RmrbQGad8OJXFPc$> is fairly complex because of the class hierarchy, so you might want to start with something simpler as your example. ____
> > > > __ __
> > > > https://github.com/epics-motor/motorSmarAct/blob/
> master/ <https://github.com/epics-motor/motorSmarAct/blob/master/>
> <https://github.com/epics-motor/motorSmarAct/blob/master/>>
> > > smarActApp/ <https://github.com/epics-motor/
> motorSmarAct/ <https://github.com/epics-motor/motorSmarAct/>
> > blob/ <https://github.com/epics-motor/motorSmarAct/blob/
> <https://github.com/epics-motor/motorSmarAct/blob/>>
> > > master/smarActApp/>
> > > > src/smarActMCSMotorDriver.cpp <https://
> urldefense.us/ <https://urldefense.us/>
> > v3/ <https://urldefense.us/v3/ <https://urldefense.us/v3/>>
> > > __https:// <https://urldefense.us/v3/__https://
> <https://urldefense.us/v3/__https://> <https://
> > urldefense.us/v3/__https:// <http://urldefense.us/v3/__https://>>>
> <http://github.com/epics-motor/motorSmarAct/blob/master/>
> > smarActApp/src/ <http://github.com/epics-motor/motorSmarAct/
> blob/ <http://github.com/epics-motor/motorSmarAct/blob/>
> > master/smarActApp/src/>
> master/ <http://github.com/epics-motor/motorSmarAct/blob/master/>
> > master/smarActApp/src/>>
> > > > smarActMCSMotorDriver.cpp__;!!G_uCfscf7eWS!
> YLctRUSDiyz4K-
> t8_BzT33ew7q6EOnMR2oSaoEqf7fY5hpd5mII4cyq4pP6Gt3vwMPp1s38VSS7kXyY4shD2qrU$>____
> > > > __ __
> > > > That uses ASCII communication, but it should not be
> > too hard
> > > to take
> > > > the concepts and use binary communication.____
> > > > __ __
> > > > Mark____
> > > > __ __
> > > > __ __
> > > > __ __
> > > > __ __
> > > > __ __
> > > > *From:*Tech-talk <tech-talk-bounces at aps.anl.gov
> <mailto:tech-talk-bounces at aps.anl.gov>
> > <mailto:tech-talk-bounces at aps.anl.gov <mailto:tech-talk-
> bounces at aps.anl.gov>> <mailto:tech- <mailto:tech-> <mailto:tech-
> <mailto:tech->>
> > > talk-bounces at aps.anl.gov <mailto:talk-bounces at aps.anl.gov>
> <mailto:talk-bounces at aps.anl.gov <mailto:talk-bounces at aps.anl.gov>>>
> > <mailto:tech-talk- <mailto:tech-talk-> <mailto:tech-talk-
> <mailto:tech-talk->> <mailto:tech-talk- <mailto:tech-talk->
> > <mailto:tech-talk- <mailto:tech-talk->>>
> > > > bounces at aps.anl.gov <mailto:bounces at aps.anl.gov>
> <mailto:bounces at aps.anl.gov <mailto:bounces at aps.anl.gov>>
> <mailto:bounces at aps.anl.gov <mailto:bounces at aps.anl.gov>>>>> *On
> > Behalf Of
> > > *LiangChih Chiang via Tech-talk
> > > > *Sent:* Wednesday, April 23, 2025 1:41 AM
> > > > *To:* tech-talk at aps.anl.gov <mailto:tech-
> talk at aps.anl.gov> <mailto:tech- <mailto:tech->
> > talk at aps.anl.gov <mailto:talk at aps.anl.gov>> <mailto:tech-
> talk at aps.anl.gov <mailto:tech-talk at aps.anl.gov> <mailto:tech-
> <mailto:tech->
> > talk at aps.anl.gov <mailto:talk at aps.anl.gov>>>
> > > <mailto:tech-talk at aps.anl.gov <mailto:tech-
> talk at aps.anl.gov> <mailto:tech-talk at aps.anl.gov <mailto:tech-
> > <mailto:tech-talk at aps.anl.gov <mailto:tech-talk at aps.anl.gov>
> <mailto:tech-talk at aps.anl.gov <mailto:tech-talk at aps.anl.gov>>>>
> > > > *Subject:* Support for piezo controller nanoFAKTUR
> > EBD-060310____
> > > > __ __
> > > > Hello, EPICS mates,____
> > > > __ __
> > > > I need to control a piezo sage with the controller
> > nanoFAKTUR
> > > > EBD-060310.____
> > > > This is my first time using this controller.____
> > > > I searched and couldn't find the EPICS support
> module
> > for it.____
> > > > __ __
> > > > I think I would need to write the EPICS motor
> driver
> > module
> > > for it.____
> > > > __ __
> > > > What module code would you recommend me to use as a
> > starter
> > > > reference?____
> > > > For example, something like ____
> > > > EPICS motor drivers for Physik Instrumente GCS2
> > (General Command
> > > > Set) compatible controllers____
> > > > https://github.com/epics-motor/motorPIGCS2
> <https://github.com/epics-motor/motorPIGCS2> <https://
> > github.com/epics-motor/motorPIGCS2 <http://github.com/epics-
> motor/motorPIGCS2>> <https://github.com/ <https://github.com/> <https://
> > github.com/ <http://github.com/>>
> > > epics-motor/motorPIGCS2> <https://urldefense.us/
> <https://urldefense.us/> <https://
> > urldefense.us/ <http://urldefense.us/>> <https://
> > > urldefense.us/ <http://urldefense.us/> <http://
> urldefense.us/ <http://urldefense.us/>>>
> > > > v3/__https:/github.com/epics-motor/
> motorPIGCS2__ <http://github.com/epics-motor/motorPIGCS2__>;
> > <http://github.com/epics-motor/motorPIGCS2__ <http://
> github.com/epics-motor/motorPIGCS2__>;>!!
> > > G_uCfscf7eWS <http://github.com/epics-motor/
> > > G_uCfscf7eWS>!
> YgABnMrr4ouWf_GcXAuVe7LU-96lfvWFNG96utdBA3mgcrk9dBsWVY7JQtxclFMQQYwD2Zz0RmrbQGad8OJXFPc$> ____
> > > > __ __
> > > > __ __
- Re: Support for piezo controller nanoFAKTUR EBD-060310 LiangChih Chiang via Tech-talk
- Re: Support for piezo controller nanoFAKTUR EBD-060310 Torsten Bögershausen via Tech-talk
Re: MAXnet Alarm State Under High Motor Command Load Peterson, Kevin M. via Tech-talk
Re: How to use the RVEL field of the motor record Mathis, Stefan via Tech-talk
2025
<2026>
Questions on EPICS 7 NT types and CA → PVAccess migration Williams Jr., Ernest L. via Tech-talk
2025
<2026>