1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  <2021>  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  <2021>  2022  2023  2024  2025  2026
Subject: Re: EPID Record
From: Till Straumann via Tech-talk <[email protected]>
To: Ben Franksen <[email protected]>, Mark Rivers <[email protected]>
Date: Mon, 15 Feb 2021 09:18:15 +0100
On 2/14/21 10:37 PM, Ben Franksen via Tech-talk wrote:
Am 14.02.21 um 03:40 schrieb Mark Rivers:
That means KI must *always* be non-zero.
No, that's not true.  Consider the case of DC motor where the EPID
output is a DAC that controls the motor velocity.  If the VAL field
is the motor position, then when the motor is at the target position
the velocity is 0, so the I term must be 0.
Right. I should have added "... except in case the output variable
should be zero when the target value is reached". I didn't mention it
because it seemed like a very exceptional situation, though your example
suggests it may not be that exceptional after all.
Hi Ben.
It is a well-known feature of PID controllers that if you do not have/enable the
integral term (KI = 0) then a finite steady-state error is always needed to
drive the output (if Kp is finite). I.e., your premise is wrong: if your controller has no 'I' then VAL can never truly sit at the target position (unless the system already
sits at the desired target (CVAL = VAL), of course).
The steady-state error is reduced by increasing Kp but limits dictated
by stability margins and bandwidth limitations have to be observed.
This is why an integrator is added: it provides infinite gain at DC to
reduce the static error but is not demanding in terms of bandwidth.
Its phase shift may affect stability and must then be compensated with
suitable Kp and Kd.
HTH
- Till
Cheers
Ben
Am 13.02.21 um 13:32 schrieb Mark Rivers:
Suppose we have been at the target position for some time, i.e.
VAL=OVAL, so that E(n)=0 for all n. Then all terms become 0 and the
output is OVAL=0 as well. But shouldn't it be OVAL=VAL instead?
Your statement that "we have been at the target position for some
time, i.e. VAL=OVAL" is also incorrect.  When it is at the target
position VAL=CVAL, not OVAL.
Yes, sorry, I have confused OVAL and CVAL here.
I think your statement that "all terms become 0" is incorrect.  The
integral term (I) does not become zero even when sitting at the
desired setpoint for infinite time, because it is the integral from
time=T0, where T0 is the time that the feedback was turned on.
So that means if we start the feedback when E=VAL-CVAL=0 then we will
first move the system *away* from the desired VAL (unless it happens to
be equal to zero). Then we accumulate the errors, increasing I at each
step, until after a while I is large enough to compensate our initial error.
That means KI must *always* be non-zero. I find it a bit strange that it
initially has to move away from the correct output value only to arrive
at that value some steps later. Is it possible to preload the I with a
non-zero value if one has a good guess what its initial value should be?
The integral term is what prevents "droop", e.g. it is what supplies
the constant power required to keep a furnace at 500 C even when the
error is 0.
Ok, I think I understand this now. Thanks.
I use the EPID record for lots of tasks and it seems to work fine.
Have you observed an issue which led you to post this message?
Not me personally. Some physicists wanted to understand the behavior of
one of our control loops better, looked at the formula and came up with
the above objection. I agree that with a non-zero KI it should work
(after enough initial cycles).
Cheers
Ben
I would rather have questions that cannot be answered, than answers that
cannot be questioned.  -- Richard Feynman
EPICS Record Ben Franksen via Tech-talk
Re: EPID Record Ben Franksen via Tech-talk
Re: EPID Record Mark Rivers via Tech-talk
Prev: RE: EPID Record Mark Rivers via Tech-talk
Next: Re: EPID Record Ben Franksen via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  <2021>  2022  2023  2024  2025  2026
Next: ELMO motion control using EPICS Abdalla Ahmad via Tech-talk